    Hi,

    I have a 16kW array fed to my cu via 3 - 5kW solis inverters. I have a 4kW export limit so each inverter has a ct clamp. The 3 clamps are together on my main incoming cable.

    Is it ok to have these 3 clamps touching each other?
    How is it decided which inverter to shut down?

    We have a lot of tripping issues, the system was installed incorrectly & still doesn't work properly. Could there be interference between the clamps & would them constantly turning on and off randomly be causing the tripping.

    Thanks in advance

    Greg Webb
     
  2. UKMeterman
    Offline

    UKMeterman Electrician's Arms

    Well,
    Each one will be indepently deciding, I am pushing out too much, need to to turn down the wick. Depending on the control loop and the nature of the local load this could cause instablitlies. You might also want to check the local supply voltage to see if you are tripping on over voltage.
     
    Last edited: Jul 15, 2018
  3. Wilko
    Online

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    Hi - just trying to understand how the 3 invertors can be limited to achieve 4kW total system output. Are you saying that each of the 3 invertors has their own CT and is independently trying to limit to 4kW? (likely result today being 12kW ...). Or if not, how does each know what the other is doing? If you've a circuit diagram and pics it might help :) .
     
    • Like Like x 1
  4. jouleflow
    Offline

    jouleflow Regular EF Member

    Location:
    wellingborough
    Thanks for the reply, I'm not an electrician so I can't say how each one is set up. I strongly believe that each one is set to 4kW so once this is reached one of them will turn down or off, if it still is over 4kW then another will turn down or off. I am positive they are all set up the same.
     
  5. jouleflow
    Offline

    jouleflow Regular EF Member

    Location:
    wellingborough
    here is a pic of all 3 ct clamps in a row on the incoming main cable.

    ct clamps.jpg
     
  6. UKMeterman
    Offline

    UKMeterman Electrician's Arms

    Ok a picture paints 1000 words, they need to be clamped round 1 of the 4 cables going into the bottom of the electricty meter!
     
  7. jouleflow
    Offline

    jouleflow Regular EF Member

    Location:
    wellingborough
    Thanks, I will try that, it just seems that the clamps will then simply be the other side of the main incoming fuse. Wouldn't they still be sensing the reverse flow to the grid in either position? I am thinking of using the brown cable from the bottom of the fuse to the meter. See pic attached.

    ct2.jpg
     
  8. UKMeterman
    Offline

    UKMeterman Electrician's Arms

    Yep, that would be the one, if you clamp round the black cable the magnetic field of the flow and return cancel each other out so there is no signal to measure.
     
    • Like Like x 1
    • Agree Agree x 1
  9. jouleflow
    Offline

    jouleflow Regular EF Member

    Location:
    wellingborough
    Of course!!, brilliant deduction. Thank you so much, things are never quite what they initially seem. If it is ok I will post again after a few days to let you know how it is working.
     
  10. sean_ork
    Offline

    sean_ork Regular EF Member

    Was this a DIY installation ?
     
  11. jouleflow
    Offline

    jouleflow Regular EF Member

    Location:
    wellingborough
    No a local company put it in last September and I had loads of problems far too many to list here but included no drip loops - ct clamps on the wrong cable - meter frying - loads of "spare" holes in roof, new supply cable from grid - earthing problems etccccccc.

    p.s just tripped again!
     
  12. sean_ork
    Offline

    sean_ork Regular EF Member

    Is your supply single or three phase ?
     
  13. UKMeterman
    Offline

    UKMeterman Electrician's Arms

    You can see the meter and supply fuse, count the fuses / cables
     
  14. jouleflow
    Offline

    jouleflow Regular EF Member

    Location:
    wellingborough
    single phase.
     
  15. jouleflow
    Offline

    jouleflow Regular EF Member

    Location:
    wellingborough
    If it helps I have an Iboost clamp on the same cable that was removed for the earlier pics. This is the current set up, the Iboost has the white wire.

    4 clamps.jpg
     