Discuss Curve (Denmans) RCDs in the Electrical Tools and Products area at ElectriciansForums.net

Reaction score
138
Anyone had problems with these rcds? Control Gear Direct, 30mA, 63A 2 pole..

I recently bought two 10-way dual rcd boards from denmans.. first one had an rcd which didnt trip on test button, even with load removed. Second rcd didnt trip under 300mS, but button worked.

Swapped them for the rcds in the second board I had (lucky me, I thought).. one rcd was ok but second one also had trip time problem. swapped the rcds around and the problem followed the rcds.

Got denmans to hotfoot replacement two boards that day... one rcd no trip on test button, the other had trip time problem!
The rcd which "worked" ok, I subsequently found to be a bit intermittent also on trip time. Once i put it on x2 test it seemed to settle down. but also the test button sometimes takes a while to trip as well! ie had to hold it down for a second or two.. the test results when working show no unusual results, all appliances were disconnected.

I did wonder if my tester (metrel 31000) was beginning to play up but worked ok at home and was only calibrated a few weeks ago.
I also put in the only other rcd i had with me, a Hager, and this has been fine.
Control Gear have posted to me 4 replacement rcds with test results, so ill see what happens..

First time ive had NO Trip problems, usually the other way...
 
I’ve been to 3 jobs in past 7 days, with a total of 7 RCDs, 4 in 1, 1 in another, and 2 in the job today.

All 7 wouldn’t time out. Phoned my rep and he said that’s why his place don’t sell them as they wouldn’t time out, that’s the way they came from factory, every one of them.

Anyone else found this?
 
I would agree with Lee above, test the RCD at the terminals with no load connected.
(Eaton RCBOs need to be tested from the cable entry rather than the terminals as the sensing coil is above the terminal.)
I have used some Lewden, curve, Denmans, CGD RCDs but I have not yet had a problem with them. They are bottom of the price range but they should operate OK.
Having seven fail at one installation sounds on the edge of possibility.
 

Reply to Curve (Denmans) RCDs in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
343
What should you do if a client has a CU that is a split board protected by 2 * 63Amp 30mA double pole RCCDs, you took Zs and tested both RCCDs by...
Replies
22
Views
2K
My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...
Replies
12
Views
1K
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
580

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock