Discuss Connecting a thermostat to an existing boiler in the Central Heating Systems area at ElectriciansForums.net

Muppet09

DIY
Reaction score
0
Hi everyone.

Im new here and I apologise if this has already been asked.

I am trying to connect my thermostat to my existing combi boiler. The thermostat is under the boiler and has 4 core wire coming out of it. The gas engineer who came out to service the boiler said that it can't be connected as it needs a 5 core wire.

Now....

From the wall socket to the boiler, is a 3 core wire. (L/N/E) that connect to the left side of a connector block. (I apologies for not knowing the name of this part) on the right side of this block are 5 wires. L/N/E and 2 black wires. (The 2 black wires are looped on the left side of the connector block)

I know I have to unloop these and send the power from L1 / L2 (this is the terminals that are looped) to the wireless thermostat sender unit. But where do I connect the L/N/E? Do I connect it to the side of the connector block (left) which has the mains wires, or to the boiler side (right)?

Many thanks
 
I think a bit more information is needed to enable us to comment on whether we can offer advice or recommend you seek professional help.
Make and model of the boiler, make and model of the thermostat and maybe a few photos would be a good starting point.
 
I think a bit more information is needed to enable us to comment on whether we can offer advice or recommend you seek professional help.
Make and model of the boiler, make and model of the thermostat and maybe a few photos would be a good starting point.

I will get some photos once I get home and try and find the makes and models ?

I have been told it will work by the engineer, but he just didn't have to correct wire is all
 
Don’t be tempted to use the green/yellow as anything other than an earth wire, even if it’s not required by the stat.
5 core flex is readily available from electrical wholesalers

Yes, I know that thank you. I am pretty good with electrics, fit all my own stuff, but due to this being my first boiler I just wanted to double check. ?
[automerge]1576510714[/automerge]
I will get some photos once I get home and try and find the makes and models ?

I have been told it will work by the engineer, but he just didn't have to correct wire is all

These are the pics I could get. Hope they help. I'm just needing to know which side of the block to run the wires. Left side with mains power or right side with boiler. Also, the black wire in the thermostat sender is in L1... Does this go to live in or live out? Cheers
 

Attachments

  • DSC_0006.JPG
    44.3 KB · Views: 25
  • DSC_0005.JPG
    55.6 KB · Views: 25
  • DSC_0004.JPG
    31.5 KB · Views: 25
  • DSC_0012.JPG
    41.4 KB · Views: 30
  • DSC_0011.JPG
    70.2 KB · Views: 32
  • DSC_0010.JPG
    74.2 KB · Views: 33
  • DSC_0009.JPG
    71.7 KB · Views: 31
  • DSC_0008.JPG
    81.1 KB · Views: 29
Last edited:
looks like you need 5 core cable. L, N, E, Lin from boiler, Lout back to boiler. lookslike someone has already misused the cpc of the existing 3 core flex.
 
A 5 core flex will be required. To do this the live and neutral to your receiver need to be connected to the existing live and neutral in the boiler together with the earth conductor, then the L1 & Lx connections in the thermostat connected to the terminals that are presently linked out in the boiler (remove link!). As there is no earth terminal in the thermostat, this will need to be terminated in a connector block.
Terminate the cables on the left (the same side as the existing cables)
 

Reply to Connecting a thermostat to an existing boiler in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

Hi folks, I'd like to get my Nest thermostat up and running with the gas combi boiler (Worcester Greenstar HIghflow 440 Standalone). FYI - I...
Replies
9
Views
1K
Good afternoon chaps, I have an Alpha E-Tec 33 combi boiler (with Google Nest 3rd Gen thermostat) that occasionally fails to put out hot water...
Replies
10
Views
959
Hi, I'd like to move the existing socket that feeds the boiler down to where I've pencilled in that can be seen on the photo. The socket to the...
Replies
10
Views
852
Hi there, We have recently replaced our central heating programmer with a Honeywell ST9400C. We now want to replace our old wireless room...
Replies
0
Views
696
Hello, I'm in the process of changing my wired remeha thermostat with the wireless hive mini, I've had a look at the manual and believe I have...
Replies
5
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock