Discuss Continuity Testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

P

Penfield

Hi,

I having a problem with the readings I'm getting whilst doing continuity tests. The readings tend to fluctuate up and down, starting at say 1.90 then going up to 2.8 then back down to 2.3 for example. Is this a problem with the meter? or does it point to a problem with the cable under test?

Kind Regards,

Paul
 
Hi,

I having a problem with the readings I'm getting whilst doing continuity tests. The readings tend to fluctuate up and down, starting at say 1.90 then going up to 2.8 then back down to 2.3 for example. Is this a problem with the meter? or does it point to a problem with the cable under test?

Kind Regards,

Paul

Which circuits are you testing ring final? Sounds like you need to switch the legs of the ring?
 
Hi Warren,
The problem is occurring mainly whilst testing lighting but today it also happened on a radial whilst trying to get the R1/R2 measurement.
 
Well generally you would expect the resistance to increase with the length of the circuit.

If you are unsure about your meter then it would be best to get it checked - not worth having a defective meter! :eek:

Check the meter with some fresh batteries and see if this changes how it operates?
 
Obviously the meter is one thing, I would still investigate further the circuits you are testing just to make sure connections are tight, no visable damage etc. Just to be sure.
 
Sometimes have the same prob.

Easiest thing to do is make sure your probes are pushed in tight and the leads arent flapping around all over the place.
 
Yup...probes and croc clips...squeeze 'em tight....some are really weak (Fluke 1652 hands up!!).....if they arent on tight, or are flappping in the wind, your readings will be all over the place...
 
Hi,

I having a problem with the readings I'm getting whilst doing continuity tests. The readings tend to fluctuate up and down, starting at say 1.90 then going up to 2.8 then back down to 2.3 for example. Is this a problem with the meter? or does it point to a problem with the cable under test?

Kind Regards,

Paul

if its been on the van overnight and is very cold then i tend to find that mine plays up a bit. bloke who calibrates mine made a point of telling me to keep it inside at room temp if poss as this will help.he says from experiance when calibrating, various cold meters will take several attempts to just zero the leads correctly. it will also reduce the chance of the crooks stealing it from your van!:mad:
 

Reply to Continuity Testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hello everyone In September 2023 I rented a beautiful 3 bedroom apartment, with all electric supply, no gas powered appliances. I noted down the...
Replies
16
Views
2K
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
422
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock