Discuss Commercial kitchen job help in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
92
i have installed some fused connection units in a commercial kitchen, normally in domestics i omit supplementary bonding due to main bonds and RCD protection being in place.

Whilst my circuit has RCD protection there are existing circuits with no RCD protection and out of interest to what extent would the below need regarding bonding?

metalic water pipes, fixed metal kitchen worktops, metal extraction hoods etc.
i can see for the most part supplementary bonding in place, am i correct in saying if i get below 0.05 ohms between all exposed conductive parts i dont need a show piece of green and yellow cabling pig tailing everwhere?
 
Green yellow pigtails

Used to love making these up when I was a kid , wrapping 6mm earth round an old broom handle

Fortunately unless you are working to the 15th edition of the regs , pigtails are no longer required
 
so am i correct in saying because my circuit (installed with 30ma RCD protection i dont need to worry about the fact it has been installed around a load of 15th edition equipment.
 

Reply to Commercial kitchen job help in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
874
Just had my design project handed back to me from my last block and I got everything right apart from one question Q9 I would take a photo but...
Replies
3
Views
1K
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
788
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock