Stuart W

DIY
Reaction score
0
I will shortly be having a range cooker installed that requires 2 x 13 amp supplies. Maximum power required is stated as 3 kW and 2.85 kW respectively. I have a redundant cooker supply on its own circuit, probably 30 amp. I would like to convert this to provide the power for the new cooker. Can you advise if this is possible please and what would be needed?
 
It won’t be a problem, however check a couple of things.

Do the appliance come with plugs fitted?
If yes, then have a single socket for each. Don’t plug both of them into a double.
If no, then don’t put a plug on them. Hardwire them both into the existing cooker outlet.

If you have to add lengths of cable, then make sure it’s of required size to carry the expected load. Ie, you cant run both from a bit of 2.5mm
 

Reply to Cooker supply to 13 amp sockets in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
661
DIYer question. I have a 32 amp supply going from consumer unit in garage to kitchen. It supplies an induction hob only. The cable is easily...
Replies
34
Views
3K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
631
I am looking for advice on getting an upgraded 25 meter extension cable from my office into my car park to charge my EV from an IP66 rated socket...
Replies
7
Views
2K
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
744

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock