Hi new to this..go easy on me. Times just out, just want to know what your take on this is. Friends wanting to get their house tested, but I’ve noticed his cooker comes off the kitchen ring, would his test fails because of this?? Like a said I’ve just past my test so not 100% sure on this, I’m not sure of the load on the cooker
 
Hi new to this..go easy on me. Times just out, just want to know what your take on this is. Friends wanting to get their house tested, but I’ve noticed his cooker comes off the kitchen ring, would his test fails because of this?? Like a said I’ve just past my test so not 100% sure on this, I’m not sure of the load on the cooker
Depends on the rating of the cooker.
 
i was going to suggest clamping a tail with as much as possible in the house off or unplugged. note current, then switch on cooker as max. as possible. note current in tail. subtract previous reading, then he'll know roughly the current draw of the cooker.
 
A lot of new cookers have relatively small current draw and some can actually be fitted with a 13a plug top. Best to check rating of cooker first.
 
would his test fails because of this??

Assuming you mean an EICR then no it will not 'fail' the outcomes of an EICR are limited to either 'satisfactory' or 'unsatisfactory' there is no pass or fail.
The R in EICR stands for Report because it is just that, a report, it is not an exam or anything like that.

If this cooker is drawing more than 13A from a single point in the ring or causing an overloading on one 'leg' of the ring then you may consider it to be something worth a C3 code or in extreme cases a C2.
 

Reply to Cooker circuit on kitchen ring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
681
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
774
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
853
For some Strange reason we have three Circuits running in the Kitchen i think for two OLD Cookers and a Ring Circuit for the house. Well the...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock