Discuss CU with a problematic RCD in the UK Electrical Forum area at ElectriciansForums.net

SJD

-
Mentor
Esteemed
Arms
Reaction score
2,812
Went to look at a consumer unit this evening, the owner is having trouble with the RCD not working, notice anything odd about the installation?
 

Attachments

  • 2013-06-06-331-sharp.jpg
    476.9 KB · Views: 78
busbar gives it away. all breakers are fed direct from main switch and looks like RCD L on both in and out is connected direcly to main switch Lout. .
 
obviously B&Q need to update the you can do it manual. or is that what you get when you accept the lowest quote?
 
Yes, RCD L in and out are indeed both connected to main switch L out.

The owner has already had 2 electricians visit, one said the CU needed a new RCD fitting, other other said it needed completely rewiring ...
 
yep, first miss piggy, followed by statler and waldorf. or was it curly, larry and mo.
 

Reply to CU with a problematic RCD in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
758
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
563
Hello, I was looking at installing a SPD into an existing split load RCD BG consumer unit. In the instructions for the SPD it states that it may...
Replies
2
Views
1K
I have pulled out an old evaporative system I purchased many years ago from storage to have a look at it and see if I can get it running. Was...
Replies
1
Views
215
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
916

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock