Discuss Conduit as earth???? in the Australia area at ElectriciansForums.net

M

mickytuff

Hi all done some testing work at a hospital and the orignal wiring was done in metal conduit, now the zs figures tested all good, my question is can u calculate the r1 and r2 figure when their isnt an earth cable as such???
 
Good question,, as for r1 thats your line conductor, and r2 being your earth in this case the conduit. in this set up I use a wander lead and zero my meter with this long lead. then go around pokeing it onto every acessory's earth the highest reading I take as my r2 reading for the test cert
 
You cant calculate R1+R2 from Zs anyway, even if a seperate cable was being used as CPC due to all parallel paths included when live testing Zs.
 
biggest probelm is if the conduit is broken you should really do a Zs at every point to confirm polarity and earth continuity ,what you should do is an r2 test instead of the r1r2 but note it on the test certs as conduit used as earth
 
LOL,, should have read the post better!! didnt see the calculate bit thought he was asking how to take the reading.. my bad.. :)
 
So on the cert in the earth continuity box what would you put l/l n/n and then????? I agree doing the r2 method to confirm the earth, which is also confirmed by doing the zs test but do i leave the box blank or put n/a due to the nature of the wiring system used????, oh and thanku all for your ideas, all gratefully recieved, shud of said that 1st realy
 
I put con or mech in the CPC box for ring mains, and would put a - in the r1-r2 box and put my r2 reading in the r2 box :)
 
I'm confused even further now.

Are you referring to the section for the cable sizes i.e 2.5/1.5 for a normal RFC??? Where conduit is used as the CPC, under the CPC size i enter 'K'.

For the measurements, L-L (r1), & N-N (rN) are as normal, for E-E (r2), again I put 'K' in the box.
 
thats the way I read it lenny,, but i have to say can you tell me about the 'K' ive always put mech or con in them places..
 
When testing i use the amtech software and you can select the earth as conduit, you enter in the size of the conduit and it gives you a equivelant figure as a c.s.a of 80mm for 20mm conduit, meaning the conduit is acting like the size of a 80mm cable i presume, strange i know, but this figure cant be accurate, as the condiut could be 1m long or 30m in length, so this isnt realy accurate, the column i was reffering to was the ring final contuity part, what i've just said is the column your referring to, i.e the cable size part.
 
I understand what your saying lenny, you put k in the e-e box and enter your r2 reading in the r2 box, as you cant calculate the r1/r2 conventially? Correct?
 
Ok nickblake here we go...............while testing with a megger multi, if you chose to test on notrip on your loop test, why do U have to connect all three leads, if you connect just line and earth it wont produce a reading and just say trp on the display, yet when you deselect no trip it tests fine with just two leads connected, so there you go, any body else had same problem???????????
 
Last edited by a moderator:
Ok nickblake here we go...............while testing with a megger multi, if you chose to test on notrip on your loop test, why do U have to connect all three leads, if you connect just line and earth it wont produce a reading and just say trp on the display, yet when you deselect no trip it tests fine with just two leads connected, so there you go, any body else had same problem???????????

In "No-trip" mode the Megger MFT electronics requires 3 wire L, N and E connections for power and reference so that the sophisticated method of noise cancellation that the Megger uses can resolve the impedance from the low level "No-trip" current pulses, even in an electrically noisy environment. It is because of this multiple current pulse and noise cancellation technique that the Megger gets unfair criticism from users of other MFTs (Fluke particularly) for it's apparently slow "No-trip" test, however, Megger users get the last laugh because they very rarely have their test inhibited by a noise error.
 
Last edited by a moderator:

Reply to Conduit as earth???? in the Australia area at ElectriciansForums.net

Similar Threads

So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
331
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
550
Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
Replies
8
Views
901
Hi all Done a EICR on a flat which had the link fuse in the service head .. had an earth wire coming off the orange cable to an earth block...
Replies
16
Views
831

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock