can anyone help please,
I am testing a new installation for another contractor, lighting circuits are wired in 1.5mm pvc singles in 4inch metal trunking, protected by 16amp type c mcbs, is this overated considering correction factors applied? thanks
 
This might be a daft idea but if you are carrying out initial verification could you not consult the installation design paperwork? You do of course have this as you are verifying the installation against this as well as bs7671
 
there maywell be a bit of derating there! unless all 18 are rather lightly loaded!

Or unless there isn't a total of 288A supply capacity, in which case you can't run them all at full whack anyway. They might be C16s to avoid tripping on inrush, but only loaded to say 5A with a fixed load. In which case it might not be as bad as it looks...
 
Or unless there isn't a total of 288A supply capacity, in which case you can't run them all at full whack anyway. They might be C16s to avoid tripping on inrush, but only loaded to say 5A with a fixed load. In which case it might not be as bad as it looks...

7671 allows for this with the paragraph below the grouping table. Although they do have to be very lightly loaded to avoid being included in the calculation, hence my comment.
 
What's with all the bloody eh's eeeh's arghhhhhs and ohhhh's then

Can ya lot nay speak proper english like eye yused to did
 
Although they do have to be very lightly loaded to avoid being included in the calculation, hence my comment.

There are two separate points here interestingly, and I was focusing on the other one to yours. As you say, if a circuit has a fixed load much lower than its ungrouped capacity, it can be discounted because it will never dissipate much heat. OTOH if heavy diversity has been applied, even where the circuits can each be heavily loaded, it might not be possible to load more than a few at a time. E.g. twelve 10A circuits each with 10A load, but all running on one 60A supply. It's only possible to load half of the circuits fully, and this will always be a worse case for cable heating than the same 60A divided between more of the circuits*, so only six contribute to the grouping.

*Seems obvious to me and can be proven in three lines of math, but I had the devil's own job convincing some sparks of this once.
 
yes i was focusing on 0.3CgIt, rather than the simultaneously loaded conductors route. thanks for the reminder, that had nearly fallen out my head.
 
It's a situation that often occurs in stage lighting. E.g. 96 circuits all protected by K10 MCBs, but running on a total of 3x60A. Only 18 can be fully loaded at once, but in practice it's more likely to be 41 circuits loaded with 4.4A, which requires less derating even though they are above 0.3CgIt.

Not that this applies to normal commercial or industrial lighting though.
 
And then Mr self proclaimed LX expert comes along and types 1 thru 96 @ full enter ;)

And then the lights come on, and then they go off again in a rather terminal fashion thanks to Mr MCCB esquire.
 

Reply to current carrying capacity in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a book on domestic wiring which says that everywhere there is a change in current carrying capacity along a circuit there must be some...
Replies
3
Views
333
Hi Guys Any one know the current carrying capacity of a 4mm 3 core single phase sy cable ran in a 20mm pvc conduit? Not sure of the right table...
Replies
2
Views
962
Hi, go easy on me please, I've just returned to the trade, well I am about to, I received my Gold Card last Thursday. I've been gen'ing up for a...
Replies
4
Views
995
Hi all, I have a question regarding the breaking capacity of circuit protective devices. So, the breaking capacity rating of devices in domestic...
Replies
13
Views
3K
Had UKPN come out to a property recently to upgrade the main fuse from 60A to 100A but when they arrived they said that the supply cable which he...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock