Discuss confused with procedure need help in the The Welcome Forum area at ElectriciansForums.net

Reaction score
0
installed a secondary 2 way consumer unit to run a boiler and immersion heater i know i have to issue an eic but what do i actually test? r1 + r2 of the radial to the secondary consumer unit and both radials from the secondary consumer? please can someone give me a rundown of what id need to test?
 
You will need to perform all the tests required to complete the fields on the EIC. Methods for performing these tests are described on your On-Site Guide.
If you have installed new circuits in a domestic property this is notifiable work under the Part P of the Building Regulations and you are required to notify the Local Authority Building Control.
I assume you are not able to self-certify the work so can expect to pay them for the privilege of inspecting it for you.
 
Have 2 schedules of test results one for the first CU showing your new circuit to the 2 way CU and the other schedule showing the new circuits on the CU that you installed. 1 inspection sheet and all the other details needed. All tests required apart from ring continuity if you have no ring finals
 
yes i know you have to contact building control you ever tried talking to newham building control? they dont even know what they are doing. ive got 2391 and 2392 but get told all different things some people saying you have to re test the whole board even the old circuits which i didnt think was right i just thought it was the new circuits your installing you had to test
 
Your description of works on the EIC is what you need to do ..



So something like ..... Install new circuit number ?? And install 2nd fuseboard and new circuits for .....

You have to ensure earthing and bonding are up to spec, plus your circuits must comply with the latest regs.

On your schedule of results for the existing board, I would use state "used" for existing circuits, and spare for any unused.
 
installed a secondary 2 way consumer unit to run a boiler and immersion heater i know i have to issue an eic but what do i actually test? r1 + r2 of the radial to the secondary consumer unit and both radials from the secondary consumer? please can someone give me a rundown of what id need to test?
It's R1+R2, r1,r2and rn are end to end resistances.
 
If like to hope if you are installing a consumer unit you are an electrician and are competent enough with testing to carry out the work following correct procedures with part p
 

Reply to confused with procedure need help in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...
Replies
16
Views
2K
Hello, I have an all-in-one washer/dryer unit and it is giving me error codes. I have the manual that describes how to test the various...
Replies
2
Views
571
Hello, I was looking at installing a SPD into an existing split load RCD BG consumer unit. In the instructions for the SPD it states that it may...
Replies
2
Views
1K
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
629
Until last week I had a dual tariff electricity supply with a cheaper overnight tariff. This was good for the storage heating, but now the storage...
Replies
2
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock