Discuss Cooker switch in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

hoppy

-
Reaction score
18
Hi Guys probably a really simple method,

but when you install a cooker switch, it is normally to the left/ right of the cooker, so do you guys put the cooker connection unit or a socket, directly below the switch in a cupboard, or do you put it behind the cooker?

If behind the cooker do you go back up the wall with the cable across and directly down behind the cooker?

Or is there something I am not thinking off to keep within the permitted wiring zones.

Thanks

Craig
 
just run it down from the control plate then across to the connection plate in an L shape. the cable zones extend horizontally and vertically from each point.
 
Not forgetting that the switch/Isolator should be a minimum of 300mm/30cm/12" what ever you understand? from the edge of the cooker and NOT above the cooker! And the cooker outlet or socket? (depending on loading of cooker) should NOT be installed in the Kitchen "cupboard" Or in the adjacent cupboard!! but on or in the wall, which may mean drilling a 75mm whole in back of cupboard to pass 13amp plug top through socket, etc etc
 
Not forgetting that the switch/Isolator should be a minimum of 300mm/30cm/12" what ever you understand? from the edge of the cooker and NOT above the cooker! And the cooker outlet or socket? (depending on loading of cooker) should NOT be installed in the Kitchen "cupboard" Or in the adjacent cupboard!! but on or in the wall, which may mean drilling a 75mm whole in back of cupboard to pass 13amp plug top through socket, etc etc

and go easy if its a single brick wall!! lol :)
 
Not forgetting that the switch/Isolator should be a minimum of 300mm/30cm/12" what ever you understand? from the edge of the cooker and NOT above the cooker! And the cooker outlet or socket? (depending on loading of cooker) should NOT be installed in the Kitchen "cupboard" Or in the adjacent cupboard!! but on or in the wall, which may mean drilling a 75mm whole in back of cupboard to pass 13amp plug top through socket, etc etc

imo it can be fitted in the base unit. i personally wouldnt, but it CAN be fitted there.
 
Not good pratice Gamblor6, AS KITCHEN FITTERS (FUTURE INSTALLS,CARPENTERS ETC) SHOULD BE ABLE TO MOVE CUPBOARDS/CABINETS WITH OUT EFECTING/DISCONNECTING ANY WIRING, I:E REMOVING SOCKETC ETC , INSTALLED IN FABRIC OF KITCHEN,
 
Not good pratice Gamblor6, AS KITCHEN FITTERS (FUTURE INSTALLS,CARPENTERS ETC) SHOULD BE ABLE TO MOVE CUPBOARDS/CABINETS WITH OUT EFECTING/DISCONNECTING ANY WIRING, I:E REMOVING SOCKETC ETC , INSTALLED IN FABRIC OF KITCHEN,

as i said i personally wouldnt, agreed its not good practice but in theory its ok.
 
Not good pratice Gamblor6, AS KITCHEN FITTERS (FUTURE INSTALLS,CARPENTERS ETC) SHOULD BE ABLE TO MOVE CUPBOARDS/CABINETS WITH OUT EFECTING/DISCONNECTING ANY WIRING, I:E REMOVING SOCKETC ETC , INSTALLED IN FABRIC OF KITCHEN,
true, kitchen fitters are quite capable of wrecking electrics without us making it easy for them.
 
i though kitchen fitters were fully qualified electricians!! they got part pee aint they!! lol...:)

New rules should be added to the BRB of electrical safety

1/ Under no circumstances should untrained Kitchen fitters,Plumbers and Tilers be entrusted with electrical installation work

2/ Above said trades are not permitted to continue their bad practices

3/ None of those above trades to become pee registered

4/ Any remaining pees to be booted out of schemes pronto

5/ Never again shall electrical safety be compromised by permitting an "open to anyone who thinks they can" mentality

6/ The ability to construct a kitchen cupboard or solder a joint should no longer be seen as an adequate substitute for the calculation of cable sizes and the compromising of safety or by being unable to interprit test results or even test
 
Not forgetting that the switch/Isolator should be a minimum of 300mm/30cm/12" what ever you understand? from the edge of the cooker and NOT above the cooker! And the cooker outlet or socket? (depending on loading of cooker) should NOT be installed in the Kitchen "cupboard" Or in the adjacent cupboard!! but on or in the wall, which may mean drilling a 75mm whole in back of cupboard to pass 13amp plug top through socket, etc etc

Is that an actual regulation mate?
 
Its fast becoming percieved as a new regulation, since this particular "guidance", made its appearance in that green book I posess, with the wrapping paper still on it :)
 

Reply to Cooker switch in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
(Trying again, as picture didn't post first time) Hi, I'd be very grateful if anyone could help me here. Below, I've pasted a sketch showing how...
Replies
5
Views
1K
Hi I am seeking help and best practices to achieve below tasks. I am not across regulations hence will appreciate best approach to achieve below...
Replies
11
Views
3K
Hi, I'm new here so apologies if this isn't the correct area to post this. We moved in to a bungalow around 8 months ago and had a full re-wire...
Replies
3
Views
1K
Hi, I'd be very grateful if anyone could help me here. Below, I've pasted a sketch showing how my oven is currently wired up, followed by 3...
Replies
0
Views
925

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock