Just a theoretical question,

If changing a CU and using adaptable box and din rail connectors, working with singles/tri-rated if extending a ring circuit would it be considered bad practise/etc to extend with 4mm2 Instead of using 2x2.5mm2? This is without taking into account de-rating factors as ran in a group etc, but we won't go into that...
 
Last edited:
Electrically theoretically ok with regard to current carrying capacity but potentially confusing when carrying out future EICR or fault finding ie ring end to end. Could be confused for 4mm radial if adaptable box not immediately visible.
 
I would extend the two legs to the new DB, but that's just me.

There's nothing stopping you from lollypopping from the adaptable box to the DB with one cable so long as it is rated appropriately.
 
been thinking of doing that, using wago862, 32A rated connectors, they take up to 4mm cable. wire it up nicely with some tri rated cable in my workshop, then on the site is just a matter of connecting it up. all cables cut and stripped for same length. should look tidy enough, no matter how hard i try my consumer units look a little bit of a mess :-(
 

Reply to CU replacement in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, looking for some advice with regards to extending cables for a consumer unit change. The old board is a mess inside with cables being cut...
Replies
16
Views
8K
EICR today which will need a new CU and clearly I am going to struggle to replace the CU where it is because of height limits - voila: Current...
Replies
9
Views
2K
Anyone got any recommendations on a through crimp tool. A job I have been to look at the client wants the CU moving to a more convenient location...
Replies
26
Views
4K
Hi. I have some TP supply SPD and JB to re wire in 25mm TRI rated cable this weekend. For the Iine conductors i am using 35mm DIN connectors...
Replies
12
Views
2K
I want to replace my consumer unit and move it down the wall so don't need a chair to get at it. However the wires leading to the Consumer Unit...
Replies
14
Views
15K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock