Hi all
I have a little problem which I would be very grateful for any advice or assistance. I work for a Developers and we are building 21 new dwellings for a client. The architect has sited the CU's in some interesting positions and I have queried these but he is adamant that they are sited where he says. Some are situated in a tiny cupboard under the stairs, which would mean running a sub main. One was even located in a wardrobe in a first floor flat and another in a downstairs toilet. I have quoted Regs 132.12 and 513.1 of BS7671-2008 and also Regulation 15 of The Electricity at Work Regulations 1989 but he will not move. He is also stating that any CU's in the hallway be mounted between 0.75 and 1.2 ffl as per Part M. This again brings into question chances of damage by accidental impact and prying fingers of children, especially the chance to push the test button. I am now at my wits end which was a very short journey as well as pulling out the last remaining hair I possess. any help would be greatly appreciated
 
ipd1961

Not sure what else you can do or say, get architect to sign off design part of EIC & departures from BS 7671, but at the end of the day if you feel its not safe perhaps let someone else do it.
T&E
 
We are contracted to carry out the installation, he has changed the CU positions after a conflict where one was sited behind an oven housing in the kitchen, so he then decided to change all the rest
 
That sounds like a contradiction to me - situating the cu in a hallway to the part M heights is nice and accessible (if anything too accessible) yet putting them in a toilet or cupboard under the stairs is less accessible albeit not inaccessible.

Why does he want them in these particular positions?
 
I suspect he's assuming that you can still run the circuits inside the wall cavity. You may like to point out that this has not been allowable for some time now!
 
Hi All
This particular architect seems to be stuck in the 1960's and his last Regs was the 14th.The client is more responsive to ideas but the architect doesn't like being wrong, which is typical. Anyway onwards and upwards and the next meeting scheduled for tomorrow shall be very interesting as I am armed with BS7671-2008 and EAWR 1989, see if he can trump that
 
it's like i always thought the football team was called partickthistlenil
 
That sounds like a contradiction to me - situating the cu in a hallway to the part M heights is nice and accessible (if anything too accessible) yet putting them in a toilet or cupboard under the stairs is less accessible albeit not inaccessible.

Why does he want them in these particular positions?
The response I have just had from him is that " that's where I want them and its not open to discussion" he seems oblivious to BS7671-2008 and EAWR 1989 and is a law unto himself. I have informed him that he will have to sign the certificate as he designed the installation and he is refusing point blank. Could be interesting when we come to sign off with Building Control
 
might be an idea to have a word with the building inspector. see if he can knock a bit of sense into the fartitect
 
The response I have just had from him is that " that's where I want them and its not open to discussion" he seems oblivious to BS7671-2008 and EAWR 1989 and is a law unto himself. I have informed him that he will have to sign the certificate as he designed the installation and he is refusing point blank. Could be interesting when we come to sign off with Building Control

I suspected that may have been the case - you come out with a load of regs and reasons why it shouldn't go there but his argument is he wants it there because he "just does and that's that".

As mentioned get him to sign as many waivers as you can to cover yourself (might even make him listen) and do what he wants, then if it hits the fan you can wave the waiver in his face and say "I told you so".
 
i hate people who choose where to fit the CU's!!! ARGH! looks nice of paper!!

recently been in a new build (2 weeks old) and reconfigured a lot of things as they were in stupid places!! and i still don't get this mounting of CU at waist height! what a load of tosh! perfect height for a kiddie to poke fingers in and mess about!
 
As far as I am aware, there is no exact mounting height for a CU.

This is the response from SELECT:-

There are no specific mounting heights for consumer units stated in either the IEE Regulations (BS7671) or in SBS Regulations.

However, BS7671:2008 - Regulation 132.12, requires that electrical equipment, which includes consumer units, should be accessible and should have sufficient space for inspection and testing etc. Therefore, consumer units should be mounted where they are readily accessible for such purposes. Mounting positions should be avoided where access is difficult i.e. some situations underneath stairs or high up on a wall
 
If thats what he wants thats what he want , just make him aware of the fact that he will have to sign the design section of the EIC , dont be nasty about it but ask him if he is qualified to do so .
If had the same sort of problems in the past and as soon as you mention signing certs they seem to go all coy, Architec's and interior designers only worry about 1 thing - asthetics
 
I think Part M plays a huge part.

I have installed CUs at a height of 500mm on new builds, although i did design the installation as well.

In most cases it was mounted back to back with the recessed meter box on the outside.
 
SBS Guidance


Electrical Fixtures
Outlets and controls of electrical fixtures and systems should be positioned at least 350 mm from any internal corner, projecting wall or similar obstruction and, unless the need for a higher location can be demonstrated, not more than 1.2 m above floor level. This would include fixtures such as sockets,switches, fire alarm call points and timer controls or programmers. Withinthis height range:



[FONT=Arial,Bold][FONT=Arial,Bold]• l[/FONT][/FONT]ight switches should be positioned at a height of between 900 mm and 1.1 m above floor level;
[FONT=Arial,Bold][FONT=Arial,Bold][/FONT][/FONT]standard switched or unswitched socket outlets and outlets for other services such as telephone or television should be positioned at least 400 mm above floor level. Above an obstruction, such as a worktop,fixtures should be at least 150 mm above the projecting surface.

Where socket outlets are concealed, such as to the rear of white goods in a kitchen, separate switching should be provided in an accessible position, to allow appliances to be isolated.

From the Scottish Building Standards handbook (2010), I will find a newer one if I can
 

Reply to Consume Unit position in new builds in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock