Hi. Im looking for the best advice for wiring an emergency stop circuit controlling a dis board via a contactor. This is a dis board feeding circuits in a workshop so the whole dis board must be de energised when the stop button is hit. The problem being the contactor is fed from the dis board in question. Any info would be great thanks.
 
It would depend who is using the system and the safety level requirement, this you need to know to you design this, when its implemented to possible save lives or injury then there are many requirement beyond just making a functional E-Stop circuit to drop out a Dist' board.
 
Is the Dis board at the origin or is it remote to the supply ie fed in armoured etc?, if the dis board is at the origin can you not install an isolator for em stop circuit then you dont have to worry about the contactor being fed from the dis board when the stop buttons are pressed as the em circuit will be isolated from separately.
 
Fit a main switch with the ability to have a trip unit attached, most main MCCB allow for this but on its own it won't meet the requirements for workshop isolation in schools and colleges etc like I say there is a lot of regulation around this although if your doing this for your own personal use then how you achieve a functioning system is your choice.
 
Where is the dis board in regards to origin of supply, why would it be bad practice to have the emergency stop circuit seperate to the dis-board this way the board will still be isolated and youd have isolation for the em circuit
 
As DW says, why are you doing it?
There is only on scenario where such a system is required, and then it is much more complex then dropping out a DB.
This is not as simple as it may seem, and there is no statute law requirement for such a system, so you must be sure of the design specifications and requirements.
If you are designing the system, then you need to be sure of your clients functional specification and then design to meet this in compliance with the statute law requirements.
 

Reply to Contactor controlled distribution board via emergency stop in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
656
Hi guys, A car showroom / workshop brand we do work for has asked us to modify a few things in the workshop. One of them being to implement...
Replies
7
Views
946
I'm doing a college design project and need to choose a suitable range of circuit protective devices for the whole contact. I've chosen and...
Replies
7
Views
4K
We have this Swiss-made Dixi horizontal borer from 1957, very nice machine still with its original DC variable voltage drive. In those days there...
Replies
9
Views
2K
Hi all, First post here, hope I'm compliant with the rules! I did do a quick search before asking this, but I couldn't quite come up with the...
Replies
3
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock