Hi all,

I have had two quotes on a consumer unit replacement which have both come in at a similar price (£10 difference) They are both recommended so no issues there.

However one has quoted for a Mk 10way AMD 3 circuit breaker consumer unit and the other has mentioned "Upgrade the consumer unit to a metal board fitted with individual RBCO's"

Are they both essentially the same? (I want to make sure we get the most for our money)

Thanks
 
Any AMD 3 board will be metal, however unless stated otherwise will be an MCB populated board, with RCD/s. The RCBO option would typically be more expensive but gives circuit level discrimination in a fault condition, rather than tripping half (or all) of the board.
 
AMD 3 stipulates Non combustible CUs within a Domestic Premises, the first quote doesn't say what type of OCPDs (circuit breakers) will be used the second mentions all RCBOs which are combined CBs and RCDs, so if an earth fault develops you will only lose that circuit with the fault on it.
I you went with an AMD 3 dual RCD CU and any of the circuits controlled by 1 of the RCDs then you would loose all the circuits protected by that RCD, if the CU has been connected up correctly, sometimes a crossed Neutral connection can cause both RCDs to trip, depends what make of RCBO CU the Electrician is supplying, most RCBO boards can a little bit more expensive. Hope my descrition is clear to you. Sorry wrong atatchment ignore Guide4
 

Attachments

  • Best-Practice-Guide-4-Issue-4.pdf
    1.2 MB · Views: 20
BG for the cheaper option. crabtree starbreaker if the job can stand the extra cost.
 
AMD 3 stipulates Non combustible CUs within a Domestic Premises, the first quote doesn't say what type of OCPDs (circuit breakers) will be used the second mentions all RCBOs which are combined CBs and RCDs, so if an earth fault develops you will only lose that circuit with the fault on it.
I you went with an AMD 3 dual RCD CU and any of the circuits controlled by 1 of the RCDs then you would loose all the circuits protected by that RCD, if the CU has been connected up correctly, sometimes a crossed Neutral connection can cause both RCDs to trip, depends what make of RCBO CU the Electrician is supplying, most RCBO boards can a little bit more expensive. Hope my descrition is clear to you. Sorry wrong atatchment ignore Guide4
 
Today I fitted a 12-way Contactum Defender, having not used this brand for a few years now. Mostly I was pleasantly surprised, nicer looking than their old metal ones, and fairly easy to install.

A couple of minor niggles - the knockouts were really difficult to knock out, and only has 3 mounting screw holes (sometimes one screw point can be over a missing bit of wall, so need more than 3 in case).

The MCBs look very much like BG, possibly they come from the same factory?
 
Today I fitted a 12-way Contactum Defender, having not used this brand for a few years now. Mostly I was pleasantly surprised, nicer looking than their old metal ones, and fairly easy to install.

A couple of minor niggles - the knockouts were really difficult to knock out, and only has 3 mounting screw holes (sometimes one screw point can be over a missing bit of wall, so need more than 3 in case).

The MCBs look very much like BG, possibly they come from the same factory?
I always use contactum now I find then very good and very reliable I've never had an rcd or rcbo fail any test. I agree they are hard to knock out but they are sturdy and well made
 
Today I fitted a 12-way Contactum Defender, having not used this brand for a few years now. Mostly I was pleasantly surprised, nicer looking than their old metal ones, and fairly easy to install.

A couple of minor niggles - the knockouts were really difficult to knock out, and only has 3 mounting screw holes (sometimes one screw point can be over a missing bit of wall, so need more than 3 in case).

The MCBs look very much like BG, possibly they come from the same factory?
The Contactum & BG Plastic CU's were identical bar the badge, the MCB's and RCD's are still identical bar the badge, the bare unit is now somewhat different.
 
Today I fitted a 12-way Contactum Defender, having not used this brand for a few years now. Mostly I was pleasantly surprised, nicer looking than their old metal ones, and fairly easy to install.

A couple of minor niggles - the knockouts were really difficult to knock out, and only has 3 mounting screw holes (sometimes one screw point can be over a missing bit of wall, so need more than 3 in case).

The MCBs look very much like BG, possibly they come from the same factory?
Drill some more fixing holes
 

Reply to Consumer Unit replacement in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I live in a flat in Scotland supplied with an old 2 meter system called THTC where one meter using a time signal supplied heating and hot water...
Replies
7
Views
1K
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K
Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock