Discuss Could someone decipher this wiring diagram for me? I bought 10-3 wire to run to it, looking to wire for 230V. in the UK Electrical Forum area at ElectriciansForums.net
Yessir, but I'm not positive what the diagram is telling me to do.Use the diagram on the right.
No.Yessir, but I'm not positive what the diagram is telling me to do.
My interpretation is this :
Hot w/ blue
Neutral w/ white, red, orange
Ground w/ brown
Hot w/ Black, yellow
Is that correct?
That’s a simple wiring diagram and I think these folks have you on the right track. It’s just a duel voltage motor
OK so basically I should be using a 2 wire not the 10-3 I bought for this.No.
Live to blue.
Neutral / other live to yellow and black together.
White, Red and Orange together in an insulated connector.
Brown in its own insulated connector.
That is correct all you need is 2 live wires and a equipment ground at 240vacOK so basically I should be using a 2 wire not the 10-3 I bought for this.
Much appreciated sirThat is correct all you need is 2 live wires and a equipment ground
Your welcomeMuch appreciated sir