Search the forum,

Discuss Contactor in the UK Electrical Forum area at ElectriciansForums.net

M

michael_brooke

Hi all
Im struggling to understand why we use contactors i know hoe they are wired and i know how they work, take a lighting circuit controlled by a contactor that needs more amps than a 6amp switch surely wudnt this trip the 6 amp mcb or am i lost all together
 
To put it simply ---- most switches can not handle the starting current used by some appliances. The contactor can....they are rated at different values of output/switching current......
 
The MCB is selected according to the inrush current expected on the circuit as well as the operating current, that's why we have type C and D MCBs.
 
Contactors and relays are used to switch greater currents than a standard switch would handle.
This can have a cost benefit, as the cabeling and control gear for the low current switching would in many cases be cheaper than cabeling and control gear designed to handle the larger current.
With the starter motor on a car for instance low current is switched via the ignition to a relay which then switches a large current to from the battery to the starter.
If a relay was not used, extra large diameter cable would have to be run from the battery to the ignition switch and then to the starter, and the ignition switch would have to be designed to handle the extra current.
The most common use of contactors is to switch currents used to stat and run motors.
However they are often used where there are lots of lights and where the lights are on different phases.
A single single phase switch is used to switch a 3phase contactor, rather than having a 3phase switch, or three single phase switches.
This also saves on cabeling, as only a single phase needs to be wired to the switch rather than wiring three individual phase conductors.
 
theres so many times when using one is beneficial I can't imagine how we would get on at times without them.
 

Reply to Contactor in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
678
Hello all, I know this is very simple but I would like some advice please. I am installing a new circuit to feed 5 external floodlights. It is...
Replies
7
Views
3K
Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
1K
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K
Hello, I bought a new build and noticed the upstairs MCB is controlling some sockets on the opposite floor, so if I flick the upstairs MCB it's...
Replies
31
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock