Discuss contactors and emergency stop buttons. in the Electrical Forum Canada area at ElectriciansForums.net

i mistakenly thought you said 3 machines

as already said -all live conductors(if required) would need 8-poles for 4-machines


the design may include 'redundancy' if required

afraid i don't know any UK rules ,hoping to learn though

- anyhow you're prob well capable of the installation work but let someone else do the all-important 'design'
 
Last edited by a moderator:
Think of a DOL motor starter would you find it acceptable for say a saw to restart on the release of the e-stop button? No, I would not.Or would you expect to have to depress the start button first? Yes, absolutley.

Think of the failure modes for a moment, the OP’s specifier appears to have given them a cursory thought. He has asked for an “overall” e-stop. Presumably this would be in case there is a failure in the control system of the machine such that the stop system did not function, or the machine started unexpectedly, thus A.N. Other could de-energise the machines remotely without having to approach the local isolator, which by definition is local to the machine! I presume that the sterilisers do not have any control circuit, or e.m stop's, which is why the OP has been asked to provide them.

However, is a single e-stop adequate, this boils down to the old chestnut of risk assessment. As you said based on room size accessibility etc.
Agreed.
However, what is unacceptable under PUWER98 & BS EN 60204-1 is the re-energising of a control circuit via the release of a stop control.
The nearest analogy is the central switching systems specified by BS4163.
Here in the link is drawn to PUWER98 and the guidance there in which takes you to 60204, even though these systems are fixed wiring in buildings, 7671 does not cover these types of control, thus bows out to statutory legislation, i.e. EAWR89, & PUWER98 which takes you to 60204.
I have no knowledge of PUWER, I presume a lot of sparks haven't?
You should not allow a contactor to be re-energised by the release of a stop button under any circumstances, I have frightened a few people with this scenario!
Can you circumvate this reg with the use of lockoff stop buttons?
A bog standard em-stop/contactor circuit would be controlling machinery!
Why would you fit a contactor to control a ring main as a ring main is a standard arrangement of circuit from 7671? Have seen plenty of ring mains/radials controlled by contactors and e.m. stops, 'gasguards' and other such devices are regulary used in conjunction with stop buttons in schools, laboratory's etc.
This does not require an e-stop, if it does, then other legislation/guidance has come into play & you thus must therefore comply with that. Ergo my previous comments.

DP switching requirements should be checked, IIRC & it is now late & my copy of 4163 is not to hand, this requires all live conductors to be switched.
You must remember that in the event of an incident then the most appropriate guidance to the system will be selected and expert witnesses may well draw analogies to 4163 as it is the most similar to this situation.
Unsure of DP switching requirements.
Missed the comment wrt the neutral. No reason at all for the N to be taken anywhere except A2 on the contactor!

O/L protection should be looked at for the control circuit as the control devices will not be able to take the full 32A load of the power CPD. Also the controls are controlling supplies from 4 CPD’s.
Agreed, anyone wiring a control circuit without appropriate O/L protection shouldnt be wiring anything!

BTW I still think the original design is flawed and unable to function correctly, safely or even at all based on the info given, which is one of the limitations of such forums.
I presumed that there was at least one typo.
There is more to this circuit than 7671 which was the point of my advice to the OP.
Paul

Like I said, genuinely interested to learn, I think this is something which could benefit a lot of forum members.
 
Last edited by a moderator:
My responses in green, I'm rubbish with this forum software it took me half an hour to get my msg with Davey's modifications into a post!!!:eek:
Please excuse any typo's /spelling its been a bad day!:(

Originally Posted by netblindpaul

Think of a DOL motor starter would you find it acceptable for say a saw to restart on the release of the e-stop button? No, I would not.Or would you expect to have to depress the start button first? Yes, absolutley.

Think of the failure modes for a moment, the OP’s specifier appears to have given them a cursory thought. He has asked for an “overall” e-stop. Presumably this would be in case there is a failure in the control system of the machine such that the stop system did not function, or the machine started unexpectedly, thus A.N. Other could de-energise the machines remotely without having to approach the local isolator, which by definition is local to the machine! I presume that the sterilisers do not have any control circuit, or e.m stop's, which is why the OP has been asked to provide them.


I like green! The sterilisers must have their own control cct to comply with the machinery directive CE PUWER98 etc.


However, is a single e-stop adequate, this boils down to the old chestnut of risk assessment. As you said based on room size accessibility etc.
Agreed.
However, what is unacceptable under PUWER98 & BS EN 60204-1 is the re-energising of a control circuit via the release of a stop control.
The nearest analogy is the central switching systems specified by BS4163.
Here in the link is drawn to PUWER98 and the guidance there in which takes you to 60204, even though these systems are fixed wiring in buildings, 7671 does not cover these types of control, thus bows out to statutory legislation, i.e. EAWR89, & PUWER98 which takes you to 60204.
I have no knowledge of PUWER, I presume a lot of sparks haven't?
You should not allow a contactor to be re-energised by the release of a stop button under any circumstances, I have frightened a few people with this scenario!
Can you circumvate this reg with the use of lockoff stop buttons?

No you can not if would not comply with PUWER98.

A bog standard em-stop/contactor circuit would be controlling machinery!
Why would you fit a contactor to control a ring main as a ring main is a standard arrangement of circuit from 7671? Have seen plenty of ring mains/radials controlled by contactors and e.m. stops, 'gasguards' and other such devices are regulary used in conjunction with stop buttons in schools, laboratory's etc.


So have I & they don't comply with 4163 or PUWER98 or EAWR89. More often than not they have been designed and installed by damn good installation sparks who don't understand control systems because it is not their area of expertise. you can't treat a contactor control circuit in this sort of application like a glorified light switch!
An e-stop button is not designed to make current flow it is only designed to break it.
It is not the fault of the install sparks it is just tha tthey have probaly never experienced it or been taught it correctly.
This sceanrio is the one I describe, there are other requiremetns in place than 7671 at play.
These installations MUST have a start & a stop button at the very minimum otherwise they DO NOT COMPLY.
If they have a momentary start button along with one or more e-stops which function in the same general manner as a DOL motor starter, or a lighting contactor circuit with push button on & push button off control then they may well comply.
However, just e-stops which when released re-energise the contactor then they DO NO COMPLY.


This does not require an e-stop, if it does, then other legislation/guidance has come into play & you thus must therefore comply with that. Ergo my previous comments.

DP switching requirements should be checked, IIRC & it is now late & my copy of 4163 is not to hand, this requires all live conductors to be switched.
You must remember that in the event of an incident then the most appropriate guidance to the system will be selected and expert witnesses may well draw analogies to 4163 as it is the most similar to this situation.
Unsure of DP switching requirements.

I can't remeber the exact requirements either, I would have to look it up & I have a few other things on tonight.

Missed the comment wrt the neutral. No reason at all for the N to be taken anywhere except A2 on the contactor!

O/L protection should be looked at for the control circuit as the control devices will not be able to take the full 32A load of the power CPD. Also the controls are controlling supplies from 4 CPD’s.
Agreed, anyone wiring a control circuit without appropriate O/L protection shouldnt be wiring anything!

BTW I still think the original design is flawed and unable to function correctly, safely or even at all based on the info given, which is one of the limitations of such forums.
I presumed that there was at least one typo.
There is more to this circuit than 7671 which was the point of my advice to the OP.
Paul


Like I said, genuinely interested to learn, I think this is something which could benefit a lot of forum members.

Hope my comments make sense.

It is NOT allowable to use an e-stop button like a light switch to switch on and off a contactor to control machinery. it will not comply with STATUTORY legislation.

You can even get this from the BRB, & that is not statutory.

Paul.
 
thanks davelerave so what you are saying is to isolate the neutrals aswell as the lives. i will suggest it to the design engineer


afraid i can only help with general advise as i don't work in UK(may be moving over which is why i'm here)

but the basics for emergency stopping would be similar anywhere

ie: stop de-energizes contactor/s + releasing doesn't re-energize

stops located where needed

system 'designed' to relevant standard

if it was required to switch neutral prob separate poles because

- for single phase the neutral current is the sum of the phase currents
and for 3 phase there's a risk of unbalanced star connected load if you used 1 neutral pole
 
thanks a lot for all your posts. tbh i had never heard of puwer98 i know thats probably well bad considering i work in hospitals! not that it makes any difference, but the em stop button is a twist to release, so it wont just re-energise, but i'm guessing to comply it must completely isolate the circuits.?
im going to defo bring it up with with the design engineer, cos i have had a few issues with him, for instance he said wire the general power (32A ring) in 4mm L&N with 2.5mm cpc. i always thought cpc must be same size as line conductors, unless the cpc is incorporated in a multicore cable (ie T&E) in 7671 it does say this i think in chapter54. also , we ran in a 95mm 4 core swa and he said to use 35mm earth , and use the steel wire armour to achieve Ze. i thought the earth should be at least half the size of line conductors.:confused: he also suggested wiring the sterilisation machines in 16mm at first! its only a 32amp isolator! was only when i brought it up and said you could use 6mm he agreed! bit dubious about him.
 
don't work in the UK but for 4sq rings wired in pvc singles we use 4sq cpc

out of interest are you talking about steel trunking/conduit and singles
 
joe,

PUWER98 applies to all work equipment in all work places whether in use by the employed or self employed. From a screwdriver to a nuclear reactor, the same as EAWR89 applies to all electrical equipment in workplaces from a say 1.5V button cell up to a 400kV installation.
Nothing is exempt, it is just that the hazards & risks and thus the mitigations are different.

It may be useful you get yourself on the HSE website and have a look at a few of the publications that are on free download there to ensure that you are compliant with statutory legislation.
A twist to release e-stop is a normal e-stop.
It is still not allowed to energise a supply with this type of device. (Full stop)

If you are employed, then the onus is on your employer and you should turn to them for advice, your supervisor, manager, QS, PDH etc. but, this does not remove your personal responsibility even as an employee.

HSE have a test case on their site where a spark in charge of an apprentice was not sufficiently diligent and the apprentice was injured, suffered an electric shock, I can't remember the outcome to the apprentice, but it did involve hospitalisation. The spark was prosecuted and fined personally due to the negligence of his actions. The spark was an employee, not a director, manager, QS or anything or any role with supervisory responsibility above that of his own work & that of the apprentice.

IF you are self employed, or running your own ltd. co. then you really need to do a bit of self study to ensure that you do not inadvertently do something that gets you into the dock, because expert witnesses will hang you out to dry. You would also be subjected to more severe punishment than an employee.

Remember "ignorance of the law is no defence", sorry, also with H&S legislation the statute is overturned, from "innocent till proven guilty" to “it is down to the defendant to prove their innocence”.

Bad I know, but that is how it is.

So you could end up in jail and just saying I did not know may only get your sentence reduced if the judge is lenient and believes you.

Also, not having a fundamental understanding of the design and function of the circuits that you are designing and installing, would not go down well in court.

p.s.
Nearly did the IEE expert witness training a few years ago but it clashed with some other stuff, so dropped it.

Paul
 
to give u a bit of an insight into my setup... im working for a building firm on a self employed basis. there is a qs but he has very little to do with things, he just basically puts his name down on the cert, he trusts all my work etc. so i am the only spark. there is a design engineer who has been out to site twice, and he is the one who obviously came up with the install , done the drawings etc. the only drawing i have relating to the pushbutton circuit etc is one showing a 4 pole contactor 32A, withe the four line conductors for the isis machines (sterilisation machines) going through the fore pole connections , and a seperate 6A circuit feeding the pushbutton, which in turn feeds the contactor coil.
 
... there is a design engineer who has been out to site twice, and he is the one who obviously came up with the install , done the drawings etc. the only drawing i have relating to the pushbutton circuit etc is one showing a 4 pole contactor 32A, withe the four line conductors for the isis machines (sterilisation machines) going through the fore pole connections , and a seperate 6A circuit feeding the pushbutton, which in turn feeds the contactor coil.


Hi Joe

Any chance you can photograph the relevant drawing and post the image here?

s.f
 
With all the varied information that has been given,I may offer a different alternative

It seems to me that the design being used will be intergrating the control circuit for the use of all machines
Press the stop and the lot are off

If thats the case why not use a control distribution panel,wiring in any remote stops in series to each machine to isolate the panel in the event of any stop button operating

You can rcbo what you like,stop buttons scattered around here there and everywhere with emergency stop control over the distribution of all via the panel
You can make up your own with a standard dist board and suitable contactor incomer with a stop and start on the panel


Too many posts to read the whole thread,so forgive me if I have not understood what you are trying to acheive
 

Reply to contactors and emergency stop buttons. in the Electrical Forum Canada area at ElectriciansForums.net

Similar Threads

Hi guys , I have to break a ring circuit through a contactor with an emergency stop button .. just want to double check my wiring in the diagram...
Replies
26
Views
3K
Hi guys, A car showroom / workshop brand we do work for has asked us to modify a few things in the workshop. One of them being to implement...
Replies
7
Views
933
I’ve been asked to provide an emergency stop button for a circuit rated at 20amps. I’ve never installed one before and only really found 10amp...
Replies
56
Views
6K
Hello, I’m need some advice on how a contactor is wired please and where the neutral go. I’m told it is connected to eco 7 and controls 3 heaters...
Replies
12
Views
3K
Hi I have a 3 phase 400v motor wired in star configuration it is controlled via a 3 pole 415v coil contactor which is switched simply via a stay...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock