Hi all

6mm Cable runs from Fuseboard into a 45amp DP swith for the cooker. (Cooker load is 7kw)
Can the cable run directly from the switch into the cooker or does it have to go from the switch to a cooker connection unit and then a cable from the ccu to the cooker?

I cannot see anything in the regs book but i may have missed it in there.
 
Hi all

6mm Cable runs from Fuseboard into a 45amp DP swith for the cooker. (Cooker load is 7kw)
Can the cable run directly from the switch into the cooker or does it have to go from the switch to a cooker connection unit and then a cable from the ccu to the cooker?

I cannot see anything in the regs book but i may have missed it in there.
Diyer obviously.
 
the purpose of a connection unit is so that the cooker can be safely isolated by the switch/isolator for disconnection. it is not mandatory as isolation can be achieved by switching off at the CU.
 
Thanks Telectrix.

My first post may not have been clear on how the cable is run:

From fuse board (32a MCB) 6mm T&E clipped direct
Goes to kitchen inside a base unit into a 45amp DP switch
Cable then comes out of the switch and directly into the cooker

Should a CCU be fitted between switch and cooker or is it ok as is?
 
it's OK, but it would be good practice to fit a CCU.
 
Cable from Consumers unit into DPswitch, from DP switch to CCU, from CCU to cooker as tel has already described, not mandatory but best practice for safe isolation reasons
 
Sounds about right, ...the so-called modern thinking!! Bung the cooker isolation switch at the back of a kitchen base unit, that you need fight through all the pot's and pans to get too!!
 
FYI - a CCU will be installed!

Sounds about right, ...the so-called modern thinking!! Bung the cooker isolation switch at the back of a kitchen base unit, that you need fight through all the pot's and pans to get too!!

How would you deal with it then? Kitchen walls are tiled floor to ceiling and the walls are block. If the walls were plasterboard on studwork I could have cut out a couple of tiles out and flush mounted a switch with the cable dropped in the void.

Customer doesnt want a 50mm deep pattress on the wall tiles with trunking (its their kitchen and they will have to look at it every day) so a switch hidden and easily accessable in a base unit seems the next best option.
 
Last edited by a moderator:
Modern houses are getting so small that there's often no space to mount the DP isolator above. As long as it's at the front of the cupboard it's ok ..... isn't it?
 
FYI - a CCU will be installed!



How would you deal with it then? Kitchen walls are tiled floor to ceiling and the walls are block. If the walls were plasterboard on studwork I could have cut out a couple of tiles out and flush mounted a switch with the cable dropped in the void.

Customer doesnt want a 50mm deep pattress on the wall tiles with trunking (its their kitchen and they will have to look at it every day) so a switch hidden and easily accessable in a base unit seems the next best option.



And there was me thinking it was an existing installation!! lol!!

I was actually referring to the trend of new kitchen builds where everything is, or has to be hidden in cupboards, with absolutely no thought as to the workability of a modern kitchen...

However, in you're case it sounds a bit strange to me, 99.5% of all kitchens have been provided with a cooker isolator at the time of electrical installation and have done, since the early 50's!!

If you are so worried about the aesthetics, WHY is the 6mm cable clipped direct from the CU to the kitchen?? Surface mounted/clipped direct cable doesn't count then??
 
Never needed to, and never have or will fit sockets, switches, etc to kitchen base/wall cabinet carcases on a new installation. Never come across a kitchen or kitchenette too small, to mount CCU's socket outlet(s), switches above worktops either.
 
And there was me thinking it was an existing installation!! lol!!

I was actually referring to the trend of new kitchen builds where everything is, or has to be hidden in cupboards, with absolutely no thought as to the workability of a modern kitchen...

However, in you're case it sounds a bit strange to me, 99.5% of all kitchens have been provided with a cooker isolator at the time of electrical installation and have done, since the early 50's!!

If you are so worried about the aesthetics, WHY is the 6mm cable clipped direct from the CU to the kitchen?? Surface mounted/clipped direct cable doesn't count then??


Previous electrician / home owner took the original cooker cable and circuit and has put an electric shower on it in the bathroom directly behind the kitchen.

The property is a bungalow. Fuseboard in garage. Cable is run in the loft space (which is above garage) and clipped above insulation to the joists and then drops down into the kitchen right in the corner and then runs behind a wall cabinet and through the worktop into base unit. The only trunking that can be seen is a 30cm piece right in the corner.
 
Last edited by a moderator:
Previous electrician / home owner took the original cooker cable and circuit and has put an electric shower on it in the bathroom directly behind the kitchen.

The property is a bungalow. Fuseboard in garage. Cable is run in the loft space (which is above garage) and clipped above insulation to the joists and then drops down into the kitchen right in the corner and then runs behind a wall cabinet and through the worktop into base unit. The only trunking that can be seen is a 30cm piece right in the corner.



From fuse board (32a MCB) 6mm T&E clipped direct

That description is not what the above is implying!!


So you have run a 6mm T&E through a wall cabinet and worktop into a base cabinet, is that right??
 
Engineer54- you said 99.5% of homes built after 1950 were built with a cooker point.

My response to this: The previous owner / Electrician used the "old" cooker circuit for a shower circuit.

The new cable for the cooker is on a seperate 32a MCB, drops down into the kithen, behind a wall cabinet ( not in/through)
The cable is then in mini trunking between the wall cabinet and worktop.
The cable then goes through the worktop and drops into a base unit to a 45a switch
 
Sounds about right, ...the so-called modern thinking!! Bung the cooker isolation switch at the back of a kitchen base unit, that you need fight through all the pot's and pans to get too!!

A new kitchen (part of an extension that I'm doing the electrics for), I'd already first fixed hob and oven isolators at socket level, and connection units in the right places, per the customers plans.

The kitchen fitter came along and required the isolators to be moved to the back of a deep cupboard above the high-level oven, so you'd probably need a ladder to reach them, as well as empty the pots and pans. Apparently that's how it's best done nowadays!

The fitter also said no need for connection units, just leave tails from the isolators hanging out the wall for them to connect. I wasn't there at the time, but the builder (who was) convinced the customer to at least keep these.
 

Reply to Cooker. supplieed via a switch direct. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
619
Good Evening. I’m currently carrying out an EICR. I have a cooker circuit radial with a 32amp mcb fed from and RCD split board. There is a 45amp...
Replies
14
Views
799
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
545
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
824
Hi I am seeking help and best practices to achieve below tasks. I am not across regulations hence will appreciate best approach to achieve below...
Replies
11
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock