Discuss Compressor 3hp motor DOL starter question in the Electricians' Talk area at ElectriciansForums.net

the direct on line contactor should come with or you should fit the correct sized overload for the motor it's controlling. You should not have any need for that that thermal overload switch as well.
I'm assuming your current set up would start the compressor automatically as the pressure drops bellow as cetain threshold? This should be run through the controls for the starter so a simple DOL starter will not work as you require it.
I don't quite understand everything you say there.
You say the DOL Starter I'm getting should have a thermal overload switch?
this is the one I'm getting
So I could check that out.
The confusing bit you say is that the DOL will not work as I require. I run the switch for the motor from the pressure sensor, then that sensor is powered from the DOL. When the pressure drops, the pressure switch powers the motor. the pressure switch will be live as long as the DOL starter is switched on.
 
That starter has an overload relay inside which can be set between 10-16A.
With the DOL starter you have selected stop/start of the motor is controlled by pushing the buttons on the front of the starter. Your set up should have the pressure switch stopping and starting the motor via the DOL contactor and overload the pressure switch should not have the motor running current through it.
 
That starter has an overload relay inside which can be set between 10-16A.
With the DOL starter you have selected stop/start of the motor is controlled by pushing the buttons on the front of the starter. Your set up should have the pressure switch stopping and starting the motor via the DOL contactor and overload the pressure switch should not have the motor running current through it.
So you are saying, I should have power going to the DOL, then to the pressure switch, back to the DOL then the motor. That really does not make any sense to me. Is that what you mean? In other words, the last thing before the motor should be the DOL?
If that is the case, then I should mount the DOL onto the frame of the compressor.
[automerge]1588251408[/automerge]
So you are saying, I should have power going to the DOL, then to the pressure switch, back to the DOL then the motor. That really does not make any sense to me. Is that what you mean? In other words, the last thing before the motor should be the DOL?
If that is the case, then I should mount the DOL onto the frame of the compressor.

Maybe if I put power through to the pressure switch, then to the starter, then the motor. But then, when the pressure switch wants to start the compressor again will the DOL reset to off? Or will it stay on?
 
Last edited:
I can't stop to answer fully but there is confusion going on between a starter with a contactor i.e. relay, which is controlled by the pressure switch and takes the motor load itself, and a mechanically latching pushbutton switch with thermal overload which is what I think is in the link. The latter is normal for compressors of this size where the pressure switch is rated for the motor current, since the electrical latching of a contactor isn't needed and can't be used if under pressure switch control.
 
the starter is a big switch designed to take the motor current what operates this big switch is a little switch, in your case the pressure switch.

If you're not clear on how to connect them up correctly why not ask your brothers mate to have a look. Or just buy a prebuilt unit big enough for what you need. Try Atlas Copco they make good compressors with everything built in.
 
the starter is a big switch designed to take the motor current what operates this big switch is a little switch, in your case the pressure switch.

If you're not clear on how to connect them up correctly why not ask your brothers mate to have a look. Or just buy a prebuilt unit big enough for what you need. Try Atlas Copco they make good compressors with everything built in.
I have asked exactly that to be sure I get the best I can. Sure, I can spend over £1k for a built unit that has a receiver this size but I would rather renovate my 1960 classic compressor tank to suit everything else in my garage for £300.
I'm not using it for professional usage, it's for now and then and I suppose I could buy a cheap smaller compressor for less and save my time learning, but when this one is finished (and I'm in no hurry), it'll see me out. Plus, I enjoy the small challenge.
I'm rebuilding a classic car in between, so it's a nice distraction during this lock down period.
But thanks to all for the advice so far, I'm slowing going up the right path. I'll post a picture when it's done.
 
I have asked exactly that to be sure I get the best I can. Sure, I can spend over £1k for a built unit that has a receiver this size but I would rather renovate my 1960 classic compressor tank to suit everything else in my garage for £300.
I'm not using it for professional usage, it's for now and then and I suppose I could buy a cheap smaller compressor for less and save my time learning, but when this one is finished (and I'm in no hurry), it'll see me out. Plus, I enjoy the small challenge.
I'm rebuilding a classic car in between, so it's a nice distraction during this lock down period.
But thanks to all for the advice so far, I'm slowing going up the right path. I'll post a picture when it's done.

What car are you working on?
 
What car are you working on?
Singer Gazelle. Nothing exotic, but a good work horse practical classic. Finished a ton of welding with her, she is now in patchy grey primer here and there, but the crap all-in-one compressor that was bolted to my receiver was just not up to the job of spraying. So I'm upgrading that, it will look more original with a twin cylinder on top. Just renovated an old 2 post lift that I got for a favour, it was rusty as hell but now smells of grease and hammerite. I recently learned a lot about hydrolic lifts and can now lift the old girl up to work on her. It's the same with that, I could have spent a couple of grand on a lift, but would rather spend the evenings figuring it out myself and trying to fix something that is fundamentally better quality.
 
My mistake miss read the original post and got mixed up thinking you were using a 32A motor. I don't think you will need that DOL starter and overload relay if the pressure switch is a decent one that's rated for 16A you could just use a 2 pole motor protection circuit breaker. These are suitable for motor disconnection as well as overload protection.
 

Reply to Compressor 3hp motor DOL starter question in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

I am back to try and hook up my Frankenstein compressor. 60 gal tank, Ebay 5hp motor, HF 5 HP, 145 PSI V-Style Single Stage Cast Iron Air...
Replies
0
Views
533
Hey, I want to use an old xbox 360 PSU- 12V 175W output- for my 12V sup pump (pump/air compressor). When I connected the PSU to the pump...
Replies
3
Views
374
We are in the process of restoring 4 of a group of 5 Brookhirst DC motor starters from 1936. These are a thing of beauty and the engineering in...
Replies
1
Views
1K
I'm a DIY'er. Setting up a dual purpose shop-cooling and overspray fan. Bought this motor which reads "1.5 hp" but, looking at the amps, shouldn't...
Replies
3
Views
884
Guys I have 2 DOL starters which share the same supply for 2 toilet extract fans I have a selector switch wired up and and a set of auxilliary...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock