Discuss Connection in shower room in the Australia area at ElectriciansForums.net

R

rob121

Evening All!

Been running cables on a small extension. Was just about to leave when the builder asked me to run a supply for a masserator (think thats how its spelt). Anyways its going directly next to the shower, located in a small unit (like a kitchen unit). Will the jb inside the unit need to be IPX4? I know that the space under a bath is classed as outside of the zones if its accessible only with a tool but doesnt mention units?

First time ive seen one before, like a big food processor inside!

Cheers Guys

Rob
 
If it is inside zone 1 then it has to be SELV because a macerator is not one of the permitted items of current using equipment. If you measure around the walls of the barrier is it within 600mm?
 
Well it is a turd processor, at the end of the day!! It processes the food that come out at the other end!! Just refuse point blank to do any maintenance on the unit in the future !!! lol!!
 
Richard, not sure of the measurements as he hasnt fitted it yet, but seen as its permanent and fixed its okay to install in zone 2 right?

Engineer54, too right. I did notice the warranty comes with its own dedicated service team. What a job ay!
 
Rob121 so long as it is not switched in zone 2, only permanently wired, then it is OK to install but everything must be IPX4.
I have often found that cupboards with items inside them are often outside of zone 2 once you take the barrier into account, however a small "kitchen unit" right next to the shower may well be in zone 2 inside the cupboard.
 

Reply to Connection in shower room in the Australia area at ElectriciansForums.net

Similar Threads

Hi, I have a client with a small caravan site, approx 5 hookups. His old toilet block was nothing much more than an old shed. He's now 'upgraded'...
Replies
2
Views
558
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
So this was an interesting conversation today and wanted peoples advice. Plumber asked me if I could fit a socket inside an enSuite Vainty unit...
Replies
21
Views
4K
One of the oddest jobs I've ever had today. Called by a plumber I know who had attended after a leak through the kitchen ceiling from bathroom...
Replies
24
Views
6K
My first posting and hope you guys can help. I am a householder in the process of planning a refurb of our bathroom (not DIY) and putting together...
Replies
11
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock