Search the forum,

Discuss Cu upgrade or not ? in the Electricians' Talk area at ElectriciansForums.net

Hi all. Not a working butnvq 3 after 3 yrs at college . Looked at wife's friends cu for her. Was tripping out at random. Checked RCA times and current all ok. Cu box looked rough with large hole in the top and two bare wires poking out. Checked insulation resist of main ring got 340ohms but didn't have time to check further. Also noted that all but one phase and neutral were all loose, and the cooker and old shower cables had melted together. Removed old shower cable and made good connections and burnt wire. Main switch seemed to be rated at 63amps and as client asked for a new shower to be installed I thought that cu would need upgrading even tho it's mcb and rcd.
advised her to ask someone more knowledgable than me.
professional came in fixed tripping( bad socket upstairs) and said box ok for shower its not very old. Wiring In place is 10mm and said he would go away and come back with a quote.
Question is this. Is the 63amp rating on main switch ok for a box feeding a ring main,immersion heater, electric oven and hob, and 9kw shower and lights etc or am I misunderstanding something.

I realise I have to tell local building control of work and present them with my works done and test results. For a certificate

I'd be interested to hear what some of the more experienced chaps say to this as it does seem afair bit for a 63A switch.

If you use the OSG diversity then you've got 32A for the ring and 39A for the shower straight away so your up to 71A without any of the other circuits taken into account.

However if you use the guidelines from some DNO that does seem to get mentioned a fair bit, then you add up all the breakers and multiply by 0.4 View attachment DNO guidelines on Max demand - GOOD.pdf so perhaps (40+32+32+16+6+6) x 0.4 = 52.8A.
 
Eng54 will be along shortly to tell you to clamp it and then be surprised at how low the reading is! Daz
 
she's bloody gorgeous Daz
 

Reply to Cu upgrade or not ? in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

Daughter has bought a house and it has a home security system, G-Tag setup. Issue is the alarm panel displays are pixelated and you cant see...
Replies
1
Views
766
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
25
Views
1K
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
913
I have an interesting scenario that could use some feedback. I have 200A service in my home with a sub panel running to a detached garage...
Replies
0
Views
624
Hope you're all well . I've had ring door bell 2nd generation hardwired for 1.5 yrs... it was connected to transformer which is connected to the...
Replies
22
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock