Discuss Crumbly PVC cable (red only) in the UK Electrical Forum area at ElectriciansForums.net

SJD

-
Mentor
Esteemed
Arms
Reaction score
2,812
Today on an EICR I came across some old (1960's, I think) PVC lighting cable - twin red/black, no earth - where the red was crumbly. It behaved like old perishing rubber, any bending and it cracks - but it is defintely plastic of some sort. The black was perfectly OK, as was the sheath. Curious to know if anyone else has seen this in PVC cable.
PVC crumbly wire.jpg
 
Last edited by a moderator:
Definitely tinned copper (the tinning can be scraped off). The sheath was vaguely grey-ish, but I didn't bring a sample home to recall exactly.
 
Interesting. The left-hand end of that specimen has a glossy sheen that initially made me wonder whether it was PE, rather than PVC, but is probably migrated plasticiser. PVC has multiple possible degradation modes such as plasticiser evaporation, hydrolysis and dehydrochlorination. How fast any of these processes occur depends on the material composition, temperature, environmental exposure etc. The processes interact and can be self-catalysing especially if the exudate cannot escape easily.

The plasticiser used in the batch of red insulation might have been of unusually low molecular weight, resulting in accelerated migration and evaporation, despite performing to spec during manufacture. Unlike cables with green goo, there won't have been any reaction with the conductors because they are tinned (the extreme loss of phthalate in green goo cables is usually the result of the antioxidant.)

Is the red insulation or the inside of the sheath sticky? Does it smell of anything?
 
No smell and nothing sticky on the red insulation inside or out, it is quite dry, has perhaps a waxy feel to it.
Unfortunately I didn't bring back a sample of the sheath but I don't recall it being sticky either.
 
I have some in front of me, Red/white/blue which I replaced some time ago which was used for two way switching in the house I live in. Kept it just for interest, but it is definitely more plastic than pvc and much harder to strip.

Regards.
 
I thought it might be PE hence my first comment.
@SJD, try burning a tiny bit outdoors. Does the smoke smell like candle wax?
 
I have some in front of me, Red/white/blue which I replaced some time ago which was used for two way switching in the house I live in. Kept it just for interest, but it is definitely more plastic than pvc and much harder to strip.

Regards.
Good to see you Clive long time no see
 
OK so it's polyethylene, rather than PVC. I'm not 100% sure what the degradation mechanism is here, but I would think it's likely to be polymer chain cleavage. When the average molecular weight decreases to a certain point, it rapidly transitions from a plastic form to a brittle one. The trigger might be oxidation. Was that sample exposed to the air e.g. in an accessory back box or from within a sheathed section of cable? Are you able to get any more samples of complete cable or is that job finished?

I wonder why the red and black behave differently, given that @brianmoooore has experience of the red failing first too. We don't know whether the correlation is causative or coincidental.
 
The sample was from the end of a cable, part exposed, part sheathed - the red seemed equally crumbly in both cases - while the black was fine.

I don't currently have the chance to get any more samples. There is still some of this cable in service, recommended to be rewired, but that is probably not happening for a while.
 
However in a sheathed cable the incident light on the insulation is much reduced and in many installed situations effectively zero. Unless the effect is shown to be absent in cable permanently in the dark, I'm inclined to think that the difference is caused by composition, rather than exposure. The question is then whether the red compound is inherently less stable, had some intentional difference in formulation that was unrelated to the colour and could equally have affected the black, or whether it was actually defective in manufacture.
 
The crumbly red section was under a light fitting and not exposed to light, same as the black non-crumbly. I'm inclined to believe the thought that either the red was a different formulation or defective. If I get called back to rewire, I'll certainly collect a better sample next time. Thanks for the comments.
 

Reply to Crumbly PVC cable (red only) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
229
Hi guys, Whilst renewing my loft insulation I came across a few runs of very old cable. (Please see attached pictures). These cables are lead...
Replies
6
Views
2K
Getting desperate to clear my small garage, and I have a bit of old red/black T&E. I used a few bits to add a socket or two in my flat and a...
Replies
5
Views
1K
Straightforward EICR job coming up on my village church. Don’t think it’s ever had one before. Quick visual survey today to estimate my time, and...
Replies
10
Views
2K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
47
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock