Discuss Connecting T&E to SWA in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
10
Hi all,

Would appreciate your thoughts on the following.

Customer has a garage CU fed by a 6mm cable from the main CU in the house. The cable exits the house and then is stretched overhead between the house and the garage. The cable is starting to sag and the customer wants it replacing. My initial thought was to replace with swa from house CU to garage CU going underground however, the main CU in the house won’t take swa and gland without pulling it all out and repositioning it, something the customer doesn’t want to do. So I’m thinking of cutting the cable where it exits the house and connecting to swa then dropping down underground and across to the garage. The CU in the garage has 2 radial circuits, 1 socket and 1 light on 32a and 6 a mcb’s respectively. I’m thinking that 6mm cable is way over the top for this demand and looking at 2.5mm swa to connect to the 6mm in a junction box under the roof overhang. The main CU is protected by a 16a mcb. It’s not the ideal solution but I think it’s safe and reasonable - any thoughts?
 
i.d still use 6mm SWA to allow for any future increase in load. make sure armour is earthed.
 
No way is 6mm over sizing the supply to another CU.
Why are you talking about a 32 amp breaker for a single socket??
Main CU protected by 16Amcb?
 
i.d still use 6mm SWA to allow for any future increase in load. make sure armour is earthed.
Thanks telectrix. Yes to earthing the armour although I think I’ve seen on the site somewhere that it’s not strictly necessary if using one of the conductors are cpc. Is this right?
 
Is there space to put the junction box adjacent to the CU? That way the box is inside and if the CU is replaced in the future the cable could be put into the new CU.
Hi R-fur, no the CU is positioned tight in a corner, looks very neat but difficult to get at plus the cables go outside almost immediately.
 

Reply to Connecting T&E to SWA in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, Can I ask you a DIY question? I'm refurbing a detached garage and adding a garden building. Garage currently has a submain supplied by...
Replies
1
Views
843
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
586
For various reasons out of my control, we have wound up in a situation where we have 1.5mm SWA cables buried in these pillars and exiting out of...
Replies
95
Views
7K
Afternoon everyone.. During some testing I have found an IR reading of 0.01MΩ between N-E. This is on a length of SWA buried underground from the...
Replies
17
Views
3K
Hi all, Newly qualified electrician here who is in the process of re-wiring my own property. I have recently converted my old CU (if I can call...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock