Discuss CU Change - Ring Tripping RCD Low IR in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

M

markthespark

Hi i went to change a CU last night and the ring main is causing the RCD to trip even with everything unplugged.

I am going back today to investigate abit more, i have just left the ring on the non RCD side for the time being.

The customer is as tight as and doesnt really want to pay for me finding a fault "as it worked before"

I am willing to spend abit of time looking for it for my own peace of mind but the house only has 1 ring so i can tell its going to be a nightmare.

Can i issue an installation certificate for the CU with low insulation resistance readings and note it in the comments?

or can i issue a EICR and recommend a rewire?

There is also no earth on the lighting but all the fittings are plastic, so i have recommended that the lights need a rewire.
 
Did you do any tests on the circuit prior to changing the consumer unit or did you discover the low insulation reading after you changed the board ???
 
Possible a trapped neutral in one of the sockets , un plug every thing insulation test , it the old thing when you do a consumer upgrade "well it worked before " just explain how the RCD works with the old system working with a neutral to earth fault where as the new wont good luck in finding it
 
EVERY quote / estimate you provide to clients for CU changes should always include a caveat that covers unforeseen issues - I've little sympathy for you.

And when you say "last night" exactly how long did you allow for the change and how much did you charge? A competent CU change will often take 1 day including all the paperwork.

Call you scheme's help line and ask for their advice - assuming you are legit!
 
Last edited by a moderator:
I got there about 3 yesterday due to taking my daughter to the docs didnt get home til 8pm!

No i didnt do any testing before i started as it was an old wylex fuse box all the wires were short and twisted together so i thought id do it when i had finished.

I am going to start by spliting the ring and narrowing it down that way.

My question is, where do i stand with the paperwork if the customer doesnt want to pay to get it fixed.

I did explain before i started that installing a new CU can flag up problems.
 
you gonna have to bite the bullet and find the fault. might sound harsh, but it's your own fault for not carrying out a few basic tests before changing the board. start by splitting the ring final ​eliminate on leg, then split faulty leg down till you've located the problem.
 
I got there about 3 yesterday due to taking my daughter to the docs didnt get home til 8pm!

No i didnt do any testing before i started as it was an old wylex fuse box all the wires were short and twisted together so i thought id do it when i had finished.

I am going to start by spliting the ring and narrowing it down that way.

My question is, where do i stand with the paperwork if the customer doesnt want to pay to get it fixed.

I did explain before i started that installing a new CU can flag up problems.
How can the CU change be "finished" if you haven't done the testing??
 
look on the bright side. you will have learnt as lesson the hard way. you'll not make the same mistake again.
 
What I would advise is as you are changing the protection parameters on a CU change never start one so late in the day start early this then gives you a chance to test and rectify any faults and you get home at a reasonable time bet its a trapped neutral
 
No i didnt do any testing before i started as it was an old wylex fuse box all the wires were short and twisted together so i thought id do it when i had finished.


My question is, where do i stand with the paperwork if the customer doesnt want to pay to get it fixed.

I did explain before i started that installing a new CU can flag up problems.


You can do an IR between lives and to earth from the busbar, no need to undo any connections.

if you explained that it can flag up problems and wrote it in your quote, i do not see the issue. You told them, there is a problem, it needs sorting.

If he won't pay it iooks like its your loss on this one. The fault needs clearing to connect to the RCD, and certify or you have just installed a white elephant in place of their wylex unit!
 
Check the obvious that your neutrals are in the right N bar!
How low are your IR readings if they are less than 0.007 MΩ then this is a good place to start from
Try and assess the cable runs to look for obvious nails, screws and so forth in the wall at odd points.
But the chances are it is just a socket outlet cable trapped or scraped.
 
Hi i went to change a CU last night and the ring main is causing the RCD to trip even with everything unplugged.

I am going back today to investigate abit more, i have just left the ring on the non RCD side for the time being.

The customer is as tight as and doesnt really want to pay for me finding a fault "as it worked before"

I am willing to spend abit of time looking for it for my own peace of mind but the house only has 1 ring so i can tell its going to be a nightmare.

Can i issue an installation certificate for the CU with low insulation resistance readings and note it in the comments?

or can i issue a EICR and recommend a rewire?

There is also no earth on the lighting but all the fittings are plastic, so i have recommended that the lights need a rewire.
TBH I am suprised you haven't been beat up over this, (message to the mods) - told you it was calmer now than a few weeks back didn't I :biggrin5:
 
recipe for disaster... starting a job when you should already be in the pub.
 
Applemac : test first .. sound advice my freind .

dont take for granted , That the ciruit is DEAD .
rewiring . two shops + 3 flats .

it was my fault for not checking the power was DEAD . 99.9% it is DEAD in my case it was 1%

my point is sound . after killing power from two flats , live cables hidden in the plaster , two of the flats have been screwing power for the shop down stair . lighting & sockets . for years . had to get a new pair of Side Cutting Pliers

After all that , the shop was feeding the some of the pub next door . aswell .

is Testing realy needed , YEAH.

Computor shop , in return the shop owner , issuded me with a new computor .
after 3 years , paying othr peoples bills , £700 electric bill he saved on . the landlord ripped up the bill .

teletix . has a vilid point .
look on the bright side. you will have learnt as lesson the hard way. you'll not make the same mistake again. Yes I have . Test , Test , Test .

sorry if mstakes , trying to work this comptor , windows 8 . word 2010
 
Possible a trapped neutral in one of the sockets , un plug every thing insulation test , it the old thing when you do a consumer upgrade "well it worked before " just explain how the RCD works with the old system working with a neutral to earth fault where as the new wont good luck in finding it
possiby a fault that a 3036 wont `see` as well....

(assuming the previous board was utilising these fuses that is)...
 
i have just left the ring on the non RCD side for the time being...The customer is as tight as and doesnt really want to pay for me finding a fault "as it worked before"...There is also no earth on the lighting but all the fittings are plastic, so i have recommended that the lights need a rewire.

Interesting as others have said that your board has a "non-RCD side".

Presumably the job is building control notifiable, is client notifying or are you on their behalf? What's going to happen about that if the sockets are not RCD protected (departs from BS7671), would you sign off on the EIC and notify with it like that?

What did you contract with the client to carry out (i.e. should fixing that ring be an extra charge)?

Don't forget the unearthed lighting warning sticker.
 
Last edited by a moderator:
rockershangout.jpg
 
Lets us have your dead test results on the ring and we might be able to shed some light also is it in twin & earth 2.5/ 1.5 or 2.5 /1.0 .

The IR readings are they in K ohms or Ohms money on a Neutral to Earth bad reading !!
 
No i didnt do any testing before i started as it was an old wylex fuse box all the wires were short and twisted together.

Unfortunately this is the fatal mistake. As much as its a total pain in the back door, it really is worth testing it to make sure it's ok, at least do global IR readings.

The issue now is that you have a board you cannot get to hold.

I ripped one out for a mate last year, it was rammed behind a cupboard and it was a non starter testing it, I got there at 8am, and didn't go home until 4am the next morning.... My stupid fault!

As for the cert, no you need to correct the problem and issue an EIC and notify, this really is the only option.
 
A few of you seem to be suprised about the none rcd side comment.
Usually a 17th dual split board as 5 x 5 rcd protection and then you get a 2way busbar that offers the option fror either a mcb or rcbo.
I always budget for 2 additional rcbo's one for the boiler and one for the cooker so in the event of a fault at least they can keep warm in the winter, have a bath and cook a meal.
I am good me.
 
A few of you seem to be suprised about the none rcd side comment.
Usually a 17th dual split board as 5 x 5 rcd protection and then you get a 2way busbar that offers the option fror either a mcb or rcbo.
I always budget for 2 additional rcbo's one for the boiler and one for the cooker so in the event of a fault at least they can keep warm in the winter, have a bath and cook a meal.
I am good me.
Hi Integrity boards should be made mandatory IMHO, far far better for now and the future
 
The Jam were awesome though
 

Reply to CU Change - Ring Tripping RCD Low IR in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
869
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
860
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I sorted the fault fairly quickly as it happens but only because I'd come across it once before and at the time a few people said it couldn't...
Replies
13
Views
374
Hi, I have a job for a customer, the consumer unit is an old 3036 board and there are several holes in it giving access to live parts, I can...
Replies
6
Views
725

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock