Discuss copper equivalent of steel in the UK Electrical Forum area at ElectriciansForums.net

D

Deleted member 9648

Does anyone have the copper equivalent of a two core 16mm SWA to hand? Or the minimum SWA 2 core CSA in which the steel would be equivalent to a 10mm copper conductor? Don't have the info to hand.
Thanks.....
 
This really isn't my area as it's rarely used in domestics.

However, I've found from one table on the net (https://www.dungannonelectrical.co.uk/dun1-shop/pdf/cable/SWA.pdf) that 2 core 16mm will have a 42mm CSA of steel.

I am then not sure if you divide by 8.8 or 2.75.

AJJewsbury explains it below: (IET Forums - SWA Size of steel armour for CPC - https://www.------.org/forums/forum/messageview.cfm?catid=205&threadid=47544)

"If the armour is only being used as a c.p.c. (and not as PME bonding conductor) then you're not really interested in its actual resistance (either absolute or copper equivalence) - just its ability to survive an earth fault current for the required time - i.e. it's "k" value (tables 54.2 and following). E.g. if the cable runs at max 70 degrees in normal service with a maximum ambient of 30 degrees, then k for copper is 143 and steel 52 - making copper just 2.75 times "better" than steel for the same c.s.a.

So if the cable had 76mm2 of steel that would be the equivalent of 27.6mm2 of copper - easily satisfying table 54.7. "
 
Many thanks for the replies.
Just to clarify an EICR on a recent build (new <5yrs ago,) steel framed outbuilding has a 2core 16.0mm SWA feeding from a TNCS supply in the main building. No main bonding has been installed to the steel frame, the supply head is a TPN 100a so a minimum 10mm copper equivalent is required to serve as main bonding and cpc. Just to complicate matters a supply back from the outbuilding serves a pump installation in the main building so converting to TT would result in two separate earthing systems in the main building.
Why the original installer put in a 2 core is beyond me, but it is what it is now.
 
Last edited by a moderator:
This really isn't my area as it's rarely used in domestics.

However, I've found from one table on the net (https://www.dungannonelectrical.co.uk/dun1-shop/pdf/cable/SWA.pdf) that 2 core 16mm will have a 42mm CSA of steel.

I am then not sure if you divide by 8.8 or 2.75.

AJJewsbury explains it below: (IET Forums - SWA Size of steel armour for CPC - https://www.------.org/forums/forum/messageview.cfm?catid=205&threadid=47544)

"If the armour is only being used as a c.p.c. (and not as PME bonding conductor) then you're not really interested in its actual resistance (either absolute or copper equivalence) - just its ability to survive an earth fault current for the required time - i.e. it's "k" value (tables 54.2 and following). E.g. if the cable runs at max 70 degrees in normal service with a maximum ambient of 30 degrees, then k for copper is 143 and steel 52 - making copper just 2.75 times "better" than steel for the same c.s.a.

So if the cable had 76mm2 of steel that would be the equivalent of 27.6mm2 of copper - easily satisfying table 54.7. "
A 76mm steel conductor would equate to around 8.9mm copper conductive equivalent
 
Many thanks for the replies.
Just to clarify an EICR on a recent build (new <5yrs ago,) steel framed outbuilding has a 2core 16.0mm SWA feeding from a TNCS supply in the main building. No main bonding has been installed to the steel frame, the supply head is a TPN 100a so a minimum 10mm copper equivalent is required to serve as main bonding and cpc. Just to complicate matters a supply back from the outbuilding serves a pump installation in the main building so converting to TT would result in two separate earthing systems in the main building.
Why the original installer put in a 2 core is beyond me, but it is what it is now.
Yep a 16mm 2 core armour isn’t going to cut it
 

Reply to copper equivalent of steel in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Does anyone know what the cable in the picture is called? Or anything about it? Labelling on the outside is “E SPC Electric Cable 600/1000v” Its...
Replies
9
Views
1K
Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
Replies
8
Views
903
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
780
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
740

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock