As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring of a two core SWA supplying an outbuilding/shed. The supply to the property is overhead TT, so DNO provide phase and neutral only, a sub 20 ohm rod provides the main earth for the house DB. The DB in the wooden outbuilding/shed (which contains no extraneous metal or services) is supplied from the main house DB by a 2 core SWA. The shed DB which is two way with RCD main switch is currently using the main house rod as it's earth, utilising the armour of the SWA as it's cpc. The plan is to give the shed it's own low ohm rod and divorce the earth from the house at the outbuilding end, whilst leaving the armour for the SWA connected to earth at the house end. The following webpage and image sums up the situation well. The recommendation I am looking for is the part of the image below that is labelled "All insulated Class II enclosure". I've read that some people just bung the SWA in a stuffing gland in a wiska. I asked Wiska to recommend something and the said they couldn't offer a suitable Class II product and suggested Pratley. So here I am asking for recomendations for a strong reliable product / solution? The shed DB is metal. Many thanks.

Voltimum - armoured cable supplies to outbuildings

outbuilding enclosure.png
 
Of course the feed to the out-building needs to meet ADS so realistically it has to be RCD protected. That could be off the main house incomer if its something like 100mA delay and MCB for over current protection, then the out building can have weak earth fault selectivity via 30mA RCD/RCBO. It is never going to have high current selectivity though if fed from usual MCB, but probably good enough for most purposes.

Or it could come off a 30mA RCD/RCBO but no selectivity at the outbuilding. I would strongly advise not taking it off a dual RCD or similar arrangement as then an outbuilding fault will take out half the house's supplies!
 
If I were doing this (irrespective of the arguments as to why) I would take the SWA in through a plastic IP68 style gland and inside tape up the end to cover the armour wires with self-amalgamating tape or similar. Of course those glands don't grip as strongly as SWA ones so you really do need to make sure the cable is properly cleated in place.
 
If I were doing this (irrespective of the arguments as to why) I would take the SWA in through a plastic IP68 style gland and inside tape up the end to cover the armour wires with self-amalgamating tape or similar. Of course those glands don't grip as strongly as SWA ones so you really do need to make sure the cable is properly cleated in place.
That's exactly how I've done it, although it can be a challenge to find a gland big enough sometimes.
 
I found CEF has some that will do larger SWA sizes. This link ought to show the 40/50/63mm hole fitting examples:

They cover cables from 22mm to 44mm OD so a fair range of SWA.
 
Last edited:
Thank you all for the thoughts, amazing. To clarify things, the house is TT (not TN-C-S) and outbuilding/shed also TT. House is currently on a re-wireable fuse board with a standalone upsteam 30mA RCD protecting the whole installation, so no selectivity. Outbuilding is old skool metal Wylex with power and lighting on MCB's. New DB's are planned for both house and outbuilding. The house is currently destined for a full rcbo board with SPD. It will have double pole RCBO's and a built-in Type 1+2 SPD as required to cover the overhead TT supply. For a belt and braces approach the main switch will also be a time delayed 100mA RCD to protect any non-RCD wiring such as the wiring/MCB in the db for the SPD.

The outbuilding currently only has power and lighting circuits, but there is potential to expand in the future. To enable selectivity, the main switch on the new shed DB was going to be a 30mA RCD with individual MCB's for the shed's circuits. The 2-core SWA supply to the shed DB was going to be put on it's own MCB on the house DB, rather than an RCBO. House and shed are only about ten meters apart if it makes a difference.

The diameter of the SWA is only 20mm, so a stuffing gland in an enclosure with armour wrapped/heat-shrunk would not be too taxing, but as mentioned, cable needs to be properly secured.

The reason for divorcing the earth was to avoid a potential difference between the outbuilding and the house. Maybe this isn't required... Maybe the shed doesn't need it's own rod and as suggested the outbuilding just use the house rod through the SWA armour. I guess I'm keen to aim to make the house and shed installs as safe as possible. Maybe the optimum is a rod at the shed in addition to the house and leave both DB's connected to both rods through the SWA armour. Your thoughts are appreciated, aiming for safe as possible especially given pets in vicinity...?
 
Last edited:

Reply to Class II enclosure + gland recommendation for divorcing SWA armour at TT outbuilding/shed? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good Morning everyone. Quick question regarding a sub main from a TNCS supply feeding an outbuilding on TT. This is a domestic installation not...
Replies
7
Views
3K
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K
I would appreciate peoples thoughts on fixing this earthing setup to correctly separate PME & TT: Setup: Workshop at the bottom of a long garden...
Replies
31
Views
11K
So I've just been reading through the electricians guide to the building regulations for my own knowledge and have come across 2 regulations which...
Replies
20
Views
3K
I know the subject of transporting pme from a house to an out building has been discussed many times. This question is the DNO is only providing...
Replies
14
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock