I've now been told by the National Grid that if I am to now choose a large cut out then I will require a CT Panel and half hour meter billing.
There CT stands for current transformer.

Basically for meters up to around 100A they are usually directly connected, i.e. the current passes through the meter to be measured, and that along with the measured voltage gives power, and then power integrated over time gives you energy (i.e. kWh).

For example, 10A at 230V = 10 * 230 = 2300W = 2.3kW, after 24 hours of constant use that is 24 * 2.3 = 55.2 kWh

However, above 100A it becomes impractical to route big cables via the meter so normally what is done is a current transformer passes a known fraction of the current to the meter for measurement, and the meter then knows to multiply by 100 or whatever the CT ratio is in order to get the real power.

This is normal for every big installation, and I guess these days the half-hour billing meter is also a standard requirement from the DNO. The catch is you might have time-of-day costs applied!

However, aside for the little details of how the metering is done, I have to agree with @Rockingit that you should engage someone you trust who has experience in this sort of thing to help from very start.

I would also say that if you are treating this as one building / system you really should look in to the heating and provision of hot water for showers, etc, as the use of heat-pumps and lower-rate heating of stored water could make a BIG difference to your electricity bill, and over a few years more than pay off the costs at the start!
 

Reply to Converting into 12 flats, KVA, phases etc. Help! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, We are converting a former office into 10 self-contained flats with kitchens, showers, heaters all electric, no gas. We have been offered a...
Replies
1
Views
726
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
I have a 230 Volt single-phase circuit with a 100 Amp cutout fuse and a 100 Amp MCB switch, so the supply is rated at 23 kVA. Only about 13% of...
Replies
54
Views
6K
Morning everyone ive been asked to calculate the maximum demand for a conversion of commercial property to 12 one bed self containted flats...
Replies
4
Views
10K
S
Hello all I am new to this site and i am glad i have found it as it looks crammed with useful advice from people in the know. I am not too...
Replies
1
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock