edexlab

-
Arms
Reaction score
386
I've just seen an install fitted 2 years ago and I'm interested in how this is G83 compliant! information regarding design etc is being forwarded to me later, but what they've done seems like madness/sheer incompetence to me

I'm going to call the company on clients behalf and hope they sort it as its a shambles this will be the 5th return visit from this firm

There are 2x Aurora 3000 inverters and one 3600, (not sure if Tl's or not i'll be checking later) each has its own Rcd and Mcb fed via 4 wy CU next to the inverters and the single phase supply is daisy chaining across each CU Rcd top terminals

System has worked without issues but recently the Rcd covering the 3600 is tripping out so customer called me in to have a look,

Other than what I've already mentioned above the cable feeding these has no isolation or relevant ocpd and is dogged into the incoming side of the DB main isolator , they've fitted 2 AC isolators next to each inverter and the supply goes through the Rcd (also daisy chained to the next Cu) and Mcb then through the meter and then to the first Ac Isolator and then the 2nd????

Also they have Dc cables in the same 50x50 trunking which I know is debatable re the insulation rating but something I'd not do.

9 feet away is the mains incomer with a 3 phase supply! it is such an easy job to have done better I'm staggered!
 
If it is a 3-phase supply and the embedded generation is not balanced across the phases then that fails G83 straight away - unless there is some dispensation from the DNO but I would be surprised by that.
 
I'm waiting for the design /system details and electrical certs from the client as she has hid them away somewhere, but my thoughts were

a) Install doesn't comply with G83, Mcs, Bs7671 and probably anything else you could think of.

b) Is she therefore at any risk of losing the tariff rate as it could be argued this system was never installed according to the requirements , leaving her to pursue the Installer for loss of revenue etc
It actually makes me mad as she paid good money from a so called reputable firm for this

I do have pictures and will post them this weekend, but its difficult to see exactly what's going on with the inverters supply (daisychained) , I tested the continuity as just looking and tugging wires became confusing very quickly
but you'll be able to see the doubling up of conductors in fhe Rcd terminals etc
 
Are you sure they're not using a single phase board as a manually re-wired three phase board?
 
Last edited:
No the existing main Db is definitely a standard 3 phase Db 4 pole main switch
As I said before the single line supply to the pv db's tapped off the meter side of the main switch as there were no spare ways available and a single phase db next to it with old type 2 mcb's and 2 spare ways, I accept that its hard to source these mcb's but even so they'd still be short one way.

Really simple job to have done properly by splitting the tails via henley blocks to feed a one way 3 phase db with an Mcb/circuit for each Inverter

Out of curiosity do you mean a single phase type enclosure with the removable busbars x 3 which sit together within the busbar guard in the same layout as a single phase board ?

I have used Schneider and I think it was Chint but these are supplied like this as 1 or 2 way 3 phase db's and not modified by an installer
Or are you talking about something someone has modified?

(Occasionally here you do come across a 3 wire single phase supply to a 3 phase board, the ones I've seen had nothing altered within the board they just used the red and yellow mcb ways only and labelled it as such)
 
Last edited:
I've had a look for this company and they are a "National company" the type that tells its customers not to trust small companies
They have poor feedback due to bad installs , hard sell tactics and very poor customer service and the directors are/were? the owners of a company which did the same but with a different product which apparently got national press coverage
 
If it is a 3-phase supply and the embedded generation is not balanced across the phases then that fails G83 straight away - unless there is some dispensation from the DNO but I would be surprised by that.


I've just spoken to the customer re paperwork of this job and She says She'll get it to me soon, but the interesting thing is they have an MCS Cert for each inverter?

I told her what I wanted to see ie MCS Cert , and she said "Oh yes I've got 3 one for each inverter"
Apparently when they complained to the Installer about the RCD tripping She was told

"No worries that's why we put 3 inverters in, in case one stopped working, You'd still have 2 more"

I have tried to post pics but having problems!
 
1004.jpg
Inverters
 

Reply to Daisy chain inverters? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

We don't normally do PV, however I was called to a PV inverter with no power, 6 years old Found supply OK, however fed through a AC type RCD. PV...
Replies
4
Views
773
Hello there I have just installed a new Solis S6-GR1P3.6K-M-DC Inverter - this replaced a 10 year old+ Sungrow inverter that failed/out of...
Replies
5
Views
2K
Hi all, My 3 month old grid tie inverter has tripped on 3 occasions at startup. Have read plenty of threads here about similar issues but unclear...
Replies
1
Views
2K
Hello - hope someone can advise please. I have a recently purchased second hand Myford lathe which has a 3-phase inverter (Siemens Micromaster...
Replies
11
Views
1K
Hello All Can I say to start with I am not an electrician but used to be a heating engineer (yes I can hear the groans). I have wired the...
Replies
85
Views
14K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock