Discuss Coding for lack of 30ma rcd protection - TT system in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

C3, as in that the circuits not protected by 30mA RCD could be improved to increase safety. wouldonly be C1 or C2 if immediate or potential danger present (respectively).
 
It depends on what the circuits which don't have 30mA protection are, you need to supply more information.

Without further information I would say no code unless something you haven't told us would mean these circuits require 30mA protection. If you at least specified the basic type of installation such as domestic or non-domestic it would help massively.
[automerge]1597180001[/automerge]
C3, as in that the circuits not protected by 30mA RCD could be improved to increase safety. wouldonly be C1 or C2 if immediate or potential danger present (respectively).

Why a C3? They haven't yet told us anything that suggest these circyits require 30mA protection.
 
It depends on what the circuits which don't have 30mA protection are, you need to supply more information.

Without further information I would say no code unless something you haven't told us would mean these circuits require 30mA protection. If you at least specified the basic type of installation such as domestic or non-domestic it would help massively.
[automerge]1597180001[/automerge]


Why a C3? They haven't yet told us anything that suggest these circyits require 30mA protection.
i assume (perhaps wrongly) that OP is referring to a domestic install, probably to 16th Ed., in which case 30mA RCD protection to cables in walls blah, blah and lighting circuits, maybe unprotected circiuts in a bathroom, would be improved by fitting 30mA RCD protection, so a C3 for improvement recommended.
 
Might help if people used the correct terminology, fault protection and additional protection.
 
Guessing at domestic install? Also going to assume that TT the Zs max have been exceeded. (C3 411.3.2.2)
However a 100ma RCD is provided for fault protection and A 30ma RCD for fault/additional protection.
I would code it as C3 if it is what I’m thinking of, a domestic install to the 16th edition. Most likely because of a lighting circuit not having additional protection at 30mA (411.3.4)
In my opinion, it’s only a C2 if no RCD is provided for fault protection on a TT system (411.5.2).
 
Probably depend when it was built and if there's no RCD then it usually required equipotential bonding, earthed conduit for wires in walls under 50mm and all that.
I don't think it would meet current Regs would it all circuits require RCD protection and 100ma is more protection of fire?(is that right) not electric shock.
 

Reply to Coding for lack of 30ma rcd protection - TT system in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

See this time after time - poor installation: new split load board on a re-wire tt installation. The main switch is not a time delay rcd. The...
Replies
2
Views
306
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
875

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock