Discuss Class I and CLass II in the The Welcome Forum area at ElectriciansForums.net

one pointer is if you have a lighting circuit from the 1960's with no cpc. you'd then use only class II fittings.
 
Class II equipment either use double insulation or a single layer of reinforced insulation for basic protection. Accessories such as plastic light switches or batten holders are not considered to be double insulated.
 
Accessories such as plastic light switches or batten holders are not considered to be double insulated.
Interesting observation! Although the lampholder itself is marked with the double square (even though it has exposed contacts with the lamp removed) the rose itself has no such marking. Perhaps that's because it comes under a junction box standard rather than an appliance in some way?
 
Batten holders do not provide double insulation and yes I have seen the labels on them. Batten holders generally provide no provision for basic protection, see the Note at the end of Reg 416.2.4
 

Reply to Class I and CLass II in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

I have had these lights installed by a contractor whose work is normally very good. He has not connected the earth in each fitting as there is a...
Replies
37
Views
2K
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
229
Hi all, Disclaimer: I'm not an electrician and have very basic knowledge of electrical installation. We've been putting in a new kitchen into an...
Replies
17
Views
2K
I am a new PAT tester for a school, and I am stuck testing a plasma globe. It has a two core wire going to it, but no class 2 mark on the...
Replies
18
Views
2K
Hi All, My colleague and I are currently doing PAT/ISITEE Testing, and we've hit a snag with a bit of equipment - we've got 19" Racks for our...
Replies
8
Views
474

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock