vbyrne

-
Reaction score
6
Hello, I was just looking for some help with the above subject with looking up the tables for the various protective device and finding the values of C connected with CCCC. I was looking for the rating factor for a BS88 fuse and I found at least 2 different tables the difference being that there were different systems B,C etc this was con fusing as I did not know what table to use . I was just wondering was there a resource out there other than the 7671 that covered this subject and also what are these different systems,
cheers.
 
CCC rating for cables in BS7671 and OSG. that value is Iz. your design current is Ib. the fuse/MCB rating is In. as long as Ib<In<Iz, then you have your values.
 
CCC rating for cables in BS7671 and OSG. that value is Iz. your design current is Ib. the fuse/MCB rating is In. as long as Ib<In<Iz, then you have your values.

Be careful there Tel or you're start giving the impression you know what you're doing and they'll be having you as a trainee mentor ......
 

Reply to Current Carrying Capacity Cables in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, I have a book on domestic wiring which says that everywhere there is a change in current carrying capacity along a circuit there must be some...
Replies
3
Views
327
Hi, go easy on me please, I've just returned to the trade, well I am about to, I received my Gold Card last Thursday. I've been gen'ing up for a...
Replies
4
Views
984
According to note 8 of table 4c1 of bs 7671, cables of differing operating temperatures when grouped together, the current rating is to be based...
Replies
4
Views
519
Hi, The current carrying capacity tables in the BS 7671 for twin and earth cables are only for buildings that have thermal insulation. I'm...
Replies
48
Views
5K
Hi Guys Any one know the current carrying capacity of a 4mm 3 core single phase sy cable ran in a 20mm pvc conduit? Not sure of the right table...
Replies
2
Views
959

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock