hi guys

ive read somewere the mounting distance for saddles when using conduit, ie how far apart they should be, cant find it anywere

any idears?

cheers
 
The spacing for 16<=dmm conduit is: 0.75m horizontal and 1.0m vertical for rigid metal
0.75m horizontal and 1.0m vertical for rigid insulating
0.3m horizontal and 0.5m vertical for pliable

The spacing for 16<d>=25mm conduit is: 1.75m horizontal and 2.0m vertical for rigid metal
1.5m horizontal and 1.75m vertical for rigid insulating
0.4m horizontal and 0.6m vertical for pliable

The spacing for 25<d>=40mm conduit is: 2.0m horizontal and 2.25m vertical for rigid metal
1.75m horizontal and 2.0m vertical for rigid insulating
0.6m horizontal and 0.8m vertical for pliable

The spacing for >40mm conduit is: 2.25m horizontal and 2.5m vertical for rigid metal
2.0m horizontal and 2.0m vertical for rigid insulating
0.8m horizontal and 1.0m vertical for pliable

Taken from OSG page 115 table 4C.
 

Reply to conduit distance in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, I have two questions regarding wiring and containment on commercial property stairwells in Ireland. We are currently wiring a 3 story...
Replies
10
Views
685
I am going to need to install a small amount of galvanised steel conduit, leading down to perhaps 4 sockets and a light switch. This is in a...
Replies
38
Views
4K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Now Ive done Periodic Inspection and Initial Virification Qualifications with LCL/EAL (so non C&G 2394/95) # strange part building Modules , this...
Replies
6
Views
944
Hi. I've read much about ac vs dc but can't find a 'simple' answer. If current alternates 50 times per second in a uk mains circuit, why do live...
Replies
23
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock