Discuss cooker tt no rcd in the UK Electrical Forum area at ElectriciansForums.net

M

midgetman

hi extended a 32 amp cooker circuit, adding a cooker switch and outlet plate. extended as it is a 7kw range cooker now situated in fireplace. old cooker now not going to be used.

problem is its on a 16th edition board and is on tt. the cooker and lighting are non rcd protected.

ideal would be to either go on rcbo or add another rcd.

how ever customer does not want to spend so can the cooker go on the 63amp rcd. there is no shower and only the rings on it.

as I said not ideal but got to be safer.

if above would then be notifiable and not minor works?

thanks
 
as I said not ideal but got to be safer.



thanks

But not safe! It is your name going on it, and you maybe doing him a favour saving him a few quid, but that will all be forgotten when someone gets hurt, and then guess where the finger will point.

Cheers...............Howard
 
cooker is on 32 amp mcb.
560d8599787ffb677fdd9dbfdf53e38d.jpg
 
But not safe! It is your name going on it, and you maybe doing him a favour saving him a few quid, but that will all be forgotten when someone gets hurt, and then guess where the finger will point.

Cheers...............Howard

Not safe with no over current protection? jeez
 
hang on. the cooker does not, nor has ever , required RCD protection. if the cable feeding the cooker isolator is buried<2" deep in wall/s, then that cable may need RCD.
 
cable is surface mounted. (fixed to wall securely behind kitchen units) however I thought all tt had to be now rcd protected..
 
you fit RCDs to a TT system if the Ze is too high to give acceptable Zs readings. a decent TT system with sub 1 ohm Ze may well negate the need for a RCD.
 
I can't see it being unsafe by putting on to the rcd side. inconvenient in case of fault but not unsafe.

maybe I see if I can find rcbo.. cheers
 
no problem with doing that, midget. better safe than sorry.
 
Am I missing something here. There's a spare way on the rcd side of the board so either move cooker over or get an rcbo. Issue mwc for extending circuit get paid run away ;)
 
You wont overload that RCD in a house with the just the RFC's and cooker on it. Just move it over to RCD side if it is even required for your installation method (buried cabling?). No need for RCBO. Don't put lights on same RCD though, leave it alone unless you have worked on circuit and RCD protection is now required, then RCBO it to minimise disruption under single circuit fault condition.
 
dp if possible. if not fit new rcd which is dp and then in effect making it a twin rcd board.

It's going to be difficult to install a DP or SP+N RCBO in a standard CU unless are stand alone. Far better to go the dual RCD route.

Actually with TT CU's and DB's all protective devices should be DP, not that many if any take any notice, or even if they know why!! lol!!
 
there's enough spare ways to put lights on rcd as well. Thought 16th you had to have upfront rcd on board..

I wouldn't do that. Leave the lights on the non RCD side so when the RCD trips, the lights stay on.

You work is related to the cooker circuit, NOT the whole installation.

The MWC comments section should be used appropriately!
 
I think the problem was the way you worded you first post suggested you were going to wire cooker circuit directly from the 63a rcd. Got some of the oldies a bit excited :p

OIY you pack it in lol
 
Shouldnt 16th edition cu's on TT have 100ma rcd up front?
All circuits will require fault protection which is usually provided by one or more RCDs.
I would have expected an S type 100mA RCD up front, and 30mA RCD protecting the downstairs sockets.
As it is, the OP will have to ensure that the new cooker circuit is provided with 30mA RCD protection.
This can be achieved by using a spare way on the RCD side of the board, or by using an RCBO on the non RCD side of the board.
The OP will then be left with either persuading the customer into having the MCBs on the non RCD side replaced with RCBOs, or just commenting on the lack of RCD protection on the EIC.
 

Reply to cooker tt no rcd in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi there , Currently doing a college project where i need to select protective devices for the contract. I'm now at the point of selecting SPDs...
Replies
5
Views
2K
Evening all, If a socket circuit is not RCD protected via an RCD/RCBO and there isn't the option of fitting an additional RCD enclosure or...
Replies
20
Views
6K
Hi all,looking for some pointers to an RCD problem, I work entirely on large poultry farms, I've only been in post a year, at some point before I...
Replies
6
Views
2K
Hi friendly people, As you may be aware, I'm a plumber, so quite possibly what I am seeing is correct, though it seems a bit odd to my untrained...
Replies
4
Views
6K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
222

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock