Just wanted to check something with the great and the good on here, I'm just about to put in a aeg induction hob in my kitchen, the two diagrams show one 400v diagram with the two lives going to connection points 1 and 2, the 230v diagram (relevant to me) shows the live going to connection point 2 but with a bridge/loop also connected to connection point 1 from connection point 2 this makes sense but I wanted to check on here. For info I am using 6mm cable on its own 32amp mcb hob is 4.7 kW.
Thanks for any replies
 
That's correct regarding the link, I wouldn't use T&E cable though, better to use 3 core H07 flex for the final connection, in your case 2.5mm2 would be fine.
 
ours has been on 6mm T/E for 20 years. it's been pulled out twice in total. once to find a fault (blown element) and once again to replace said element. the 6mm cable shows serious adhesion of cobwebs but is otherwise fine.
 
And of course there's the take heed of manufacturers instructions thing, I've probably connected 100 cookers with good old 6mm T&E over the years but these days the right flex just seems more appropriate and professional. And a built in oven will get a bit warmer than 70 degrees too. :)
 
And of course there's the take heed of manufacturers instructions thing, I've probably connected 100 cookers with good old 6mm T&E over the years but these days the right flex just seems more appropriate and professional. And a built in oven will get a bit warmer than 70 degrees too. :)

only on the inside.
 

Reply to Connecting an induction hob in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have an install where the client has supplied an induction/gas hob combination unit. We have a 6mm cable supplying the hob, the induction part...
Replies
3
Views
953
Hi all, I've just tried wiring an indesit IB65B60 induction hob. I read the instruction manual and it said for 240v connections to put the...
Replies
23
Views
4K
Hi all I'm in the process of swapping out my 4 zone CDA induction hob for a 5 zone Bosch. Currently the existing wire starts as a 5 core cable...
Replies
10
Views
2K
Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance...
Replies
2
Views
338
Hello I have two new appliances Electric oven rated at 3.95 KW Induction hob rated at 7.2 KW total of 11.15 KW Currently it is on its own...
Replies
17
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock