I looked at a contactor schneider ict 4 pole 400v 25a. The fault was a loud knocking noise coming from the electricial riser cupboard.

I suspected one of the contactors was pulling in and out rapidly (this known as chattering?)

I am hoping you can point me in a direction as I'm not massively contactor experienced.

The contactor is for 4x 16a ceiling heater circuits. There is a control circuit with timeclock bringing on all contactors for a shop. There is a Sunvic Tlm2453 Room Thermostat controling the heaters.

My question is which is more likely to to be the fault, the contactor or thermostat. The chattering is happening when the thermostat is reading near the set temp. When I set thermostat up to about 28°c the contactor stopped chattering completely. But when its set around 20-21°c (near room temp) it will happen.

Is there a component in the thermostat that could cause this. Simular to like faulty pir sensor relay clicking and causing lighting to flash constantly?

Many thanks
 
Hi Dengar,

Welcome to the forums.

Does the chattering happen if the required temperature is much higher than say room temperature? Or just as the temperature approaches the required?
 
Hello

Thanks for replies. It's when it's very close to required temperature.

I believe the boards were upgraded by a 3rd party around 4-5 months ago. The issue is apparently 1 month old.

Cheers
 
Thermostat.

It’s sitting on the edge of the required temperature and is clicking on and off repeatedly.
It’s happens a lot, but more noticeable with contractors because of the noise.
Yep looks like the stat is going U/S
 
Is the stat mechanical? Has the stat got a neutral wired to it, the neutral is used for the return for the anticipator. This is a small thermistor type device that kind of pre-heats the bi-metal strip, reducing 'hunting' and making the stat more efficient. I may not have explained it completely correctly but it's along those lines!
 
Good post Robconi, I think this particular stat is 16 amp resistive rated, they require a neutral for small current loads and that could be part of the issue as it's just pulling in a coil with next to no loading on it.
 
The stat mentioned (TLM2453) is a simple mechanical stat that is probably not snapping over smartly due to contact wear or a weakened spring, and is arcing near the set point.

The neutral is required for any level of load. Its purpose as Rocboni describes is to power the accelerator heater, which warms the stat slightly when the room heaters are on, so that its temperature does not lag so far behind the rising room temperature. If the accelerator neutral is not connected, the symptom will be longer cycles with more overshoot above the set temp, because the stat will still be warming up when it is due to go off. It wouldn't cause this faulty switching behaviour.
 
I would also agree with the above and add that the positioning of the stat can make it prone to chasing IE rapid repeated on/off signals, can we assume this is not located over or near the heating source?
 
My apologies. My post seemed to have spammed. Couldnt find delete.

Its located on a pillar type support wall. It's not close to any heating sources.
 
Last edited:

Reply to Contactor issues on ceiling heater circuits in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys, Had a call out today about an odd issue with a newish Creda DT storage heater. Basically.. Storage heaters were installed in one flat...
Replies
4
Views
788
I have a 2 year old 2000w electric panel heater. Devola Designer 2kW Smart Glass Panel Heater with Timer White - DVPW2000WH -...
Replies
0
Views
594
Hi, A baseboard heater in my house emits a short buzzing sound every 30 seconds. It seems to happen only when the room is near the temperature...
Replies
1
Views
815
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock