Discuss CU replacement with earthed conduit and singles in the UK Electrical Forum area at ElectriciansForums.net

I can't help but notice that with everyone's fusebox installs the mcbs/rcbos all seem to have a bit of tilt tk them. Did you find that when fitting this? I haven't used one yet and probably never will If they suffer from the mk or mcg slant I can't stand it
 
I can't help but notice that with everyone's fusebox installs the mcbs/rcbos all seem to have a bit of tilt tk them. Did you find that when fitting this? I haven't used one yet and probably never will If they suffer from the mk or mcg slant I can't stand it
Yes I think it is a problem inherent with them. Torquing the lower terminals to 2.5Nm seems to instill a slightly lean, though it's not quite as bad as MK at its worst. They use a similar busbar to MK so maybe something to do with that design, or the clips.

I did try a couple of times to improve it, and to be honest it was slightly worse before the cover went on.

They are nice at the price and the enclosures seem pretty strong compared to some, so happy to use them when I can get them. Waiting for my CEF to get Click in, and may give those a go....
 
If you make some spacers so it clears the switch, you could just maybe just drill, tap and use machine screws.
Or remove the switch and pop-rivet two smaller plates on.
Probably 100 ways to do it!

In the meantime (being over-paranoid) I wonder if a label saying "Isolate Above Not Here" might be a thought in case someone pulls back the tape thinking some wally has taped over the switch!
Nothing is fool-proof for a sufficiently talented fool...
 
You could get some 2 pack araldite epoxy adhesive. Remove switch, etc for a flat face and just glue a suitable piece of steel to the steel. Screwfix do some for about a fiver.
Call at some small fabrication works or garage, maybe. I'm sure someone will cut and provide a suitable piece of steel from a cut off for next to nothing.
 
It's a tidy (and popular) solution to convert the existing board into a marshalling box, but in this case it only worked because of the small number of ways required in the board that would fit in the available space. Had there been three more circuits, that would have been a problem.

This is a situation where I would have used Conlok fittings for the top two conduits The downward conduits could have been dealt with very quickly with a length of 50x50 trunking. Take the old board off, put the trunking against the bottom of it and draw the hole positions through. A few minutes with a drill and a Q-Max and you have a replica that should just drop straight on. But the top two conduits are in the way and assuming they can't be unscrewed, need to be cut back in situ.

If there is enough room to slide some protective hose over the cables and up inside the conduit, you can get rid of 80% of the cross-section of steel with a mini grinder / Dremel disc and snap the rest off. But then you have a plain unthreaded end of conduit for which a Conlok coupling is the obvious solution. It feels like cheating but why not indeed?
 
Soon as you do it, always a better way to improve.
But a steel plate or something and screw it up, jobs a gooden...

Any chance a look inside you junction box.. show the boys its not a mess?
 
It's a tidy (and popular) solution to convert the existing board into a marshalling box, but in this case it only worked because of the small number of ways required in the board that would fit in the available space. Had there been three more circuits, that would have been a problem.

This is a situation where I would have used Conlok fittings for the top two conduits The downward conduits could have been dealt with very quickly with a length of 50x50 trunking. Take the old board off, put the trunking against the bottom of it and draw the hole positions through. A few minutes with a drill and a Q-Max and you have a replica that should just drop straight on. But the top two conduits are in the way and assuming they can't be unscrewed, need to be cut back in situ.

If there is enough room to slide some protective hose over the cables and up inside the conduit, you can get rid of 80% of the cross-section of steel with a mini grinder / Dremel disc and snap the rest off. But then you have a plain unthreaded end of conduit for which a Conlok coupling is the obvious solution. It feels like cheating but why not indeed?
I did wonder about Conlock, but it seemed to have a poor reputation in the places I searched....

One of the top conduits was actually no longer in use but naturally it was the right hand one, so not helpful...

Circumstances in this one required a fairly fast turn around - tenant off work and at home, needing EICR done, etc - and most of the time was needed fixing the other issues in the property...

I'll maybe get some conduit and conlok when I have some free time and have a play around until I'm confident I could do a competent job.

Alternatively if it was empty I'd probably try drawing a CPC through the conduit, or even suggest a rewire...

For now, there is unlikely to ever be need for more circuits (small 1 bed flat). The only real compromise was the lack of an SPD.
 
I did wonder about Conlock, but it seemed to have a poor reputation in the places I searched....

One of the top conduits was actually no longer in use but naturally it was the right hand one, so not helpful...

Circumstances in this one required a fairly fast turn around - tenant off work and at home, needing EICR done, etc - and most of the time was needed fixing the other issues in the property...

I'll maybe get some conduit and conlok when I have some free time and have a play around until I'm confident I could do a competent job.

Alternatively if it was empty I'd probably try drawing a CPC through the conduit, or even suggest a rewire...

For now, there is unlikely to ever be need for more circuits (small 1 bed flat). The only real compromise was the lack of an SPD.
I also wondered about Conlock (having never used it).
The thing that cast lingering doubts is that I believe a small hex grub screw is used to tighten up the fitting, and this doesn't feel adequate to confirm a joint in a CPC. I might be totally wrong, just a gut reaction.
 
Just carried out an EICR on a flat that was wired in the 70s - with singles run in earthed conduit to each point and the trunking providing the earth at each socket/light point.

Ground floor flat, so needs RCD protection on sockets at least and seems due a CU change, but I have no experience with metal trunking so would appreciate the benefit of those with more experience...

View attachment 86492

Upper board can go as there is now a combi and central heating - no off peak circuits being used....

The lower board has approx 8 conduit lengths coming up, and 2 from above...All seem to be correctly glanded to the board - and the ZS readings at all sockets/fittings seem to be fine...

Obviously the chances are nil of finding a board to exactly match what's there - but I'd rather minimise the work - not to mention not having the skill or experience on metal conduit work (and this not being an empty flat where I could learn on the job).

What's the best way to ensure continuity with a new board?

1 option I can see is to leave the existing board in place purely as a 'junction box' for the earths and singles.... and fit a new one above it - leaving only the two upper conduits to deal with.

Another would be to replace the lower board with plastic trunking - terminating all the lower conduit with their existing bushes , but then I'd need to find a way to ensure continuity across the trunking - really don't want to have to cut metal trunking to do the job as it maybe 'should' be done.

If they are cut back, is there an approved clamp or similar to earth them, without needing to thread them for the correct glanding? I've found what is called a bonding nipple that looks like it would still allow space for the singles to exit.

Follow up question - all the sockets I checked have adequate Zs, but are getting that through the socket screws to the earthed back box (with the trunking glanded into each box). There are no fly leads from the box to the earth terminal on sockets. Some of the boxes have a terminal, to make that easy but others do not - but could be screwed, and drilled with self tapping and ring terminals used to make fly leads....

That is apart from the one more recently added socket which had a plasterboard backbox and earth cut short ? (Currently out of use until I can fix it)

In terms of an EICR on an existing installation, would you consider it essential to add the fly leads, a recommend, or not necessary at all as long as the earthing is satisfactory?

Final Question - Easycert has the option to choose 'conduit' for the earthing sizing on the test list. Is there any check that needs to be done to ensure equivalent sizing, or is pretty much all conduit greater than the equivalent T&E sizing?
Are you sure the ‘bonding nipples’ ? are the correct thread?
I like the idea of pulling new cabling through the existing conduit but it could be risky. For me converting the existing fusebox to a j-box din rail, new lid etc and t+e or kopex to the new board is the way.
I have an MICC board change next week but luckily they all come into the top of the board ?
 
Think I would try to maintain the good cpc continuity and save time by not disconnecting/reconnecting the 8/9 conduits and incorporate existing box into new consumer unit/trunking.
 

Reply to CU replacement with earthed conduit and singles in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I've inherited a very tight space, a KMF switch and some split-con for a sub-main to try and tidy up. It's a joyous non-restrained single...
Replies
3
Views
198
Have been asked to do remedials on an EICR that was carried out a year or so ago by another electrician. Curious to know what code you would give...
Replies
12
Views
1K
Has anyone got experience terminating steel conduit from 1935 (so likely imperial measurements) into a new metal enclosure? This was the work of...
Replies
3
Views
672
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
744
Hello everyone, Following on from my previous post where I received advice on taking a spur off a 40a feed (thank you). I performed the work...
Replies
4
Views
889

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock