- Reaction score
- 17,165
If it's a point for point rewire then it should be relatively cheap as its just pulling new cable in to existing conduit.
Discuss Circuits earthed on metal box/conduit: Does it need a rewire? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
There's so many sockets and circuits though, it would cost a fortune in labour I assume. There's 8 offices within the warehouse in total that are all done the same way.If it's a point for point rewire then it should be relatively cheap as its just pulling new cable in to existing conduit.
He told me straight out that metal conduit used as earth is not allowed in new installs.Get a spark in that knows what he's doing. Suggest he read the regs book that he's supposed to keep in his van.
He told me straight out that metal conduit used as earth is not allowed in new installs.
He also told me that changing the CU meant the entire install had to be treated as a new install.
I'm trying to work with it for now and I hope he'll have a read of the regs before he returns after my subtle prompting.
In fairness very few electrical contractors would have test equipment to perform high current continuity tests on containment now.Thanks Dave, if you were my electrician my life would be a lot easier. I've asked them to fully test the circuits today. If the readings are too high and he insists on a rewire then I'll get someone else in for a second look.
In fairness very few electrical contractors would have test equipment to perform high current continuity tests on containment now.