Morning all,

I'm Having an issue with a cooker install and wonder if anyone can help.
Every time the cooker is switched on there is a RCCB trip (Rated at 80a 30Ma). The circuit will take a supply but no load of any kind. I connected a DeWalt charger to the socket on the cooker plate (only drawing 0.85a) and it still trips. The rest of the ring main/lighting circuit has no issues and tests with no problems.

Testing path -
Tested appliances, all good.
New cable run, thought it may be a neg earth fault due to a rogue screw/nail so replaced the cable again.
Removed all other connections in the distribution board so only the cooker was connected, same problem.
Swapped out the 40a breaker.
Swapped out the cooker connection plate.
All polarity & resistance checks out.

Scratching my head here, any help would be appreciated.

Thanks,
D
 
Morning all,

I'm Having an issue with a cooker install and wonder if anyone can help.
Every time the cooker is switched on there is a RCCB trip (Rated at 80a 30Ma). The circuit will take a supply but no load of any kind. I connected a DeWalt charger to the socket on the cooker plate (only drawing 0.85a) and it still trips. The rest of the ring main/lighting circuit has no issues and tests with no problems.

Testing path -
Tested appliances, all good.
New cable run, thought it may be a neg earth fault due to a rogue screw/nail so replaced the cable again.
Removed all other connections in the distribution board so only the cooker was connected, same problem.
Swapped out the 40a breaker.
Swapped out the cooker connection plate.
All polarity & resistance checks out.

Scratching my head here, any help would be appreciated.

Thanks,
D
When you say all Polarity and Resistance checks OK what where the IR readings? and was the cooker ON when you tested L to E and N to E, and at what voltage setting did you use on your MFT
 
Morning all,

I'm Having an issue with a cooker install and wonder if anyone can help.
Every time the cooker is switched on there is a RCCB trip (Rated at 80a 30Ma). The circuit will take a supply but no load of any kind. I connected a DeWalt charger to the socket on the cooker plate (only drawing 0.85a) and it still trips. The rest of the ring main/lighting circuit has no issues and tests with no problems.

Testing path -
Tested appliances, all good.
New cable run, thought it may be a neg earth fault due to a rogue screw/nail so replaced the cable again.
Removed all other connections in the distribution board so only the cooker was connected, same problem.
Swapped out the 40a breaker.
Swapped out the cooker connection plate.
All polarity & resistance checks out.

Scratching my head here, any help would be appreciated.

Thanks,
D
you have replaced the cable again .so did you not do ir on the circuit to see which leg was giving a fault .
 
could even be a N-E reversal in the cooker switch/socket.
 
I'm guessing but as this is a new circuit added, then we have to presume the RCD wasn't tripping before ............

In the absence of any meaningful test results we can only speculate.
The OP has gone notably quite, at work maybe?
 

Reply to Cooker install - RCCB tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
704
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi, Just been scratching my head about this one and wonder if I've missed anything. A few weeks ago I installed a new circuit for a 3kw oven and...
Replies
6
Views
821
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
866
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
346

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock