Discuss Commercial sub mains exceed max zs of mccbs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

jackhammerJIM

-
Esteemed
Reaction score
453
Thoughts required on todays scenario .

Commercial premises fed from 100 amp 3 phase TNS supply ZE 0.40

feeds 80 amp 3 phase switch fuse (max zs 0.57)

feeds 400 amp mainswitch protek panel in 35mm swa 16mm earth

125 amp mccb (0.24 max zs) submain exceeds max zs at 0.57

Had this down as a code 2 but max zs of 80 amp switch fuse will disconnect in under 5 seconds ....

Dogs dinner of a set up , any one in agreement of my code 3 ????
 
Even if your Ze was 0.10 you wouldn't achieve selectivity. I don't suppose you did a line/neutral reading at source of supply.
 
Even if your Ze was 0.10 you wouldn't achieve selectivity. I don't suppose you did a line/neutral reading at source of supply.

not yet . Im going in early tomorrow so will test L N .

The main panel and sub mains were installed 5 years ago with no paperwork and not a lot of thought in design .

In your opinion does it warrant a code 2 ?
 
Fault protection is provided at the 80A switch-fuse the problem you have is selectivity by possible poor design and a high Ze.
 
So you have 0.40 at the 80A switch-fuse which supplies a switch panel at which Zs is 0.57 thus, the Zs for the 125A device at this panel will be excessive due to the 0.57?
 
It isn't confusing to you because you can visualise it but to someone reading you first post it is not clear.
 
Read the first post again it is not that confusing .

The report will state that the 125a sub mains from the 400 amp panel board exceed maximum permissible zs values but the disconnection time will be met by the 80 amp switch fuse at source
This statement to me gives the impression is all okay and maybe it is as fault protection is provided but the issue of selectivity is not clearly addressed. There is no selectivity between x and the supply protective device y whereby fault protection is provided by y. Or something along those lines.
 

Reply to Commercial sub mains exceed max zs of mccbs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
I am helping a local football club who are having some issues with Zs being too high on the submain. They have the supply Henley blocked into a...
Replies
9
Views
2K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
All of the work described below will be completed by a qualified electrician, I am just curious and using the info for planning!! I am planning a...
Replies
13
Views
4K
I want to use a manual change over switch to safely connect a 21kVA single phase tractor PTO powered generator to my mains supply in case of...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock