Existing 10Amp cooker is fed by 6mm from main consumer unit (32A MCB) to cooker switch then 6mm fed to a 13Amp double socket, off that is one plug for supply to cooker and one plug for igniter for gas hob.

I have a 16Amp rated oven coming and would like to install a 45Amp rated cooker plate and keep existing double socket for gas igniter. Will be replacing MCB in consumer unit to 20Amps.

I am guessing the cooker cabling is done in a radial so my question is from new 45Amp cooker plate shall I just wire a cable from this to existing socket also in 6mm or can I reduce this cable size from 45Amp plate to socket???
 
That all sounds fine, as long as you're having the entire circuit on a 20a MCB you can feed the socket for gas hob ignition with 2.5mm cable from the incoming terminals on the cooker outlet. But as it's only a 16a rated oven you could fit a 'dual' surface box with a 20amp outlet plate and single socket, the link would be within the same box so all nice and tidy.
 

Reply to Cooker cabling advice in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind...
Replies
23
Views
836
I have had my kitchen rewired ready for a new kitchen. I was originally going to have a gas cooker so a 3 pin 13a socket was left on the end of...
Replies
2
Views
366
Good Evening. I’m currently carrying out an EICR. I have a cooker circuit radial with a 32amp mcb fed from and RCD split board. There is a 45amp...
Replies
14
Views
799
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
551

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock