Search for tools and product advice,

Discuss Crimping 6mm T+E in the UK Electrical Forum area at ElectriciansForums.net

S

sjm

Hi Guys.

So as the title says I recently had to crimp some 6mm T+E using yellow pre-insulated butt crimps. I have a pair of Engex ratchet crimping pliers, which work very well with red and blue crimps, but when I tried to crimp the 6mm the crimps could be easily pulled from the cable. I eventually (after several attempts) managed to get a firm crimp by using the yellow setting first then using the blue die to about half way, then releasing the jaws from the ratchet.

Has anyone else had this problem? Am I using cheap butt crimps, should I get a better crimping tool?
Any suggestions or advice would be greatly appreciated.

Thanks in advance.
Steve.
 
When did you last have your crimper calibrated.... also the tug test is not an indication of a good crimp... it may seem tight but under short circuit when possibly many thousands of amps will flow for a split second that is what decides a good and a bad crimp..... cheap ratchet crimper result in poor crimp....also the quality of the crimps also is to be put into question.
I assume being 6mm it is stranded which is ok for your standard ratchet crimper and butt crimps.
 
Rather use the uninsulated crimps and heat shrink to insulate if necessary. I find the insulated blue / yellow crimps are hit and miss at best, the uninsulated are much more consistent.
 
I had some blue crimps from screwfix once and they where absolutely dreadful. Got some more from TLC and they where some much better.
 
Wago do a red 40 amp push in and it can handle a 6mm2, I use them and have a box on the van, no good using them though unless you have a decent enclosure, they are bulky.
 
Good quality crimp in my opinion.. And if you think a crimp is a crimp well your wrong. Bought a batch from screwfix and then a batch a week later (No im not using a lot of crimps but a van is a skip and its easier to buy new then look) and they were totally diffrerant..
 
When did you last have your crimper calibrated.... also the tug test is not an indication of a good crimp... it may seem tight but under short circuit when possibly many thousands of amps will flow for a split second that is what decides a good and a bad crimp..... cheap ratchet crimper result in poor crimp....also the quality of the crimps also is to be put into question.
I assume being 6mm it is stranded which is ok for your standard ratchet crimper and butt crimps.

Crimpers calibrated?

Get serious, if you can’t tell by the pressure you apply to the crimper then you’ve no right being an electrician.

All crimp manufacturers are slightly different, do you have a set of crimpers for each crimp size and manufacturer also the cable manufacturers? It’s the only way they could be calibrated.

I want to see someone calibrate a BICC crimper. Sorry DW but due to the mechanics of the crimping tool it's impossible!
 
Had the same issue a while ago crimping earth for unused 6mm core in SWA, stupid cheap ratchet crimper of ebay, yellow crimp just slipped strait off....so I stupidly tried the blue size on the crimper and got it stuck, cut the cable back and threw the whole thing in the bin.

Just used the non ratchet type one that came in the assorted lug it box worked fine...but wouldn't use it for live cables.

I like the idea of solder/braze cables then heat shrinking them does anyone here do that ?
 
I have recently had this issue, and eventually found that the wall thickness of the metal inside the crimp varies a lot between good quality and cheap crimps. Basically, the diameter was the same on both, but on the cheapies, the wall was thinner, and the crimpers only crimp so far.

From now on, i will only use "SWA" branded crimps, and they work fine.

Also, some ratchet crimpers have an adjustment.

Mine is a star shaped disc which has a screw that can be loosed off, the "star" turned and then screwed tight.

Although, this still didnt work on the cheap crimps.
 
I have recently had this issue, and eventually found that the wall thickness of the metal inside the crimp varies a lot between good quality and cheap crimps. Basically, the diameter was the same on both, but on the cheapies, the wall was thinner, and the crimpers only crimp so far.

From now on, i will only use "SWA" branded crimps, and they work fine.

Also, some ratchet crimpers have an adjustment.

Mine is a star shaped disc which has a screw that can be loosed off, the "star" turned and then screwed tight.

Although, this still didnt work on the cheap crimps.

I have the same sort of crimpers, with the adjustable "star" shaped thingy!!lol But I always double crimp and not in the same spot!!! this is a common mistake.....I crimp in the middle of the crimp, then at the top of the crimp, this ensure a sound connection. As for tug testing, I used the wago's the other day for the first time and Im not convinced they are maintenance free!!! I tugged them all and most seemed fairly loose.....some even came off after I decent tug..lol But the push fit ones seemed to spin around on the cable????? WTF????

I think they need to test the wago's for a few more years yet, before they can be classed as maintenance free!!. As for the crimpers, the "star" shaped thingy that JASON mentioned can be used to tighten or slacken the pressure of the tool.
 
Jason has hit the nail on the head, the quality of the crimp as well as the crimper is key to a decent connection.

SWA crimp terminals are the best quality for the insulated type, in fact even their CT crimps are likely the best quality on the market.

Crimpers, you get what you pay for, it never ceases to amaze me when you see sparks that have spent £30-£40 on a set of decent VDE rated sidecutters or pliers, normally both, and yet object to spending decent money on a decent crimper and get a cheap £10 jobby from B&Q or Maplin.

I use one of THESE for crimping up to 6mm² insulated connectors/terminals and one of THESE for the uninsulated crimps

People often make the mistake of using the ones designed for one type of terminal for both types, and this is always creates a bad termination.
 
I just looked at the spec for the first set of crimpers OS put up.
No specific conductor sizes given for a coloured crimp size, so how much do you crimp a 1.5 compared to a 1mm. Both go in a red crimp.

DW, calibrating a set of crimpers, don’t make me laugh!
 
Think i've said this a few times on here when crimping matters come up,. ...I don't like and never have liked the PVC Butt crimps, the heat shrink pre-insulated butt crimps are not too bad, but i still prefer bare crimping with 2 layers of heat shrink tube cover. One to cover the actual bare metal joint and an overall cover. As everyone has stated it's all very much down to the quality of both the crimps and crimping tool being used as to whether your finished crimp joint is going to be any good or not!!

As for calibrating crimp pliers, Yes it can be done, but only with those crimping tools that have the facility, and they normally come in at around £100+ or more and will be the type, say manufactures and the MOD use. Though maybe now day's the throw away philosophy has taken over!! lol!!
 
I just looked at the spec for the first set of crimpers OS put up.
No specific conductor sizes given for a coloured crimp size, so how much do you crimp a 1.5 compared to a 1mm. Both go in a red crimp.

DW, calibrating a set of crimpers, don’t make me laugh!

I think you will find all crimps suffer the same problem Tony, I have never had a crimper that adequately crimped a 1.0mm, but then I have a specific crimper for 0.5 and 1.0mm crimps :)

With regards calibration, Yes you can have crimpers calibrated, in the telecoms (mobile) and the Nuclear industry all tools of this nature have to be calibrated on a regular basis or you cannot use them. I have had my crimps calibrated on numerous occasions when working on cell Infrastructure projects and on Nuclear sites..However for general sparking work so long as you keep your crimpers in good order and lubricate occasionally then they should never need to be calibrated, only the occasional adjustment if possible.
 
We did some subbie work for a controls firm on the Loyd's bank building in London about 10 years ago and they wanted all our crimping tools to be calibrated , we ended up just using their ones for the job as it would have held up the job getting our ones done .

But i am with you on this one Tony , what a load of balls !
 
I think you will find all crimps suffer the same problem Tony, I have never had a crimper that adequately crimped a 1.0mm, but then I have a specific crimper for 0.5 and 1.0mm crimps :)

With regards calibration, Yes you can have crimpers calibrated, in the telecoms (mobile) and the Nuclear industry all tools of this nature have to be calibrated on a regular basis or you cannot use them. I have had my crimps calibrated on numerous occasions when working on cell Infrastructure projects and on Nuclear sites..However for general sparking work so long as you keep your crimpers in good order and lubricate occasionally then they should never need to be calibrated, only the occasional adjustment if possible.

I wonder if my soldering iron needs calibrating yet? :smilewinkgrin:
 
Calibration of crimpers .. Back in the early eighties I worked for an electrical engineers and we did a lot of panel work for bt although I believe they were still known as post office then. We had to use calibrated crimpers and on a regular basis had to send them test pieces of crimped cables of various sizes. Presume they put them on a test rig of sorts. You were only supposed to use those calibrated crimpers on their work and not just grab any old pair.
They were a funny lot to do work for... Also had to regularly calibrate the avo's but that's another story.
 
Crimps for me are a temporary repair.

Like Geordie I’ll solder a ferule on and insulate as necessary. Be it control or 11KV, different situations require different insulation methods.

I had to extend some 400mm² singles, I turned my own ferules out of copper round bar to be sweated on to the two conductors.


To be honest my ratchet crimpers have hardly been used in all the time I’ve had them. (30 years.) But then I’ve been in industries where a failure could be catastrophic.
 
For normal every day crimping tools, they can't be calibrated end of!! They will be deemed ''fit for purpose'' or otherwise, by any certifying lab. Those crimping tools that can and are calibrated, will have areas where parts can be readily replaced and/or adjusted to bring them within required parameters, ..eg within manufactures stated ''calibration'' values !!
 
Im happy to use pre-insulated crimps, but the ones we get at work are good gear.
I have a set of Newey and Eyre crimpers, which are re-branded Cembre Crimpstar ones (a friend owns a cembre set, and theyre exactly the same). Cembre seem to be the market leader in crimping tools. These are the branded ones: http://www.cablejoints.co.uk/images...mbre-Crimpstar-Ratchet-Crimpers1267524905.jpg
For bootlace crimps, I have a set of self adjusting ones. These are the exact ones:
http://img.directindustry.com/images_di/photo-g/manual-crimping-tool-20429-3268223.jpg
 
I have recently had this issue, and eventually found that the wall thickness of the metal inside the crimp varies a lot between good quality and cheap crimps. Basically, the diameter was the same on both, but on the cheapies, the wall was thinner, and the crimpers only crimp so far.

From now on, i will only use "SWA" branded crimps, and they work fine.
Also, some ratchet crimpers have an adjustment.

Mine is a star shaped disc which has a screw that can be loosed off, the "star" turned and then screwed tight.

Although, this still didnt work on the cheap crimps.


Thats the make i use and there ratchet crimper also and no probs so far
 
I use Klauke for my smaller crimps only SWA stuff as above screwfix are pants, knipex for bootlaces round and square and cembre hydraulics for bigger stuff.
 
Crimps for me are a temporary repair.

Like Geordie I’ll solder a ferule on and insulate as necessary. Be it control or 11KV, different situations require different insulation methods.

I had to extend some 400mm² singles, I turned my own ferules out of copper round bar to be sweated on to the two conductors.


To be honest my ratchet crimpers have hardly been used in all the time I’ve had them. (30 years.) But then I’ve been in industries where a failure could be catastrophic.

one of the guys i work with uses ck ratchet crimpers for ferrules.

usually the guy doing the testing has to recrimp them all as they just slide straight off.

personally on ferules etc i just use crimping pliers as your guaranteed a good connection cause your used to how much pressue there should be (plus i always crimp mine 1 size down after as well for a tight connection).
(was in a pinch a while ago and a pair of grips make a nice temp ferrule crimper, much easier to use than ratchet crimpers as well)

with crimpers i just use a pair of silverline crimpers but there collecting dust in my bag as only really use anything bigger than 1mm onece in a blue moon.


ill buy a decent pair eventually but there is no point atm as i dont need one at all. (would use cold chisel and hammer if they broke though till i got replacement)
 
one of the guys i work with uses ck ratchet crimpers for ferrules.

usually the guy doing the testing has to recrimp them all as they just slide straight off.

personally on ferules etc i just use crimping pliers as your guaranteed a good connection cause your used to how much pressue there should be (plus i always crimp mine 1 size down after as well for a tight connection).
(was in a pinch a while ago and a pair of grips make a nice temp ferrule crimper, much easier to use than ratchet crimpers as well)

with crimpers i just use a pair of silverline crimpers but there collecting dust in my bag as only really use anything bigger than 1mm onece in a blue moon.


ill buy a decent pair eventually but there is no point atm as i dont need one at all. (would use cold chisel and hammer if they broke though till i got replacement)

400mm Ferules don’t just slide off when I’ve sweated them on!

From what you have said so far before you buy that decent pair of crimpers, learn what they do first!
 
(plus i always crimp mine 1 size down after as well for a tight connection).

(was in a pinch a while ago and a pair of grips make a nice temp ferrule crimper, much easier to use than ratchet crimpers as well)

Are you being serious? Please don't do this, get rid of your home made grip-crimpers and don't use the 'next size down' slot in the tool. Just spend a few pounds on a half-decent ratchet crimper and use it properly, you're much less likely to start a fire or have call backs on your jobs.
 
Last edited:
Are you being serious? Please don't do this, get rid of your home made grip-crimpers and don't use the 'next size down' slot in the tool. Just spend a few pounds on a half-decent ratchet crimper and use it properly, you're much less likely to start a fire or have call backs on your jobs.

not a rachet crimper.

pliers and it more to add extra pressue on small cables. my crimpers work fine and i dont need to do this, its just become a habbit.


the idea of a bootlace is to squeeze it onto the cable, the tighter the crimp the better connection
 
not a rachet crimper.

pliers and it more to add extra pressue on small cables. my crimpers work fine and i dont need to do this, its just become a habbit.


the idea of a bootlace is to squeeze it onto the cable, the tighter the crimp the better connection


As long as the pressure is applied correctly, with the correct tool, you may be right.
 
Crimpers are tested using 'go' / 'no go' tools, which test the pressure of the mating surfaces. Ours were checked every 6 months. A fail and they were binned, err brought home :)
 

Reply to Crimping 6mm T+E in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
693
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
943
We often see folk asking about which crimp tool to buy/use so I decided to round up my collection and put them to the test. Ladies and gentlemen...
Replies
25
Views
10K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
778

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock