can anyone help please,
I am testing a new installation for another contractor, lighting circuits are wired in 1.5mm pvc singles in 4inch metal trunking, protected by 16amp type c mcbs, is this overated considering correction factors applied? thanks
 
This might be a daft idea but if you are carrying out initial verification could you not consult the installation design paperwork? You do of course have this as you are verifying the installation against this as well as bs7671
 
there maywell be a bit of derating there! unless all 18 are rather lightly loaded!

Or unless there isn't a total of 288A supply capacity, in which case you can't run them all at full whack anyway. They might be C16s to avoid tripping on inrush, but only loaded to say 5A with a fixed load. In which case it might not be as bad as it looks...
 
Or unless there isn't a total of 288A supply capacity, in which case you can't run them all at full whack anyway. They might be C16s to avoid tripping on inrush, but only loaded to say 5A with a fixed load. In which case it might not be as bad as it looks...

7671 allows for this with the paragraph below the grouping table. Although they do have to be very lightly loaded to avoid being included in the calculation, hence my comment.
 
What's with all the bloody eh's eeeh's arghhhhhs and ohhhh's then

Can ya lot nay speak proper english like eye yused to did
 

Reply to current carrying capacity in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a book on domestic wiring which says that everywhere there is a change in current carrying capacity along a circuit there must be some...
Replies
3
Views
276
Hi Guys Any one know the current carrying capacity of a 4mm 3 core single phase sy cable ran in a 20mm pvc conduit? Not sure of the right table...
Replies
2
Views
950
Hi, go easy on me please, I've just returned to the trade, well I am about to, I received my Gold Card last Thursday. I've been gen'ing up for a...
Replies
4
Views
925
Hi all, I have a question regarding the breaking capacity of circuit protective devices. So, the breaking capacity rating of devices in domestic...
Replies
13
Views
3K
Had UKPN come out to a property recently to upgrade the main fuse from 60A to 100A but when they arrived they said that the supply cable which he...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock