cmac70

Been asked to quote for new cooker supply. The only practical route is to run cable outside the house. SWA seems over kill for cooker circuit. Not got full watts of cooker yet. All I know they have told need 40A breaker. Was thinking of running 10.0mm cable in conduit. Because the run is 30m. Hoping to get wattage later today.
 
Who's told them they need a 40A breaker? I'll be very suprised if they're having a cooker over 15kW fitted in a domestic property.
 
I was think that but the husband said its a big range one. The best he has past me his wife number. So ever she looked at spec's or blind leading blind. Can't do proper cable calc without knowing that.
 
It might need 10.0mm2.

fitted one last year, cost 5 grand, came with its own 10.0mm2 heat resistant 3 core (not very) flex which was then fitted to fixed wiring.

it had pizza setting - grill could be on AT SAME TIME as the over. New one on me but when you looked at the figures it needed a big supply.
 
stupid question possibly, but you're saying the only practical route is outside the house. Was the previous cooker electric? if so, could you not follow the same route but just upgrade the cable?
can't believe anybody would be happy with a cable on the outside of their house just for a damn cooker. seems crazy!
 

Reply to Cooker circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
602
For some Strange reason we have three Circuits running in the Kitchen i think for two OLD Cookers and a Ring Circuit for the house. Well the...
Replies
18
Views
2K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
844
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
866
Hi folks, DIYer here, hoping for some advice before most likely calling in a spark. I'm looking to wire in new cooker and hob (separate units)...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock