Discuss Do SPDs need RCD protection ? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi there ,
Currently doing a college project where i need to select protective devices for the contract. I'm now at the point of selecting SPDs and had a couple questions. I have chosen MCG RCBOs for my circuit breakers in this project for all my boards apart from the board supplying distribution circuits which has MCCBs - so my SPDS will need to be same brand and the MCG SPDs require a 63A MCB to go with it. 1st of all its a commercial building -TN-C-S , do I need SPDs in every DB board ?.
Secondly do SPDs need RCD protection- as in does the MCB that goes with it need RCD protection. And if they do need RCD protection how would I go about installing them in RCBO boards.
If they need RCD protection and in my boards are RCBOs would I have to install a separate RCD to protect the MCB that's with the SPD or could I fit the SPD with an RCBO ?
 
I would fit SPD’s @ the origin… but you can fit them elsewhere too
The Mcb supply to the SPD will provide protection… On a TT system mcb protection would be ok….most SPD ‘s are integral with the main switch
 
Secondly do SPDs need RCD protection- as in does the MCB that goes with it need RCD protection. And if they do need RCD protection how would I go about installing them in RCBO boards.
Let's do this bit first. No. An SPD has to be able to dissipate surges to earth. If you had an RCD in front of it, after the first 20-30ma of the surge the RCD would trip and the surge would have to find another path rendering the SPD rather ineffective.
So most of the time it's as simple as install the MCB and install the SPD off it.
Here is a Fusebox example:
(there's also an earth wire from underneath the SPD to the CPC bar which you can't see)
1685281916578.png


do I need SPDs in every DB board
Generally if they are all within the same building downstream of the same supply, no.
If a distribution circuit went to another building via an overhead supply then it's a different situation as lightning could strike the distribution circuit.
 
Let's do this bit first. No. An SPD has to be able to dissipate surges to earth. If you had an RCD in front of it, after the first 20-30ma of the surge the RCD would trip and the surge would have to find another path rendering the SPD rather ineffective.
So most of the time it's as simple as install the MCB and install the SPD off it.
Here is a Fusebox example:
(there's also an earth wire from underneath the SPD to the CPC bar which you can't see)
View attachment 108448


Generally if they are all within the same building downstream of the same supply, no.
If a distribution circuit went to another building via an overhead supply then it's a different situation as lightning could strike the distribution circuit.
Ok thank you noted- and the building is as one but has 2 blocks- cafe block with a pool in basement and the hotel block with the rooms in. So I will put the SPD in The main board which then supplys the other boards and as it is a 3 phase board I'll put a 3 pole SPD on
 
Let's do this bit first. No. An SPD has to be able to dissipate surges to earth. If you had an RCD in front of it, after the first 20-30ma of the surge the RCD would trip and the surge would have to find another path rendering the SPD rather ineffective.
So most of the time it's as simple as install the MCB and install the SPD off it.
Here is a Fusebox example:
(there's also an earth wire from underneath the SPD to the CPC bar which you can't see)
View attachment 108448


Generally if they are all within the same building downstream of the same supply, no.
If a distribution circuit went to another building via an overhead supply then it's a different situation as lightning could strike the distribution circuit.
Off topic, but you've done well to get the conductors all nice and neat, especially with the annoying neutral leads from the RCBO's.
 

Reply to Do SPDs need RCD protection ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi got a 8 panel solar system on bungalow, changing the board to 18th edition spd board Solar feed is chased into wall so will this need a type B...
Replies
4
Views
235
I've been installing Type 2 SPDs in consumer units for several years now, and they always come as a pair, connected across L & E, and across N &...
Replies
2
Views
523
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
998
Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
Replies
2
Views
497

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock