kW)- True power ( x 1000 )
kVA)- Apparent power ( x 1000 )
kVAr)- Reactive power ( x 1000 )
Load )- The current drawn by ElectricalEquipment connected to an Electrical Circuit .
Prospective Short Circuit Current . – The maximum currentwhich could flow between live conductors . ( PSCC)
Prospective Fault Current - The highest current which could flow in a Circuit due to aFault . ( PFC )
Regulation612.11. Prospective FaultCurrent
(PFC ) → to any of ( PSCC ) or ( PEFC )
The ProspectiveShort Circuit Current & Prospective EarthFault Current shallbe Measured . ETC ( at the Origin ) – Consumer Unit / Tails
(PSCC ) – Line & Neutral
(PEFC ) – Line &Earth
Q)The Instrument to be used for a Polarity test . Before the Supply is connected. ?
A)This test is usually conducted while measuring the value of ( R1+ R2 ) where a Low Reading Ohm Meter is used .
(if conducted as a separate test any from of Continuity Tester is used )
O.S.G.p/77
( I must stress O.S.G. is Guidance only )
Guidanceon Initial Testing of Installations .
ii) Checking that the TestInstrument is made in accordance with the appropriate safety standards such as( BS-EN 61243-3for Two pole voltage detectors & ( BS-EN 61010 or BS-EN 61557 for Instruments .
iv) Observing the safetymeasures & procedures set out in HSE Guidance NoteGS-38 for all Instruments . Leads . Probes & Accessories . ETC .
O.S.G.with the Supply Connected
vi)Check “ Polarity “ of supply . using anApproved Voltage Indicator .
Q)An instrument that may be used for a “ Live “ Polarity Test – after the Supplyis connected .
A)A voltage indicator meeting the requirements of ( GS-38) HSE … This will come up a lot on “ Exams “( GS-38Leads )
Specification)- BS-EN 61243-3 : 1999 –Live working . Voltage detectors . Two-pole low voltage type .
Specification)- BS-EN 61010-1 : 2010 -Safety requirements for electrical equipment for measurement . Control . & Laboratory use ( General Requirements)
IfInstallation(s) are to be Tested to show that they complywith BS-7671 – The following instruments will be Necessary
Testing)- 612.1.
The test of Regulations 612.2. to 612.13.ETC.
Measuringinstruments & monitoring equipment & methods shall be chosen inaccordance with the relevant parts of ( BS-EN 61557 ) if other measuring equipmentis used . it shall provide NO LESS degree of performance & SAFETY .
- Lowrésistance ohmmeters . ( BS-EN 61557- 4 )
- Insulationrésistance ohmmeters . ( BS-EN 61557- 2 )
- Earthfault loop impedance testers ( BS-EN 61557- 3 )
- Earthelectrode résistance testers ( BS-EN 61557- 5 )
- RCDtesters ( BS-EN 61557- 6)
Insulation Résistance ( IR )
2392-10. Dead Test - Line& Neutral to be Linked out for this Test( Megger 1552 - Two lead(s) Lead one L&N )– Lead two Earth
Instrumentto be Used. ? … ( Insulation ResistanceTester ) for Exam purposes -&-s ►► PS NOT MEGGER
ElectricalInspection & Testing .
ContinuityTesting . ( Closed Circuit )
Examplelittle ( r[SUP]1[/SUP] ) end to endLine conductor ( Closed Circuit ) Youwill get a reading Ωs ?? ( r[SUP]1[/SUP]) to ( r[SUP]1[/SUP])
AnInspection & Test which is carried out on a NewInstallation to prove Compliance is called an InitialVerification .
( EIC ) The Electrical Installation Certificatemust be accompanied be a Schedule of Test results & Schedule of Inspection
Withoutthese two documents’ . The Electrical Installation Certificateis not Valid .
Regulation. Chapter 63 p/163 .
632.1. Initial Verification
Followingthe Initial Verification required by Chapter 61. anThe ElectricalInstallation Certificate. together with a Schedule of Inspections & Schedule of Test results .shall be given to the person ordering the work .
Thiscalculation is for BS-EN MCBs
MCBtype B . Time must be achieved when a currentof between ( 3 & 5) times its rating passes through it
MCBtype C . Time must be achieved when a currentof between ( 5 & 10) times its rating passes through it
MCBtype D . Time must be achieved when a currentof between ( 10 & 20) times its rating passes through it (disconnection of the device Ia )
Producetable(s) for Zs values . a specificvalue of current is required & the worst case is Used. ( B – 5 . C – 10 . D - 20 )
Whenthese values are used it is simply a case of ApplyingOhms Law – to the supply voltage 230V
&( Ia ) to obtain a ( Zs ) value
Thiscalculation will satisfy regulation 411.4.5. ( Zs x Ia ≤ Uo )
MCB– B : The ( Zs ) for a 20A type B ?? Calculated .
5 x 20= 100 … ( 230 ÷ 100 = 2.3Ω )
MCB– C : The ( Zs ) for a 20A type C ?? Calculated .
10 x 20 = 200 … ( 230 ÷ 200 = 1.15Ω )
MCB– D : The ( Zs ) for a 20A type D ?? Calculated .
20 x 20 = 400 … ( 230 ÷ 400 = 0.57Ω )
Working my way around the 17[SUP]th[/SUP] Edition.
Reduced– voltage transformer ( Centre Trapped ) ◄◄
(Zs ) values for Circuit Breakers ( Table 41.6 – p/54 )
( Calculatedin the same way as the Circuit Breakers ( Table 41.3 – p/49 )
The only difference is the Voltage ( 55V or 63.5V ) Table 41.6 : We arenot Calculating 230V ◄◄
32Atype B – MCB . ( 32 x 5 = 160 )
(55 ÷ 160 = 0.34Ω )
Maximum Earth Fault Loop Impedance ( Zs ) for 5 sec Etc
&Uo of ( 55V ) Single Phase .
&( 63.5V ) Three Phase
MCB– BS-EN 60898 & BS-EN 61009-1 protective devices . Usually have two short circuit capacitiesmarked on them .
(Icn ) Which is the rated Short Circuit Capacity – is the Maximum Current whichthe device could interrupt without causing ant damage to other Equipmentsurrounding it .
( Ics) Which is the ( In-service Rated Short Circuit Capacity ) is the Maximum Fault Current which the device could interrupt safetywhilst remaining safe to Use .
Itis better to select a device with an ( Ics )which is higher than the ( PFC ) as the devicewill still be fine for continued use .
( Markedon the MCB - Icn ?? 6000 or 10.000 )
BS-EN 61009-1 / RCBOs
Insulation Résistance : ( 3 Test ) Regulations . [ Testing IR at theMain Switch ]
Dead Test .
Safety Isolation Procedures’ . are required hereprier to Testing
This can be carried out at the “ Main Switch “ of the Consumer Unit being Tested . You mustmake sure that the Main Switch is on the ONposition with all the Circuit Breakersfor all the Circuits to be tested . in doing this you must ensure that “ Lamps . Dimmer Switches . & Appliancesare removed Prior to Testing .
• The Test is carried out between the Line & Neutral - using the Insulation Résistance Tester [ Megger ] Using the 500MΩ Volts scale
500V is applied – Your reading should be Greaterthan 999MΩ is Obtained .
• The Test is carried out between the Line & Earth -using the [ Megger 1552 ]
500V is applied – Your reading should be Greaterthan 999MΩ is Obtained .
• The Test is carried out between the Neutral & Earth -using the [ Megger 1552 ]
500V is applied – Your reading should be Greaterthan 999MΩ is Obtained .
Reason(s) :
This proofs that the Line& Neutral are not touching :
This proofs that the Neutralto Earth are not touching :
This proofs that the Line&Earth arenot touching : Throughout the Circuits’ .
Polarity ( 4 ) : This Test is the Forth Test . “ DeadTesting “ “ Wiring Regulations “
Safety Isolation Procedures’ . are required hereprier to Testing ☑
This Test is to ensure that all Switches Fuses& Circuit breaker are in the line conductorOnly & Socket-outlets are wired correctly . 612.6 ☑
• In this case am only Testing the Lighting Circuitonly . ↔ Polaritywould have been Tested through the Continuity Ring Final Circuit Test .
Very similar to Continuityof CPC. Although a read is not required . So the ( R1 plusR2 – Need Not be Recorded )
Consumer Unit – Inside . Having removed the Line Conductor from the circuit to be Tested . it isplaced into the Earth bar ( Met )
The Test Instrument to be used is then brought toeach point in the Lighting Circuit to ensure that Polarity is correct . while areading is not required this can be put on the Buzzer or Bell set mode . ↔ The Test is carried out between the Switch live & Earthat the Ceiling Roseor Batten Holder → with the Switch on the OFF position “ No Buzz “
Switch - the Switch ON it Indicates a Buzzing“ The polarityis correct . if this was carried out using a Low-résistance Ohmmeter thesame Test would show the meter reading from greater from scale ( 999MΩ ) down the a lowrésistance 0.15Ω in the same in the case of ( R1 plus R2 ) forContinuity of CPC
“ Useful Junk “
( 999MΩ ) megohms is a Near-perfect résistancereading for a Wire/Cable
The Megohmmeter . or Megger 1552 – multi function tester . is a measuring device thatTests high Electrical Résistance .
Typically these measurements aremade on Electrical Wires & Motor Winding to test the Insulation value ofthe wires . The prefix “ Meg ” describes a numerical value of 1.000.000. in thecase of an Ohmmeter that value is also described in Ohms .
An Electrical/ Electric terminal positive polarity 612.6 ☑
Continuity of CPC.(1 test ) : r[SUP]1[/SUP] & r[SUP]2 [/SUP].
Dead Test :
Safety Isolation Procedures’ . are required hereprier to Testing ☑
Continuity of CPC.Lighting circuit . having identified the right Circuit Breaker
i) Remove the Lineconductor from the Circuit breaker . Then place it into the Earth bar ( MET ) –Line & Earthtogether
if we look at the Test books some indicate the Link between the top of the Circuit breaker to the Earth bar .
ii) Some indicate the CPCfor that circuit is removed & the Line removed& placed into a connectorblock [ anyone of the will do ] “ Loop “
You must go to the furthest point . & With aTest Instrument low-ohmmeter place it on the Low-ohms scale ( Ω ) The Test isthen taken between the CPC & Line conductor at theCeiling Rose :- in this case a reading of .16Ω that is obtained. proofs continuity of the CPC .
• To proof and theory to the ↔ Consumer Unit breakthe Line conductor go back & take a reading . [ it shows greater than rangeproving continuity was CPC was Testedinitially ]
The PSC { prospective short circuit current }is the maximum available current which can flow in the event of a fault betweenLive conductors { Line – Line } or { Line – Neutral } it iseither directly measuredor if your meterwon’t do direct { Line –Line} then
{ Line – Neutral doubled will suffice }
Line & Neutralcables are ShortedCircuited is called the Prospective Short Circuit Current PSCC .
PSC ↔ ( MCB ) ↔ Protectivedevice must be capable of breaking it Safely ◄ ≈ A.C. Sign .
PFeC { prospective earthfault current } is the maximum fault current between a Liveconductor and earth . { Fault Current is ShortCircuit }
This can measured directly or
by dividing the maximum Line– Earth supply voltage by ( Ze )
PFC {prospective short circuit current } is either the PSCC or PEFC . Whichever isGreater .
By Calculation’s to Obtain PSCC { 230 ÷ by Ze 0.15Ω = 1.53kA } Supply has been connected .
{ 400V ÷ Ze 0.15Ω = 2.6kA }
When we are referring to Design ! Designing for an Installation for Domestic . Design stage – Design purposes.
Broken RingFinal Circuit ? ( As a Tester this is what -&-s arelooking for )
However . We find the Ring to be Broken . the Protective Device couldnot do it’s job as it is rated at 32A & the cable is rated only at 20A .Hence Overloading .
TheRing ? becomes Two Overload Radial . ( From a Tester point of View )
TheRing is a Continuous Loopno matter how it has been designed
p/362)- Appendix 15 ( Informative ↔ telling us )
Ring& Radial circuit arrangements
1) Ring Final Circuit arrangements Regulation– 433.1.
( Informative ↔ telling us )
TheLoad current in any part of the circuit should be ( Unlikely) to exceed for long periods the current carrying capacity of the cable ( Unbroken Ring Final Circuit )
Regulation– 433.1. refers ) This can generally be achieved by .
iv)Taking account of the total floor area being served ( The Regulations aresaying - Rule of Thumb . a Limit of 100m[SUP]2[/SUP][SUP] [/SUP] has been adopted) Ring
Nowif we look at the O.S.G. p/158 . A1 Ring 30 or 32A . 2.5 / 1.5 . – Maximum floorarea served ( m[SUP]2[/SUP] ) 100m[SUP]2 [/SUP]
i)locating socket outlets to provide reasonable sharingof the load around the ring .
Consumer Unit Arrangements . Design Stage .
Part “ M “ requires that reasonable provision be made for people togain Access to a building and use its Facilities .
Prescribes that Switches . Sockets outlets . &“ Other Equipment “needs to be at Appropriate Heights .
Wording → “ Other Equipment“ Consumer Unit . Height of between 0.45m from the floor level Up . 0.⇈ to 0.45m ↳ 0.45m to ↱1.2m from floor level .
2392-10 .
Who is responsible for Inspection & Testing .? The person carrying out the Inspection( YOU )
Remember ? Inspection& Testing . are two different words ( Inspection ) ( Testing )
2392-10 )- Work Near Electricity “ Assessor “
You are doing a ►► Risk Assessment
Introduction to Short Electrical Training :
2391-10 – 2392-10 –
All Dead Testing should have Safety IsolationProcedures’ prier to Testing .
Safety Isolation Procedures’ . are required hereprier to all Testing ☑
All Dead Testingshould have Safety Isolation Procedures’ prier to Testing .
i) Using GS-38 Prove Test Leads .
ii) first thing to do is Isolate the Supply . That is going to beTested . - Take the GS-38 test leads to a known sourceto ensure that theyoperate correctly
“ if they are workingaright “ they go tothe supply that is to be Tested – then Test between Line to Neutral - Line to Earth - Neutral to Earth .
iii) Then the Test Leads are replied to a known source to ensure that they are still Operatingcorrectly .
iv) At this stage you are placing a Locking OFF- device – followed by Signs in the area that is tobe Tested .
Execution:
SinglePole ( 1P )
SinglePole & Neutral ( 1P + N )
DoublePole ( 2P )
ThreePole ( 3P )
ThreePole & Neutral ( 3P+N )
FourPole ( 4P )
ElectricalEndurance : MCB
≥32A .. Over .
≤32A .. Under .
AmbientWorking Temperature ( °C )
Part( 1 ) Sorry am having problemdownloading Amber .
DomesticInstallation )- 2392-10 . “ Electrical Calculations’ “
100A supply . ( Scenario )
ElectricShower 50A : ( Power Circuit )
Cooker– 32A :
RingFinal Circuit ( 1 ) 32A :
RingFinal Circuit ( 2 ) 32A :
ImmersionHeater 16A :
UpstairsLighting 6A :
DownstairsLighting 6A :
Add )- up the requirements ofEach Circuit ( 50A + 32A + 32A + 32A + 16A+ 6A = Total Demand 174A )
►►This is because the CIRCUITS are RARELY LOADED to theirFULL CAPACITY . ◄◄ at the One Time
Apprentices. You are Using the Principle of Diversity
Note )- NOT Total Demand 174A
Shower )- Classed as Instantaneous Water Heater )- O.S.G. Table 1B – p97
Row– ( 5 ) NO DEVIRSITY . Plain English 100%
Apprentices. Only the rated LOAD of the Appliance should BE USED …….. ( NOT the RATING of the PROTECTIVE DEVICE ) ◄◄◄ MCB
Shower[ 10.000 ÷ 230V = 43.47A ] Power Circuit.
Cooker)- As a designer . Would you apply Diversity ( YES )
1x 4 kW – Oven :
2x 1.5kW – Hob/rings :
1x 2kW Hob/ring :
1x 1kW Hob/ring :
1x 2kW – Grill :
Totalpower required = 12kW … 12.000 )
TotalLoad ( Amps ) - 12.000 ÷ 230V = 52A
Itis NOT likely that all of the elements of the Cookerwill be Used at the same time .
Dueto the required cooking times of the food the Oven will be On first . & itwill have reached its required temperature before the Hobs are Used .
[The Cooker will have ( Thermostats & SimmerStats build into it which will Switch ON & OFF to maintain the Cooking Temperatures ]
Asform a Designer point of View ? For aShort periods of time an Overload could Occur ) if all Loads on at the SameTime . Xmas Time .
Regulation133.1.1. – Selection of Electrical Equipment . Every item of equipment shall COMPLY with the appropriate BritishStandard .
RegulationBS-7671:2008 . Suggest that a small Overload isbetween ( 1.25 & 1.45A )
RegulationBS-7671:2008 . Protective Devices have toCOMPLY with certain requirements .
(Table 41.3 – p/49 . MCB / RCBOs ) … RCBOs are – MCB/RCDs in One ) Overload & / or Short Circuit :
BS-EN60898 & BS-EN 61009-1 … Protective Devices must CARRY a CURRRENT of atLEAST ( 1.13 times the device rating for 1 hourwithout operating -
Theymust OPERATE within 1 hour at a Maximumof ( 1.45 times their Rating )
Part( 2 ) Sorry am having problemdownloading
“ UsefulJunk “
Apprentices, The current which causes Operation of the PROTECTIVEDEVICE in the conventional timeis Shown by the Symbol ( I[SUP]2[/SUP] )
Diversitycan now be applied .
RingCircuit(s) – O.S.G. . Table 1B - row 9.. ( Only Applies to Domestic Installations ) 2392-10
Diversityis Calculated at 100% .. for circuit ( 1 ) & 40% for circuit ( 2 ) – Plain English Largest / 100% - Second / 40%
O.S.G.– Table 1B row 9 . Ring ( 1 ) Largest / 100% - 32A
O.S.G.– Table 1B row 9 . Ring ( 2 ) Second / 40% ( by Calculations 40% is 0.4 = )
Nowthe Calculation is ( 32A x 40% = 12.8A ) 32A x 0.4 = 12.8A
PlainEnglish Largest / Second .. ( 32 + 12.8 = 44.8A ) → Total allowance for Ring =44.8A
O.S.G.the hint is in the Name 1B ? Immersion Heaters & Thermostatically controlled Water Heater )- NO Diversity
Atthis Stage I must point out )- O.S.G. 1B– Individual Household Installations ( 2392-10Domestic Installation(s) Top of Page .Look PS. That’s what you are Applying
Apprentices)- Only the Total Load should be Calculated . Immersion Heater … ( 3000 ÷ 230V= 13A )
Note: Domestic / 100A . Single Phase
Lightingcan be Calculated using ( 66% ) of the Total Demand.
Twolighting circuits at 6A = 12A … [ 12 x 66% = 7.92A ]
(MD ) Maximum Demand for your Installation is [ 43.37A – Shower : 32A – Cooker : Ring Circuits – 42.8A : Immersion heater 13A : Lighting 7.92A :
Apprentices?? What is the MaximumDemand used Now ??? 43.37+ 32 + 42.8 + 13 + 7.92 = 139.09A
DomesticInstallation(s) Ring Final Circuits areNOT fully Loaded
DomesticInstallation(s) Shower(s) are used for avery short time .
DomesticInstallation(s) Lights are NOT all on atthe same time . Yeah
DomesticInstallation(s) Cooker is Why diversity can be Used
ExternalEarth Fault Loop Impedance ( Ze )
Thisis the Résistance between Live Conductors & Earth
Remember)- You have Résistance in every Cable .
p/161- 612.11.ProspectiveFault Current .ETC.
Itcan be Obtained by ( Measurement ) ( Enquiry ) (Calculation )
230V/ 400V . protected at the Supply cut-out by Fuses [ BS-1361 type 2 : BS-88-2 : BS-88-6 : ??
( Enquiry )
TTSystem - 21Ω . → Apprentices . O.S.G.- p/11
TN-S - 0.8Ω
TN-C-S– 0.35Ω
Calculationsfor cable size . can be carried out using these values . it is Important toMeasure these values before allowing the Installation to be put into Service .
PLEASE NOTE )- The Only system for which calculation of ( Ze) would be possible is a ( TN-C-S system )
Thisis because the Fault Path External to the Installation is the same for both (PSCC ) & ( PEFC ) - Prospective EarthFault Current
Forthis Calculation to be carried out ( The value of ►► PSCC between Line & Neutral shouldbe Known .
Ohm’sLaw )- Uo / Ze = PSCC .
Symbols’used in the Regulations - p/36
(Uo ) Nominal A.C. rms Line Voltage to Earth ( V )
(Ze ) That part of the Earth Fault Loop Impedance which is External to the Installation . ( Ωs )
HiBruce .
Electricians’.
:19:
Lighting Protective System .Should be considered with regard to Bonding .
Theperson carrying out the WORK has a full Understanding of ( BS-EN 62305 )
2392-10:
BS-7671:2008 . Only provides us with Informationwhich is relevant to Equipment which we could purchase & fit at the time itwas published .
Regulations)- Table 41.3 . Example – BS-EN 60898MCBs . BS-EN 61009-1 – RCBOs
Why?? for us . To use different ProtectiveDevice(s) to be used on Domestic Installation(s) Why ? We have different types of Levels of OVERLOAD .
MCBs- B – C – D .
UsefulJunk
( A ) is NOT used asIDENTIFICATION as it could be CONFUSEDwith the CURRENT RATING of the DEVICE .
No Insulation has ( Infinite Résistance ) is perfect . ( IR ) Insulation Résistance
Youcan get Small Amounts of Electricity flowing along & through Insulation to Ground/ Earth
( IR ) Insulation Résistance
CommonSense tells us that the more Voltage we have .The more Current there’ll be .
TheLower the Résistance of the Cable/ Wire – The more Current for the same Voltage.
Whatmakes Insulation GO bad ? Just one Example .Yeah
:45:
GoodInsulation has High Résistance .
PoorInsulation . relatively Low Résistance .
Dependingupon such factors as the Temperature or Moisture content of the Insulation [ Résistance decreasesin Temperature or Moisture]
Combinedwith the Electrical Stresses that Exist ??
Asa Pin Hole(s) or Crack(s) develop. Moisture &foreign penetrate the surface(s) of the Insulation . ( Providing a Low Résistancepath for Leakage Current )
PowerCables : 2392-10 : Insulation Résistance
Whentesting Cables . ( Fault Finding ) it is Usuallybest to disconnect at Both Ends in Order to Test the Cable by itself .
UsefulJunk . ( IR )
Formany years One – Megohm has been Widelyused as a fair allowable lower limit for Insulation Résistance of OrdinaryIndustrial Electrical Equipment
Ratedup to ( 1000 Volts ) PS – Wording Above 500V - 1000V
Regulation. Table 61 – p/158 . Will Reinforce this Matter .
Apprentices> When a Measurement of ( PFC ) is taken as Close to the Supply Intake asPossible . ( Meaning !! At the Origin )
Apprentices> The 5 xtimes test must Only be carried out on RCDs with trip ratings ( I∆n ) up to 30mA -&-sQ/As ( Or less 30mA )
Apprentices> Maximum ( Zs ) What is the Measured value of ( Zs ) for anAltered Circuit ? A ) That it is Lowerthan the Maximum Permitted Value .
Designing: Supply Characteristics .
Natureof Supply Parameters [ This can be gained by Enquiry or Measurement ]
U )-Is Line to Line orLine .
Uo)- is Lineto Earth
Symbolsused in the Regulation . p/36 )- U . Voltage betweenLines . ( V )
Uo)- is Lineto Earth ( V )
Electricityonly has Current when it is on the move . Yeah .
Formulafor Inductive Reactance : XL = 2πƒL
Thereare 4-factors thatdetermine the Résistance of a material :
1)Type of material :
Therésistance of various types of materials are different . for instance . gold isa better conductor of electricity than copper . & therefore has lessrésistance .
2)Length :
Therésistance of a material is directly proportional to it’s length . The longerthe material is . the more résistance it has . This is because the electronsmust flow through more material . & therefore meets more friction over theentire distance .
3)Cross-Sectional Area :
Therésistance of a material is inversely proportional to the cross sectional areaof the material . This means that the thicker the substance is across . thelower the résistance .
Thisis because the larger the cross sectional area is . the less friction there isover a given length [ picture in your mind . if you will . that a fire hosewill pass more water than a garden hose . because the wider the pipe . the lessrésistance it has ]
4)Temperature :
Invarious types of materials . résistance can vary inversely or directly with thetemperature . This is because of the chemical properties of the material . incarbon . for instance . the résistance decreases as the temperature rises . Sowe say it varies inversely . in copper . however . the opposite is true . withthe rise in temperature . we have a rise in the résistance .
* So not only can résistancechange with heat . but causes heat as well .
Regulation705.512.2. External Influences :
( Agricultural & HorticulturalPremises)
Callsfor all equipment to have a degree of Ingress Protection of at least ( IP44 ) for protection against water splashing from any direction .
Wheremore Onerous Environmental Conditions Apply ?? Higher degree of IngressProtection will be required .
Compliance: Regulation 705.512.2. )- Where equipment of ( IP44) rating is NOT available . it shall be placedin an EnclosureComplyingwith ( IP44 ) ◄◄
IPX5)- Protection against Water Jets from anydirection ( Note : Under stated conditions )
IPX6)- Protection against Powerful Water Jets fromany direction
IPX7)- Protection against the effects of TemporaryImmersion in Water .
IPX8)- Protection against the effects of Continuous Immersionin Water .
arty:
Apprentices& 2392-10 )- Please take the Time to Read
:24:
This Test is Conducted on Domestic Installations .
I do this Test First . Why ??To make sure that I have a Earth returning back to Transformer Windings . External
BeforeI connect up My Earthing to the Consumer Unit.
TestSequence & Descriptions .
Thefollowing Test(s) are carried out with the SupplySwitchedOFF
ExternalEarth Fault Loop Impedance . ( Ze )
TheReason behind this Method )- To establish that a good Earth Exists at the Installation in Order for theremaining Test(s) to go ahead.
ProspectiveFault Current . ( PFC )
612.11.)- Protective EarthFault Current shall be Measured .
Bydoing this Test you have to Remove (Disconnect the Main Protective Bonding Conductor ) Earth – from the ( MET ) in the Consumer Unit . ( MET – MainEarthing Terminal)
TheReason behind this Method )- You are Removing Parallel Earth Paths . ◄◄◄◄
ByTesting the Line & Earth. You have a straight path to back to the Transformer Windings .
(Ze ) Measured at the Supply Position .
Onelead on ( The Disconnect the Main Protective BondingConductor ) Earth
&the Other Lead on ( At the Top of Main Switch ) Line
Younow have a Closed Circuit . ( Protective Earth Fault Current shall be Measured )
Itis one off the Easiest of all Test(s)
Line & Earth cable Only which has been Removed from ( MET ) Simple -&-s will pick your Brains on this ◄ 2392-10
-&-s)- The following Test(s) are carried out with the SupplySwitchedOFF ◄
Apprentices( What is Ze I hear you Say ??? )
Symbolsused in the Regulation . p/36 .
Thatpart of the Earth Fault Loop Impedance whichis External to the Installation ( Ωs )
Apprentices: Basics
Rememberthat the : 17[SUP]th[/SUP] Edition – is British Standard :iagree:
Meaning)- ( R1 +R2 ) …. Line / R1
Meaning)- ( R1 + R2) …. CPC / R2
Putthe two together . You have ( Line / CPC ) ↔ ( Line - R1 + CPC - R2 )
Inany Exam . The Regulations will get you out of Trouble .
Toconfirm This .
Symbolsused in the Regulations p/36
( R1 ) – Résistance of the Line Conductorof a Distribution or Final Circuit (Unit Ω )
TheRegulations are pointing you to . Appx 4 – Schedule of Test Results .
Symbolsused in the Regulations p/36
( R2 ) – Résistance of the CircuitProtective Conductor→( CPC )of a Distribution or Final Circuit ( Unit Ω )
TheRegulations are pointing you to . Appx 4 – Schedule of Test Results .
(Ze ) External to the Installation p/36
Meaning )- Outside of theBuilding → Ze ] ↔ [ Zs Inside of Building.
(Ze ) You are checking that you have agood Earth from the Transformers Winding
(Zs ) You are checking That your Installationis Earthed →(Zs ) 612.9 – The Earth Fault Loop Impedance . is required to be determined forthe furthest point of each circuit
-&-s You will be asked the Qs ) Formula Calculating Earth Loop Impedance . itwill be the Option of 4 Qs ) mixed up .
( Zs = Ze + R1 + R2) ◄◄ This Qs is the start of Testing Calculation(s) for 2392-10
The colour has been added for Clarity
ApprenticesBasics
LearningCurve
Regulation(s)p/333
( EIC ) Electrical Installation Certificate
Weare looking under ( Main Protective Conductors )
EarthingConductor : - Material( Copper ) C.S.A ( 10mm[SUP]2[/SUP] ) … Connection Verified Tick inbox
MainProtective Bonding Conductors : - Material (Copper ) C.S.A ( 16mm[SUP]2[/SUP] ) … Connection Verified Tick inbox
Youare Confirming )- To incoming Water & / or Gas service … ConnectionVerified Tick inbox
TheEarthing is very Important in any Installation/ or Jobs
Pointto Note : Please mark your Earthing in ConsumerUnit ?? Gas / Water ( White InsulatingTape . Why ?? if you have to come backfor any Reason you can Indentify for Testing reason . Testing comes under Common Sense . Yeah
Remember that the Certificationis you Proof in a court of Law i) Your complied with British Standards . ii)As a Competent Person . Tester .
:35:
Testing. Yes this will come up on 2392-10 -&-s Q/As
Initial Verification – New Installation ( Certificate )
Regulation632.4.
All)- defects or omissions revealed during Inspection & Testing of theInstallation work covered by the ( Certificate ) shallbe made good before the Certificate is issued
PlainEnglish : The regulation(s) are telling you to Cover you But .
Electricians’are not Perfect 99.9% . mistakes can bemade accidently . The Reason for Testingin Order from the Regulation(s) is that every test has a reason(s) ??
TheRegulation(s) prescribed Tests . Etc
612.2.1.Continuity of ProtectiveConductors ( Dead Test) Do we have Earthing ?? ETC .
612.2.2.Continuity of Ring Final Circuit Conductor( Dead Test ) is the Ring a Complete Loop?? ETC . Do we have reverse Polarity
612.3.2.Insulation Résistance ( Dead Test ) has the cable been damaged ?? L/N – E . Megger 1552 two leads .
500V≥ 1.0MΩ ( Mains ) 2 x 230V = 460 / 500V ( your fire up doublethe Voltage ) Testing the Cable only
SELV: = 50V .A.C. = 250V D.C. ≥ 0.5MΩ
(They are only three Qs on this matter ( Table 61 – p/158 – ( 250V ≥ 0.5MΩ ) ( 500V ≥ 1.0MΩ ) ( above 500V – 1000 ≥ 1.0MΩ )
Look at the Wording . SELV / (250V ≥ 0.5MΩ )
2392-10)- Testing Q/As -&-s Yes ◄
612.3.3.Where the circuit includes ELECTRONICE DEVICESwhich are LIKELY to INFLUENCEthe results or be DAMAGED.
Onlya MEASUREMENT between the LINE conductors connected together & the EARTHING ARRANGEMENT shall be MADE . ( L& E ) Only
Nowthe Regulations are TELLING us ????? ( CoverourButs )
NOTE 1 )- AdditionalPrecautions . such as ( DISCONNECTION ) may be NECESSARY to avoid damage to ELECTRONICEDEVICES
Nowwe can say Informative
Apprentice’sBasics .
Continuityof Protective Conductors . 612.2.1.
Method 1 )- ( R1 + R2 ) Line / CPC → This also proves Polarity
Method 2)- ( Measurement of R2 → or Bonding ) R2 / Wander Lead
Point to Note )- Test Voltages & Minimum Insulation Résistance .
Table 61 – p/158 - 500V to 1000V ( Above )
613.3.1. Insulation Résistance ( Domestic Installation - 500V between Live conductor(s)where appropriate during this measurement . Line & Neutral may be connected together . L/N –E separate
RingFinal Circuit ( DeadTest ) Loop Testing
Thereason behind this Test !!
RingLoop Testing ensures that any Ring Circuits wired in the Installation you havecreated are actually a ( RING CIRCUIT ) & not forming a ( Radial )
“ Figure of Eight loop “
Testing must include the relevantTests from the following Checklist ( 612. )
O.S.G.(- When a Test shows a failure to comply . The installation must be corrected .The test must then be Repeated . As must any earlier test could have beeninfluenced by the failure .
Itthen chases onto the Regulation(s) 612.1.
TheTests of regulation(s) 612.2. to 612.13. where relevant . Shall be carried out &the results compared with relevant Criteria .
TheRegulation are telling us in Order . each test has its Reason
Apprentices. O.S.G. p/80 – 2392-10 will use this system
Continuityof Ring Final Circuit Conductors . p/80 – A Three-step Test is required to Verify the Continuity of the Line . Neutral & Protective conductors & the correct wiring ofthe Ring Final Circuit . Etc
Step1 )- p/81 / End to End ( MeasuredSeparately ) L/N/CPC
Step2 )- p/81
Step3 )- p/82
Youwill see ?? ( Little r[SUP]1[/SUP]+ r[SUP]2[/SUP] ) don’t get confused with ( R1 + R2 )
2392-10: NEW
Purposeof Initial Verification .
InitialVerification . in the context of Regulation 610.1.is intended to confirm that the Installation complies with the Design & hasbeen Designed & constructed in Accordance .
610.1. ) 611.2. ) 612.1. )
2392-10: ( T )
Certificates
Appendix6 of BS-7671 contains Three model forms for the Initial Certification of a ( NEW ) Installation or for an Alteration or Addition toan existing installation as follows.
Ambringing you to the Point )- Single Signature ( ElectricalInstallation Certificate)- That is you 2392-10
WhereDesign . Construction . Inspection & Testing are the RESPONSIBLY of ONE PERSON )- That is you 2392-10
ACertificate with a Single Signature MAY REPLACEthe MULTIPLE SIGNATURE form ◄◄◄
:iagree:
2392-10: This will come up -&-s
:sweatdrop:
Regulationp/339 . ( PIR)
Periodic Inspection Report .
Regulations )- row 5 . The “ Extent& Limitations “ box should fullyIndentify the elements of the Installation that are covered by the report &those that are not . This aspect having been agreed with the CLIENT & other interested parties before the Inspection & Testingis CARRIED OUT .
Tester. GN-3 p/19 .
Scope)- it is essential that the Inspector & the Person ordering the Inspectionknown the “ Extent “ of the Installation to beInspected & any Criteria regarding the “ Limit“ of the Inspection . ( BOTH should be AGREED & RECORDEDon the CERTIFICATE )
Regulation)- Schedule of Inspections P/340
Bottomof Page ??
NOTES : ( LIM ) ◄◄ -&-s/ Big time . PS trip up Q .
ToIndicate that . exceptionally . a “ LIMITATION“ agreed with the person ordering the work preventedthe Inspection being carried out ( Applicable for a PeriodicInspection Only )
2392-10: ( ADS )
:iagree:
TestingRCDs
Wherean RCD has a rated value of ( I∆n ) not exceeding ( 30mA ) & is used toprovide Additional Protection to BASIC PROTECTION the operating time of the device mustnot exceed ( 40mS ) when subject to a Test Current of ( 5 x I∆n )
2392-10:
Example Only . -&- ( 2 Seconds time ) GN-3 . p/56
Generalpurpose RCDs to BS 4293 .
Becauseof the variability of the time delay it is not possibly to specify a maximumtest time . it is therefore imperative that the circuit protective conductordoes not rise more that 50V above Earth potential ( Zs I∆n ≤ 50V ) it issuggested that in practice a ( 2 second )maximum test time is SUFFICENT . -&-s now you know
2392-10: Get your self a copy of ( GN-3 )
FunctionalTesting .
Operationof residual current devices .
Whilethe following tests are NOT a specific requirement of BS-7671 it is recommendedthat they are carried out . GN-3 . p/56
Q)Prior to these RCD tests it is Essential for Safety Reasons , that the EARTH LOOP IMPEDANCE is tested to check the requirements’have been met . WHY ??
( Wehave a Earth ) .. Common sense . RCD must havean Earth ( 612.9↔ 612.10 )
2392-10: 612.6.
4 different scenarios . requirea Polarity Test .
i)- Unit used ( Ω ) All single pole devices & circuit breakers are connected inthe Line conductor Only .
ii)- Unit used ( Ω ) The line conductor must be connected to the centre terminal ofan Edison Screw Lamp holder ( with the Exception of E14& E27 lampholders to BS-EN 60238 )These are European . They have known to be usedon exams .
iii)- Unit used ( Ω ) All polarities of Socket outlets ( Ring & Radial must be Verified )
O.S.G. – p/78 ↓
iv)- Unit used ( Ω ) The Polarity of the mains supply must be correct . [ Using anapproved voltage tester ] with the supplyconnected
Apprentices)- ( MCB ) - Each protective device in a consumer unit is Classified as a “ WAY “ . We have 12 Way – ConsumerUnit ( CU )
Apprentices)- Continuity of Main Protective BondingConductor . ( PIR )
Alot off you will have a Multi Function Tester ( At this point you have zero the Megger to the test leads .
(for the sake of -&-s . if you don’t have a Megger ? you do it the old fashion way “ Subtract Leads“ Leads 0.02 – reading 0.4 = 0.38Ω ) you may get asked this one ??
i) Isolate Main Supply . ( Lock OFF )
( R2 ) - 612.2.1.
ii)Disconnect Bonding Conductor from Main Earth Terminal ( MET )
iii)Place One lead on conductor & other on the Earth Clampconnection ( you Using Wandering Lead )
Bonding Conductor → to Water pipe ( you have A to B – continues Loop )
iv)Zero lead Résistance & set to Ω
v)Take reading ensuring Less than ( 0.05Ω )
( Remember to replace Disconnect Bonding Conductor fromMain Earth Terminal ( MET ) BACKwhen Testing is Done )
UsefulJunk .
UnderFault conditions the Fault current should flow in a controlled manner through aCPC.
Oneother way of looking at this . A “Dedicated “ CPC would carry most of the fault current as it provides the mostdirect path & lowest Impedance back to the source of energy .
InitialVerification : Apprentices’
610.1. Wording .
EveryInstallation shall . DURING ERECTION ◄◄◄ ( And )on Completion BEFORE BEING PUT INTO SERVICE ◄◄◄ .be Inspected & Tested to VERIFY .Etc
PlainEnglish : Test it whilst your working on the Job .
Apprentices’: Basics . Yeah Reg – P/35
Youmust understand the basics .
Listedbelow are 4 terms that describe vital information in the Calculation process .
Thefirst factor you need to consider is ( DESIGN CURRENT)
17[SUP]th[/SUP]Edition - ( Ib) Design current of circuit
PlainEnglish ( Ib) Term used to describe a circuits DESIGN current in AMPS (The Load )
( In ) Rated current or current setting of PROTECTIVE device AMPS
17[SUP]th[/SUP]Edition - ( Iz) Current-carrying capacity of a cable for continuous service under theparticular installation conditions concerned .
PlainEnglish ( Iz) Term used to describe a circuits value in AMPS . once all de-rating factorshave been considered .
17[SUP]th[/SUP]Edition - ( It )Tabulated current-carrying capacity of a cable .
PlainEnglish ( It) Term used to describe the Tabulated current rating of a cable in AMPS ( The CURRENT a cable can SEFELYCARRY )
(Ib ≤ In ≤ Iz ≤ It )
Thisformula states the underlying principle of the calculation of a circuits CableSize .
Theprotective device current rating must be ( Equal to or Next Largest Size ) so that the circuit issufficiently protected
Formula)- used for cable calculation .
(Ib ≤ In then Iz ≤ It )
TheOver current protective device must be ( Equal to or Greater ) than the designcurrent .
Howto Establish the value of Volt Drop ( Vd ) Red Book BS-7671:2008
Eachcable rating in the Tables of Appendix 4 of BS-7671:2008
Hasa corresponding volt drop figure in mili-volts per metre of run ( mV/A/m )
Tocalculate the cable volt-drop ??
Volt-drop= Ib x ( mV/A/m ) x L ÷ 1000
Where.
Ib)- Design current in amps .
mV/A/m)- The mili-volts per amp per metre dropped
L)- The circuit length in metres .
► 1000 )- Converts the mili-volts into Volts ◄
Scenario : ◄◄
4.0mm[SUP]2[/SUP]PVC sheathed circuit feeds a ( 6kWshower ) & has a length of run of ( 16m ) Find the total Voltage Drop . ( Vd )
i)-Work out the Design Current . ( I = P/V = 6000 ÷230V = 26.08A ) ◄ Round up to 4– 26.08695652
ii)Obtain the . mV/A/m from Appendix 4
Table( 4D5 ) p/282 .
Thevolt drop figure for ( 4.0mm[SUP]2[/SUP] T&E is 11 mV/A/m )
iii)Input all the values into the Formula & work out the Volt drop to ( Twodecimal places & add the value V )
Voltdrop = 26.08 x 11 x 16 ÷ 1000 = 4.59V
Sincethe Permissible volt drop in this Instance is ( 5% of 230V ) which is ( 11.5V ) Now does the cable in Question meet volt droprequirements . ??
( 4D5 ) p/282
FlatPVC Cables .
Earth Loop Impedance . 2392-10
Résistance ( Measured in Ohm’s )
Isthe property of a conductor to limit the flow of current through it when avoltage is APPLIIED . The larger the conductor is the less résistance it has .
Thesmaller the conductor is the more résistance it has . .
(Thus . a voltage of one volt applied to one ohm résistance results in a currentof one ampere ) Yeah
2391-10 / 2392-10
Multipliersare used by the Designer & are required toallow for one of the following .
O.S.G.Table 9B )-
Usedso the Designer can give values of Résistance at the Ambient Temperatureexpected during the Test(s) ( 20°C is classed as1 )
O.S.G.Table 9C )-
Usedso the Designer can give values of Résistance at the Conductors Maximum OperatingTemperatures .
Reply to ***Cont../ Useful Information for Electricians & Apprentices*** in the Australia area at ElectriciansForums.net
I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Hi all,
My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
I've just spent an hour getting bogged down with the maths trying to work out diversity for 2 cooking appliances on the same circuit (32A MCB)...
Greetings everyone. My first post here, having read a similar thread, I understand that following the manufacturers guidance is all important...
Hi
First time with this kind of a job for me.
I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a...