Hi guys and gals, I am struggling to figure out how to achieve what seems to be a simple control circuit. I’ve wired a test rig and the system works as expected apart from the lamp not illuminating! What I am trying to achieve is a 13amp socket controlled contactor. Part of the control circuit will be a 230v 15watt warning lamp, once the lamp blows or is removed the contactor will drop thus de-energising the 13amp socket. When tested the lamp glows ever so slightly so obviously there’s an issue with such a high resistance of the contactor coil! Is there a different type of coil available on the market with a lower resistance? Is there another method that I’m not thinking of? Advice would be much appreciated. Thanks in advance.
 
How are you trying to achieve this at the moment?
A sketch of your circuit would be interesting to see as what you are trying to do is not as easy as it seems.
 
Hi guys and gals, I am struggling to figure out how to achieve what seems to be a simple control circuit. I’ve wired a test rig and the system works as expected apart from the lamp not illuminating! What I am trying to achieve is a 13amp socket controlled contactor. Part of the control circuit will be a 230v 15watt warning lamp, once the lamp blows or is removed the contactor will drop thus de-energising the 13amp socket. When tested the lamp glows ever so slightly so obviously there’s an issue with such a high resistance of the contactor coil! Is there a different type of coil available on the market with a lower resistance? Is there another method that I’m not thinking of? Advice would be much appreciated. Thanks in advance.

You have lamp and contactor coil in series.....you have a dim lamp......what do you think is happening! :)
 
Last edited:
@Andy-1960 beat me to the punch, I'd be using a current sensing relay. Have its control contacts cut the contactor if your indicator lamp burns out.

If you need to run a lamp in series with the coil, you'll need to very carefully balance the current & voltage ratings to give reliable operation, a non-trivial challenge without detailed specs.
 
@Andy-1960 beat me to the punch, I'd be using a current sensing relay. Have its control contacts cut the contactor if your indicator lamp burns out.

If you need to run a lamp in series with the coil, you'll need to very carefully balance the current & voltage ratings to give reliable operation, a non-trivial challenge without detailed specs.
Yes buddy this would be as close as I have got so far.
 
These machines are used by trained professionals. We’re are simply talking about a power supply, a contactor and a warning light. Once energised these mobile machines have to be activated by competent persons.

I think the point we're trying to make is... if this warning light is the only thing standing between a non-competent person getting an unwanted dose of x-rays and them not, then it needs to be pretty bullet proof in terms of reliability.

I'd be thinking multiple lamps, possibly two sense relays and two contactors to provide some level of fail safe setup.

There are special relays I believe that are designed for use in safety solutions that basically prevent operation if a component fails, but machine safety is a specialised area that I'm not familiar with.
 
Out of interest, what specific regulation are you trying to comply with here?
Off the bat there would seem to be a few cheap solutions as oppose to building a monitoring circuit, an example been redundancy, why not just have 2 lamps and when one fails it is clearly obvious and maintenance will repair it or the user trained to report it.
That aside the current monitoring option seems the best as previously mentioned but my concern is your reliance on a contactor to isolate a power outlet, if this is for safety then by design it needs to be fail safe and have redundancy in the design thus the contactor needs monitoring as well via a safety control circuit... when you are trying to comply to machine code standards or similar standards then what often seems a simple solution can require a expensive and complex system to ensure safe use and operation.
 
Is this a first installtion of it's type?
I would have thought that hundreds of these machines would be in use and if it's goverened by legislation there would be an approved and tested method of providing the socket supply.

There must be a similar system in Hospitals with the Danger Xray in use sign above the door, presumably if that indicator fails then the equipment must be disabled.

As above somewhere a backup indicator would seem the simplest choice with a warning notice.
 
I appreciate everybody’s reply’s and concerns. They’re all valid in their own right. Thank you.
Out of interest, what specific regulation are you trying to comply with here?
Off the bat there would seem to be a few cheap solutions as oppose to building a monitoring circuit, an example been redundancy, why not just have 2 lamps and when one fails it is clearly obvious and maintenance will repair it or the user trained to report it.
That aside the current monitoring option seems the best as previously mentioned but my concern is your reliance on a contactor to isolate a power outlet, if this is for safety then by design it needs to be fail safe and have redundancy in the design thus the contactor needs monitoring as well via a safety control circuit... when you are trying to comply to machine code standards or similar standards then what often seems a simple solution can require a expensive and complex system to ensure safe use and operation.
New HSE regulations for x-ray machines in vetinary surgery’s.
 
Is this a first installtion of it's type?
I would have thought that hundreds of these machines would be in use and if it's goverened by legislation there would be an approved and tested method of providing the socket supply.

There must be a similar system in Hospitals with the Danger Xray in use sign above the door, presumably if that indicator fails then the equipment must be disabled.

As above somewhere a backup indicator would seem the simplest choice with a warning notice.
It’s an old school surgery that just had a red lamp in a batten holder. The X-ray machine just on a 13amp standard plugtop. Warning notices present.
 

Reply to Contactor control circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I know this is very simple but I would like some advice please. I am installing a new circuit to feed 5 external floodlights. It is...
Replies
7
Views
3K
I'm moving a socket installed on a lighting circuit (installed by previous owner who was a professional electrician so I assume he knew what he...
Replies
7
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
We have this Swiss-made Dixi horizontal borer from 1957, very nice machine still with its original DC variable voltage drive. In those days there...
Replies
9
Views
2K
Hi I am helping with some village lights and need some advice as to a route forward (our electrician is unavailable for an undefined period) We...
Replies
6
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock