Discuss Course work in the UK Electrical Forum area at ElectriciansForums.net

J

Jordanh1992

A 230 volt 14 kW domestic storage heater, installed in a house is to be supplied by a 15m run of PVC insulated and sheared cable, clipped to a surface. The circuit is to be protected by a BS 3036 fuse and the value of external impedance is 0.85 ohms. Calculate the minimum size cable that can be used for this circuit to comply with shock protection.
Ib: 60.87
In: 100
It: 60.87
Iz: 65 No correction factors...
csa= 10mm2
VD = 4.4 x 60.87 x 15/1000 = 4.02 (VD is below 11.5)
Max Zs = 0.53 and that is already higher than the Ze? What should I do...
 
so...has any thought been given to the earthing arrangements here....as if its a TN system...you wouldn`t even start as the Ze has failed....if its a TT then an RCD to 30mA would be required for fault....at which point you can use the formula 50/0.03=1666.66
so, i give you 1667 ohms....so, as far as disconnection times are concerned....
 
you dont need to know the earthing arrangements to complete the question.
and i wouldnt be using 100A fuse for a 60a load , is 63 or 80a not available ?
 
you dont need to know the earthing arrangements to complete the question.
and i wouldnt be using 100A fuse for a 60a load , is 63 or 80a not available ?
biff....i`v given him an example of how to carry out an adiabatic on his other thread he`s got going....now, let him suss it out for himsen....
 
A 230 volt 14 kW domestic storage heater, installed in a house is to be supplied by a 15m run of PVC insulated and sheared cable, clipped to a surface. The circuit is to be protected by a BS 3036 fuse and the value of external impedance is 0.85 ohms. Calculate the minimum size cable that can be used for this circuit to comply with shock protection.
Ib: 60.87
In: 100
It: 60.87
Iz: 65 No correction factors...
csa= 10mm2
VD = 4.4 x 60.87 x 15/1000 = 4.02 (VD is below 11.5)
Max Zs = 0.53 and that is already higher than the Ze? What should I do...


ok Im doing 2395 in june someone will correct me if im wrong.

Here is what i come up with.

[FONT=&quot]If= Uo/Zs 230/0.85=270.85

[/FONT]
[FONT=&quot][/FONT] S= √(I²×t) [FONT=&quot][FONT=&quot]270.85[/FONT] [/FONT][FONT=&quot] x [/FONT][FONT=&quot][FONT=&quot]270.85 [/FONT]x 5 = 366798.61[/FONT]


[FONT=&quot]square root of that is: [/FONT]605.63

divide that by k factor of 115= 5.26mm

So the next cable size is 6mm





[FONT=&quot] [/FONT]
 
Jeeze I'm not asking for the answer or I would have said that...
iv been trying to work this out for over a week, I'm asking for advise... Where to look, what to take into account, what I might be doing wrong! I'm not an expert, but if you wanna be awkward then that's fine. And nope the tables show that the only protective device is an 100A
 
Calm down Jordan :)

You're not stupid and you are persistent so you'll get there in the end.

The question asks about shock protection so it's asking about disconnection time not cable temperature. Forget Adiabatic (in this case) and work out disconnection time for the 3036 fuse.

Are you SURE it's not a 1.4kW storage heater? (they exist, 14kW storage heaters don't , as far as I know, exist).

Hope that's helpful
Laurie
 
Calm down Jordan :)

You're not stupid and you are persistent so you'll get there in the end.

The question asks about shock protection so it's asking about disconnection time not cable temperature. Forget Adiabatic (in this case) and work out disconnection time for the 3036 fuse.

Are you SURE it's not a 1.4kW storage heater? (they exist, 14kW storage heaters don't , as far as I know, exist).

Hope that's helpful
Laurie

Have to disagree with you it asks this

Calculate the minimum size cable that can be used for this circuit to comply with shock protection?
 

Reply to Course work in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hello, hopefully ive got this right but if someone can check over my maths for me, id appreciate it. Im needing to install a new supply cable...
Replies
3
Views
894
Morning team Question about volt drop. I presume I am missing something here. So firstly the facts out the OSG. Table 7.1, page 66, lighting...
Replies
20
Views
3K
This is my first post so please be gentle! I've been asked to extend an RFC into an extension at the back of an 8 year old property. It is a...
Replies
24
Views
3K
Hi I've a few questions regarding volt drop. Apologies if its a little longwinded but I'd like to get my head around everything. An example...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock