Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.

Discuss copper equivalent of steel in the Electrical Forum area at ElectrciansForums.co.uk.

Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. wirepuller
    Offline

    wirepuller Forum Mentor

    Location:
    south uk
    Does anyone have the copper equivalent of a two core 16mm SWA to hand? Or the minimum SWA 2 core CSA in which the steel would be equivalent to a 10mm copper conductor? Don't have the info to hand.
    Thanks.....
     
  2. Leesparkykent
    Offline

    Leesparkykent Super Moderator Staff Member Super Moderator

    Location:
    Kent
    In conductivity or as in CSA?
     
  3. westward10
    Online

    westward10 In echoed steps I walk across an empty dream. Staff Member Moderator

    Location:
    Northamptonshire
    For conductivity off the top of my head as no books to hand 95.0 or above.
     
    • Like Like x 1
  4. Ian1981
    Offline

    Ian1981 Forum Mentor

    Location:
    North east
    The ratio in gn8 for copper to steel is 8.5.
    So a 85 mm steel conductor -equivalent conductive copper conductor is 10 mm
    85/8.5=10
     
    • Like Like x 1
    • Dumb Dumb x 1
  5. happyhippydad
    Offline

    happyhippydad Member Electrician's Arms

    Location:
    Gloucestershire
    This really isn't my area as it's rarely used in domestics.

    However, I've found from one table on the net (https://www.dungannonelectrical.co.uk/dun1-shop/pdf/cable/SWA.pdf) that 2 core 16mm will have a 42mm CSA of steel.

    I am then not sure if you divide by 8.8 or 2.75.

    AJJewsbury explains it below: (IET Forums - SWA Size of steel armour for CPC - https://www.theiet.org/forums/forum/messageview.cfm?catid=205&threadid=47544)

    "If the armour is only being used as a c.p.c. (and not as PME bonding conductor) then you're not really interested in its actual resistance (either absolute or copper equivalence) - just its ability to survive an earth fault current for the required time - i.e. it's "k" value (tables 54.2 and following). E.g. if the cable runs at max 70 degrees in normal service with a maximum ambient of 30 degrees, then k for copper is 143 and steel 52 - making copper just 2.75 times "better" than steel for the same c.s.a.

    So if the cable had 76mm2 of steel that would be the equivalent of 27.6mm2 of copper - easily satisfying table 54.7. "
     
    • Like Like x 1
  6. spinlondon
    Offline

    spinlondon Forum Mentor

    Location:
    Harlow Essex
    I believe the minimum CSA for the armour to have the equivalent conductivity of a 10mm2 copper conductor is 95mm2.
    I think it would be cheaper to run in a 3core.
     
    • Like Like x 1
  7. wirepuller
    Offline

    wirepuller Forum Mentor

    Location:
    south uk
    Many thanks for the replies.
    Just to clarify an EICR on a recent build (new <5yrs ago,) steel framed outbuilding has a 2core 16.0mm SWA feeding from a TNCS supply in the main building. No main bonding has been installed to the steel frame, the supply head is a TPN 100a so a minimum 10mm copper equivalent is required to serve as main bonding and cpc. Just to complicate matters a supply back from the outbuilding serves a pump installation in the main building so converting to TT would result in two separate earthing systems in the main building.
    Why the original installer put in a 2 core is beyond me, but it is what it is now.
     
    Last edited: Jan 9, 2019
  8. Ian1981
    Offline

    Ian1981 Forum Mentor

    Location:
    North east
    A 76mm steel conductor would equate to around 8.9mm copper conductive equivalent
     
    • Like Like x 1
    • Dumb Dumb x 1
  9. Ian1981
    Offline

    Ian1981 Forum Mentor

    Location:
    North east
    Yep a 16mm 2 core armour isn’t going to cut it
     
    • Like Like x 2
    • Dumb Dumb x 1
  10. buzzlightyear
    Offline

    buzzlightyear please let me back in to the prison cell. Electrician's Arms

    Location:
    star command
    where's Pete with the information he mostly on the ball .stop taking his job. ;)
     
    • Funny Funny x 1
Loading...
Similar Threads - copper equivalent steel Forum Date
Domestic Earthing copper pipes ............. DIY Electrical Forum Mar 13, 2019
Cable plasticiser reacting with copper. Electrical Forum Jan 26, 2019

Share This Page

Users found this page by searching for:

  1. copper equivalent of swa

    ,
  2. equivalent conductor area copper steel

Electricians Directory Post a Domestic Job Post a Commercial Job